Sign In Help
Schneider Electric
HelpSign In
Schneider Electric Exchange
  • Home
  • Collaborate
  • Develop
  • Shop
Home Collaborate Develop Shop Log in or Register Help

Invite a Co-worker

Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel

Invitation Sent

Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
  • Home
  • Collaborate
  • Exchange Community
  • :
  • EcoStruxure IT
  • :
  • EcoStruxure IT forum
  • :
  • Re: Issue with IDCE as authentication server in ITA
Community Menu
  • Forums
    • By Topic
        • EcoStruxure IT
          • EcoStruxure IT forum
        • Industrial Automation
          • Industry Automation and Control Forum
          • Alliance System Integrators Forum
          • Machine Solutions in the Digital Transformation
          • EcoStruxure Automation Expert / IEC 61499 Forum
          • Industrial Edge Computing Forum
          • Level and Pressure Instrumentation Forum
          • Modicon User Group
          • PLC Club Indonesia
          • SEE Automation Club Forum
          • Fabrika ve Makina Otomasyonu Çözümleri
          • Форум по промышленной автоматизации СНГ
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Forum
          • SCADA and Telemetry Devices Forum
        • Power Distribution IEC
          • Power Distribution and Digital
          • Power Standards & Regulations
          • Paneelbouw & Energie Distributie
          • Eldistribution & Fastighetsautomation
        • Power Distribution Softwares
          • EcoStruxure Power Design Forum
          • SEE Electrical Building+ Forum
          • LayoutFAST User Group Forum
        • Wireless Information Network Solutions
          • Instrument Area Network
          • Remote Monitoring
          • Tank Level Monitoring
          • Remote Data Collection
        • Solutions for your Business
          • Solutions for Food & Beverage Forum
          • Solutions for Healthcare Forum
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Forum
        • Healthcare
          • Solutions for Healthcare Forum
      • EcoStruxure IT
        • EcoStruxure IT forum
      • Industrial Automation
        • Industry Automation and Control Forum
        • Alliance System Integrators Forum
        • Machine Solutions in the Digital Transformation
        • EcoStruxure Automation Expert / IEC 61499 Forum
        • Industrial Edge Computing Forum
        • Level and Pressure Instrumentation Forum
        • Modicon User Group
        • PLC Club Indonesia
        • SEE Automation Club Forum
        • Fabrika ve Makina Otomasyonu Çözümleri
        • Форум по промышленной автоматизации СНГ
      • SCADA & Telemetry Solutions
        • Geo SCADA Expert Forum
        • SCADA and Telemetry Devices Forum
      • Power Distribution IEC
        • Power Distribution and Digital
        • Power Standards & Regulations
        • Paneelbouw & Energie Distributie
        • Eldistribution & Fastighetsautomation
      • Power Distribution Softwares
        • EcoStruxure Power Design Forum
        • SEE Electrical Building+ Forum
        • LayoutFAST User Group Forum
      • Wireless Information Network Solutions
        • Instrument Area Network
        • Remote Monitoring
        • Tank Level Monitoring
        • Remote Data Collection
      • Solutions for your Business
        • Solutions for Food & Beverage Forum
        • Solutions for Healthcare Forum
      • Food & Beverage
        • Solutions for Food & Beverage Forum
      • Healthcare
        • Solutions for Healthcare Forum
  • Blogs
    • By Topic
        • Industrial Automation
          • Industrial Edge Computing Blog
          • Industry 4.0 Blog
          • Industrie du Futur France
        • SCADA & Telemetry Solutions
          • SCADA and Telemetry Blog
        • Power Distribution IEC
          • Power Events & Webinars
          • Power Foundations Blog
        • Power Distribution NEMA
          • NEMA Power Foundations Blog
        • Power Distribution Softwares
          • EcoStruxure Power Design Blog
          • SEE Electrical Building+ Blog
        • Solutions for your Business
          • Solutions for Food & Beverage Blog
          • Solutions for Healthcare Blog
          • Solutions for Retail Blog
        • Community experts & publishers
          • Publishers Community
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Blog
        • Healthcare
          • Solutions for Healthcare Blog
        • Retail
          • Solutions for Retail Blog
      • Industrial Automation
        • Industrial Edge Computing Blog
        • Industry 4.0 Blog
        • Industrie du Futur France
      • SCADA & Telemetry Solutions
        • SCADA and Telemetry Blog
      • Power Distribution IEC
        • Power Events & Webinars
        • Power Foundations Blog
      • Power Distribution NEMA
        • NEMA Power Foundations Blog
      • Power Distribution Softwares
        • EcoStruxure Power Design Blog
        • SEE Electrical Building+ Blog
      • Solutions for your Business
        • Solutions for Food & Beverage Blog
        • Solutions for Healthcare Blog
        • Solutions for Retail Blog
      • Community experts & publishers
        • Publishers Community
      • Food & Beverage
        • Solutions for Food & Beverage Blog
      • Healthcare
        • Solutions for Healthcare Blog
      • Retail
        • Solutions for Retail Blog
  • Ideas
        • Industrial Automation
          • Modicon Ideas & new features
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Ideas
          • SCADA and Telemetry Devices Ideas
  • Knowledge Center
    • Building Automation Knowledge Base
    • Industrial Automation Knowledge Base
    • Industrial Automation How-to videos
    • SCADA & Telemetry Solutions Knowledge Base
    • Digital E-books
    • Success Stories Corner
    • Power Talks
  • Events & Webinars
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Technology Partners
  • Support
    • Ask Exchange
    • Leaderboard
    • Our Community Guidelines
    • Community User Guide
    • How-To & Best Practices
    • More
Join Now
How can we help?
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
51268members
Join Now
245486posts
Join Now

