This question was originally posted on DCIM Support by Andres Alfredo Gonzales De La Cotera Herrera on 2019-05-24
Informative alarms are being presented "Lost of communication in devices" (when I refer devices are: UPS, PDU, ATS A ° A °, etc), but when I access by web or I do ping it is the opposite. In other words, they are false alarms. I would also like to ask you if you have the DDF for Air Conditioning UNIFLAIR AMICO Models SUAV0601A and the SDAV0601A that uses the web card: pCOWeb Carel.
(CID:144310877)
Solved! Go to Solution.
This answer was originally posted on DCIM Support by Valentin Kozlov on 2019-05-24
Hi Andreas!
DCE communicate with devices via SNMP protocol.
You should check your network restrictions about SNMP.
It possible that communication via http or ICMP (ping) is allowed, but other protocols are restricted.
Also you should check if SNMP community configured in DCE settings are the same on NMC cards.
DDF for uniflair you can download following this link: https://ddf.ecostruxureit.com/
Type Amico in search field and choose needed file
(CID:144311065)
This answer was originally posted on DCIM Support by Valentin Kozlov on 2019-05-24
Hi Andreas!
DCE communicate with devices via SNMP protocol.
You should check your network restrictions about SNMP.
It possible that communication via http or ICMP (ping) is allowed, but other protocols are restricted.
Also you should check if SNMP community configured in DCE settings are the same on NMC cards.
DDF for uniflair you can download following this link: https://ddf.ecostruxureit.com/
Type Amico in search field and choose needed file
(CID:144311065)
This comment was originally posted on DCIM Support by Andres Alfredo Gonzales De La Cotera Herrera on 2019-05-28
Hello Valentin,
Thanks for the message, downloaded the ddf from the web, but in the attached files I did not find uniflair_am_uniflair_le_amico_leonardo_ug40mp40_TCPIP_Modbus_CCU, you can help me.
(CID:144311768)
This comment was originally posted on DCIM Support by Andres Alfredo Gonzales De La Cotera Herrera on 2019-05-28
I have added the ddf, but the Air Conditioning is recognized by the DCIM as the model UG40 / MP40, is it correct?
(CID:144311819)
This answer was originally posted on DCIM Support by Jake Hiltz on 2019-05-24
Hi Andres,
To add to Valentin's reply about the DDFs, you will need either of these 2 DDFs, depending on whether you need SNMP or Modbus.
uniflair_am_uniflair_le_amico_leonardo_ug40mp40_SNMP_CCU
uniflair_am_uniflair_le_amico_leonardo_ug40mp40_TCPIP_Modbus_CCU
(CID:144311132)
This comment was originally posted on DCIM Support by Andres Alfredo Gonzales De La Cotera Herrera on 2019-05-28
Hello Jake Thanks for the message, downloaded the ddf from the web, but in the attached files I did not find uniflair_am_uniflair_le_amico_leonardo_ug40mp40_TCPIP_Modbus_CCU, you can help me.
(CID:144311767)
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Discuss challenges in energy and automation with 30,000+ experts and peers.
Find answers in 10,000+ support articles to help solve your product and business challenges.
Find peer based solutions to your questions. Provide answers for fellow community members!