  • Informative alarms are being presented "Lost of communication in devices" (when I refer devices are: UPS, PDU, ATS A ° A °, e...
Community Menu
  • Forums
    • By Topic
        • EcoStruxure IT
          • EcoStruxure IT forum
        • Industrial Automation
          • Industry Automation and Control Forum
          • Alliance System Integrators Forum
          • Machine Solutions in the Digital Transformation
          • EcoStruxure Automation Expert / IEC 61499 Forum
          • Industrial Edge Computing Forum
          • Level and Pressure Instrumentation Forum
          • Modicon User Group
          • PLC Club Indonesia
          • SEE Automation Club Forum
          • Fabrika ve Makina Otomasyonu Çözümleri
          • Форум по промышленной автоматизации СНГ
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Forum
          • SCADA and Telemetry Devices Forum
        • Power Distribution IEC
          • Power Distribution and Digital
          • Power Standards & Regulations
          • Paneelbouw & Energie Distributie
        • Power Distribution Softwares
          • EcoStruxure Power Design Forum
          • SEE Electrical Building+ Forum
          • LayoutFAST User Group Forum
        • Solutions for your Business
          • Solutions for Food & Beverage Forum
          • Solutions for Healthcare Forum
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Forum
        • Healthcare
          • Solutions for Healthcare Forum
      • EcoStruxure IT
        • EcoStruxure IT forum
      • Industrial Automation
        • Industry Automation and Control Forum
        • Alliance System Integrators Forum
        • Machine Solutions in the Digital Transformation
        • EcoStruxure Automation Expert / IEC 61499 Forum
        • Industrial Edge Computing Forum
        • Level and Pressure Instrumentation Forum
        • Modicon User Group
        • PLC Club Indonesia
        • SEE Automation Club Forum
        • Fabrika ve Makina Otomasyonu Çözümleri
        • Форум по промышленной автоматизации СНГ
      • SCADA & Telemetry Solutions
        • Geo SCADA Expert Forum
        • SCADA and Telemetry Devices Forum
      • Power Distribution IEC
        • Power Distribution and Digital
        • Power Standards & Regulations
        • Paneelbouw & Energie Distributie
      • Power Distribution Softwares
        • EcoStruxure Power Design Forum
        • SEE Electrical Building+ Forum
        • LayoutFAST User Group Forum
      • Solutions for your Business
        • Solutions for Food & Beverage Forum
        • Solutions for Healthcare Forum
      • Food & Beverage
        • Solutions for Food & Beverage Forum
      • Healthcare
        • Solutions for Healthcare Forum
  • Blogs
    • By Topic
        • Industrial Automation
          • Industrial Edge Computing Blog
          • Industry 4.0 Blog
          • Industrie du Futur France
        • SCADA & Telemetry Solutions
          • SCADA and Telemetry Blog
        • Power Distribution IEC
          • Power Events & Webinars
          • Power Foundations Blog
        • Power Distribution NEMA
          • NEMA Power Foundations Blog
        • Power Distribution Softwares
          • EcoStruxure Power Design Blog
          • SEE Electrical Building+ Blog
        • Solutions for your Business
          • Solutions for Food & Beverage Blog
          • Solutions for Healthcare Blog
          • Solutions for Retail Blog
        • Community experts & publishers
          • Publishers Community
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Blog
        • Healthcare
          • Solutions for Healthcare Blog
        • Retail
          • Solutions for Retail Blog
      • Industrial Automation
        • Industrial Edge Computing Blog
        • Industry 4.0 Blog
        • Industrie du Futur France
      • SCADA & Telemetry Solutions
        • SCADA and Telemetry Blog
      • Power Distribution IEC
        • Power Events & Webinars
        • Power Foundations Blog
      • Power Distribution NEMA
        • NEMA Power Foundations Blog
      • Power Distribution Softwares
        • EcoStruxure Power Design Blog
        • SEE Electrical Building+ Blog
      • Solutions for your Business
        • Solutions for Food & Beverage Blog
        • Solutions for Healthcare Blog
        • Solutions for Retail Blog
      • Community experts & publishers
        • Publishers Community
      • Food & Beverage
        • Solutions for Food & Beverage Blog
      • Healthcare
        • Solutions for Healthcare Blog
      • Retail
        • Solutions for Retail Blog
  • Ideas
        • Industrial Automation
          • Modicon Ideas & new features
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Ideas
          • SCADA and Telemetry Devices Ideas
  • Knowledge Center
    • Building Automation Knowledge Base
    • Industrial Automation How-to videos
    • Ask Exchange
    • Digital E-books
    • Success Stories Corner
    • Power Talks
  • Events & Webinars
  • Support
    • User Guide
    • Leaderboard
    • Releases Notes
How can we help?
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
49540members
Join Now
242897posts
Join Now

Informative alarms are being presented "Lost of communication in devices" (when I refer devices are: UPS, PDU, ATS A ° A °, etc), but when I access by web or I do ping it is the opposite. In other words, they are false alarms. I would also like to ask you

Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Solved Go to Solution
Back to EcoStruxure IT forum
Solved
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 07:37 PM
0 Likes
6
138
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 07:37 PM

Informative alarms are being presented "Lost of communication in devices" (when I refer devices are: UPS, PDU, ATS A ° A °, etc), but when I access by web or I do ping it is the opposite. In other words, they are false alarms. I would also like to ask you

This question was originally posted on DCIM Support by Andres Alfredo Gonzales De La Cotera Herrera on 2019-05-24


Informative alarms are being presented "Lost of communication in devices" (when I refer devices are: UPS, PDU, ATS A ° A °, etc), but when I access by web or I do ping it is the opposite. In other words, they are false alarms. I would also like to ask you if you have the DDF for Air Conditioning UNIFLAIR AMICO Models SUAV0601A and the SDAV0601A that uses the web card: pCOWeb Carel.