Issue with IDCE as authentication server in ITA

Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Back to EcoStruxure IT forum
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-06 12:16 AM
0 Likes
16
281
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-06 12:16 AM

Issue with IDCE as authentication server in ITA

This question was originally posted on DCIM Support by Everard Eduard on 2019-12-19


Hi,

We want to use DCE as authentication server in ITA.

But get the following error and can't select any username.

What can be the reason?

Regards,

Eduard

(CID:152571091)

Labels
  • Data Center Expert
  • Data Center Operation
Share
  • All forum topics
  • Previous Topic
  • Next Topic
16 Replies 16
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-06 12:17 AM
0 Likes
0
281
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-06 12:17 AM

Re: Issue with IDCE as authentication server in ITA

This comment was originally posted on DCIM Support by spezialist on 2019-12-19


Dear Everard Eduard,

From your question:

We want to use DCE as authentication server in ITA.

Where did you get such information? As far as I know, the DCE-server has never been and cannot be an authentication server.

With respect.

(CID:152571119)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-06 12:17 AM
0 Likes
0
281
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-06 12:17 AM

Re: Issue with IDCE as authentication server in ITA

This comment was originally posted on DCIM Support by Everard Eduard on 2019-12-19


Hi,

Stange answer? DCE is even listed in the drop down menu.

Regards,

Eduard

(CID:152571141)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-06 12:17 AM
0 Likes
0
281
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-06 12:17 AM

Re: Issue with IDCE as authentication server in ITA

This comment was originally posted on DCIM Support by spezialist on 2019-12-19


I am also interested to know: and how does it work?..

(CID:152571162)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-06 12:17 AM
0 Likes
11
281
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-06 12:17 AM

Re: Issue with IDCE as authentication server in ITA

This answer was originally posted on DCIM Support by Jef Faridi on 2019-12-19


Hi Eduard,

What is the version of your DCE?

It is supported to integrate DCE as authentication server in DCO/ITA.

However, it seems we have software bug that needs to be fixed. I have verified this moment ago with ITA 9.0.4 & DCE 7.7.1, getting similar error when trying to add user that should have been authenticated via DCE. 

I have logged a bug report for this.

Thanks,

Kind regards

(CID:152571185)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-06 12:17 AM
0 Likes
0
281
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-06 12:17 AM

Re: Issue with IDCE as authentication server in ITA

This comment was originally posted on DCIM Support by spezialist on 2019-12-19


Dear Jef Faridi,

From your answer:

It is supported to integrate DCE as authentication server in DCO/ITA.

Tell me please, somewhere in the documentation on DCE it is said about such a possibility?

The DCIM community will be grateful if you indicate where is located the detailed description of this possibility (in the documentation or on the DCIM portal).

Very thanks for the support.

(CID:152571206)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-06 12:17 AM
0 Likes
0
281
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-06 12:17 AM

Re: Issue with IDCE as authentication server in ITA

This comment was originally posted on DCIM Support by Greg Sterling on 2019-12-19


There is a mention to this functionality in the DCO documentation here: https://sxwhelpcenter.ecostruxureit.com/display/UADCO8x/Configuring+authentication+servers+used+for+...

(CID:152571231)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-06 12:17 AM
0 Likes
0
281
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-06 12:17 AM

Re: Issue with IDCE as authentication server in ITA

This comment was originally posted on DCIM Support by spezialist on 2019-12-19


Greg Sterling, thanks for the info.

If possible, briefly tell us which authentication mechanism is used in this case (via DCE)?

In addition, I drew attention to this:

Indirect AD authentication (via DCE) is not recommended.

Can you comment please?

Very thanks for the support.

