Afternoon,
I have an issue when trying to upload the latest ISO (8.1) to the DCO server ready for upgrade. I am not sure why this is happening, previous upgrades have been fine, but this one doesnt seem to work. I have tried 2 different browsers and get the same issue.
The upload gets to 100% but doesnt upload the file as it come up with a message saying "Servername didnt send any data"
(CID:120136438)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 05:16 PM
This answer was originally posted on DCIM Support by Martin Parks on 2017-06-20
Issue Resolved,
Instead of doing it via the "System" "Upload / Download" it works if you select "Others" on the left hand side, and "File Manager"
(CID:120136467)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 05:16 PM
This answer was originally posted on DCIM Support by Martin Parks on 2017-06-20
Issue Resolved,
Instead of doing it via the "System" "Upload / Download" it works if you select "Others" on the left hand side, and "File Manager"
(CID:120136467)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 05:16 PM . Last Modified: 2023-10-22 02:52 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.