(CID:144310877)

Solved! Go to Solution.

Labels
  • Data Center Expert
  • DDF
Share

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 07:38 PM
0 Likes
2
138
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 07:38 PM

Re: Informative alarms are being presented "Lost of communication in devices" (when I refer devices are: UPS, PDU, ATS A ° A °, etc), but when I access by web or I do ping it is the opposite. In other words, they are false alarms. I would also like to ask you

This answer was originally posted on DCIM Support by Valentin Kozlov on 2019-05-24


Hi Andreas!

DCE communicate with devices via SNMP protocol.

You should check your network restrictions about SNMP.

It possible that communication via http or ICMP (ping) is allowed, but other protocols are restricted.

Also you should check if SNMP community configured in DCE settings are the same on NMC cards.

 

DDF for uniflair you can download following this link: https://ddf.ecostruxureit.com/

Type Amico in search field and choose needed file

(CID:144311065)

See Answer In Context

Share
  • All forum topics
  • Previous Topic
  • Next Topic
6 Replies 6
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 07:38 PM
0 Likes
2
139
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 07:38 PM

Re: Informative alarms are being presented "Lost of communication in devices" (when I refer devices are: UPS, PDU, ATS A ° A °, etc), but when I access by web or I do ping it is the opposite. In other words, they are false alarms. I would also like to ask you

This answer was originally posted on DCIM Support by Valentin Kozlov on 2019-05-24


Hi Andreas!

DCE communicate with devices via SNMP protocol.

You should check your network restrictions about SNMP.

It possible that communication via http or ICMP (ping) is allowed, but other protocols are restricted.

Also you should check if SNMP community configured in DCE settings are the same on NMC cards.

 

DDF for uniflair you can download following this link: https://ddf.ecostruxureit.com/

Type Amico in search field and choose needed file

(CID:144311065)

See Answer In Context

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 07:38 PM
0 Likes
0
138
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 07:38 PM

Re: Informative alarms are being presented "Lost of communication in devices" (when I refer devices are: UPS, PDU, ATS A ° A °, etc), but when I access by web or I do ping it is the opposite. In other words, they are false alarms. I would also like to ask you

This comment was originally posted on DCIM Support by Andres Alfredo Gonzales De La Cotera Herrera on 2019-05-28


Hello Valentin,
Thanks for the message, downloaded the ddf from the web, but in the attached files I did not find uniflair_am_uniflair_le_amico_leonardo_ug40mp40_TCPIP_Modbus_CCU, you can help me.

(CID:144311768)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 07:38 PM
0 Likes
0
138
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 07:38 PM

Re: Informative alarms are being presented "Lost of communication in devices" (when I refer devices are: UPS, PDU, ATS A ° A °, etc), but when I access by web or I do ping it is the opposite. In other words, they are false alarms. I would also like to ask you

This comment was originally posted on DCIM Support by Andres Alfredo Gonzales De La Cotera Herrera on 2019-05-28



I have added the ddf, but the Air Conditioning is recognized by the DCIM as the model UG40 / MP40, is it correct?

(CID:144311819)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 07:38 PM
0 Likes
1
138
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 07:38 PM

Re: Informative alarms are being presented "Lost of communication in devices" (when I refer devices are: UPS, PDU, ATS A ° A °, etc), but when I access by web or I do ping it is the opposite. In other words, they are false alarms. I would also like to ask you

This answer was originally posted on DCIM Support by Jake Hiltz on 2019-05-24


Hi Andres,

To add to Valentin's reply about the DDFs, you will need either of these 2 DDFs, depending on whether you need SNMP or Modbus.

uniflair_am_uniflair_le_amico_leonardo_ug40mp40_SNMP_CCU

uniflair_am_uniflair_le_amico_leonardo_ug40mp40_TCPIP_Modbus_CCU

(CID:144311132)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 07:38 PM
0 Likes
0
138
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 07:38 PM

Re: Informative alarms are being presented "Lost of communication in devices" (when I refer devices are: UPS, PDU, ATS A ° A °, etc), but when I access by web or I do ping it is the opposite. In other words, they are false alarms. I would also like to ask you

This comment was originally posted on DCIM Support by Andres Alfredo Gonzales De La Cotera Herrera on 2019-05-28


Hello Jake Thanks for the message, downloaded the ddf from the web, but in the attached files I did not find uniflair_am_uniflair_le_amico_leonardo_ug40mp40_TCPIP_Modbus_CCU, you can help me.

(CID:144311767)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 07:38 PM
0 Likes
0
138
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 07:38 PM

🔒 Closed

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Share
Top Experts
User Count
APC_Steve
Lt. Commander APC_Steve Lt. Commander
2
GavanOB
Lieutenant GavanOB Lieutenant
1
lasalle_1
Crewman lasalle_1
1
Jef
Commander Jef Commander
1
tjlaw
Lieutenant JG tjlaw Lieutenant JG
1
See More Top Experts
Find a Service Provider
Find a certified partner to help you address your integration, installation, maintenance and project needs.
View all Providers
Support

Have a question? Please contact us with details, and we will respond.

Contact Us
FAQ

Look through existing questions to find popular answers.

Learn More
About

Want to know more about Exchange and its possibilities?

Learn More

Full access is just steps away!

Join Exchange for FREE and get unlimited access to our global community of experts.

Connect with Peers & Experts

Discuss challenges in energy and automation with 30,000+ experts and peers.

Get Support in Our Knowledge Base

Find answers in 10,000+ support articles to help solve your product and business challenges.