(CID:152571236)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-06 12:17 AM
0 Likes
0
281
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-06 12:17 AM

Re: Issue with IDCE as authentication server in ITA

This comment was originally posted on DCIM Support by Everard Eduard on 2019-12-19


Hi Jef,

I'm running the same version as you:

ITA 9.0.4 & DCE 7.7.1

Regards,

Eduard

(CID:152571246)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-06 12:17 AM
0 Likes
0
281
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-06 12:17 AM

Re: Issue with IDCE as authentication server in ITA

This comment was originally posted on DCIM Support by Valentin Kozlov on 2019-12-20


spezialist, this mechanism was implemented in early DCO versions. At that moment DCO had no AD authentication feature, but it was in DCE. So you create remote user in DCE which authenticated via AD. And after that create user in DCO which autenticated in DCE.

And when you try to login into DCO, it call DCE, which call AD and in the end of the journey user is athenticated by AD 🙂

(CID:153092177)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-06 12:17 AM
0 Likes
0
281
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-06 12:17 AM

Re: Issue with IDCE as authentication server in ITA

This comment was originally posted on DCIM Support by Jef Faridi on 2019-12-20


Hi all,

Many thanks for the info Eduard. Issue might basically be related to the latest improvement in DCE itself, however as mentioned I have logged an investigation/enhancement case for this.

 

And to clarify:

In ITA (or DCO) when configuring authentication servers, the supported types are:

Active Directory

Data Center Expert

LDAP

This type of authentication has been (and still is) supported since early DCO versions.

The scenario Valentin you are describing may or may not work, but that is not supported in ITA (or DCO). User(s) must be local to DCE, when DCE is being used as authentication server.

 Kind regards

(CID:153092189)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-06 12:18 AM
0 Likes
0
281
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-06 12:18 AM

Re: Issue with IDCE as authentication server in ITA

This comment was originally posted on DCIM Support by spezialist on 2019-12-20


Valentin Kozlov and Jef Faridi,

Many thanks for the useful information.

It seems to me, that this detailed information should be published on the DCIM portal in both the DCO and DCE support sections.

With respect.

(CID:153092195)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-06 12:18 AM
0 Likes
0
281
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-06 12:18 AM

Re: Issue with IDCE as authentication server in ITA

This comment was originally posted on DCIM Support by Jef Faridi on 2019-12-20


Hi,

This feature is being used in DCO/ITA, for more info please see the following page:

https://sxwhelpcenter.ecostruxureit.com/display/UADCO8x/Configuring+authentication+servers+used+for+...

Kind regards

(CID:153092198)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-06 12:18 AM
0 Likes
0
281
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-06 12:18 AM

Re: Issue with IDCE as authentication server in ITA

This comment was originally posted on DCIM Support by spezialist on 2019-12-20


Jef Faridi,

I know this and this is good, but it does not say about the restriction that you wrote about:

The scenario Valentin you are describing may or may not work, but that is not supported in ITA (or DCO). User(s) must be local to DCE, when DCE is being used as authentication server.

I think this is an important nuance.

With respect.

(CID:153092201)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-06 12:18 AM
0 Likes
0
281
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-06 12:18 AM

Re: Issue with IDCE as authentication server in ITA

This comment was originally posted on DCIM Support by Jef Faridi on 2019-12-20


Hi,

The documentation (in the above mentioned web page) says "Indirect AD authentication (via DCE) is not recommended."

But, thanks for the suggestion, will add additional note to make it more clear.

Kind regards 

(CID:153092207)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-06 12:18 AM
0 Likes
0
281
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-06 12:18 AM

Re: Issue with IDCE as authentication server in ITA

This comment was originally posted on DCIM Support by spezialist on 2019-12-20


Ok, many thanks for the clarification.

(CID:153092213)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-06 12:18 AM
0 Likes
0
281
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-06 12:18 AM

🔒 Closed

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Share
Top Experts
User Count
Jef
Commander Jef Commander
41
APC_Steve
Lt. Commander APC_Steve Lt. Commander
24
gsterling
Lt. Commander gsterling Lt. Commander
20
Cory_McDonald
Lieutenant Cory_McDonald Lieutenant
13
GavanOB
Lieutenant GavanOB Lieutenant
7
See More Top Experts
Find a Service Provider
Find a certified partner to help you address your integration, installation, maintenance and project needs.
View all Providers
Support

Have a question? Please contact us with details, and we will respond.

Contact Us
FAQ

Look through existing questions to find popular answers.

Learn More
About

Want to know more about Exchange and its possibilities?

Learn More

Full access is just steps away!

Join Exchange for FREE and get unlimited access to our global community of experts.

Connect with Peers & Experts

Discuss challenges in energy and automation with 30,000+ experts and peers.

Get Support in Our Knowledge Base

Find answers in 10,000+ support articles to help solve your product and business challenges.

Ask Questions. Give Solutions

Find peer based solutions to your questions. Provide answers for fellow community members!

Register today for FREE

Register Now

Already have an account?Log in

About Us FAQ Terms & Conditions Privacy Notice Change your cookie settings
©2020, Schneider Electric