  • Re: InRow "ACRP502 and ACRC301S" Fan fault Error!!!
Community Menu
  • Forums
    • By Topic
        • EcoStruxure IT
          • EcoStruxure IT forum
        • Industrial Automation
          • Industry Automation and Control Forum
          • Alliance System Integrators Forum
          • Machine Solutions in the Digital Transformation
          • EcoStruxure Automation Expert / IEC 61499 Forum
          • Industrial Edge Computing Forum
          • Level and Pressure Instrumentation Forum
          • Modicon User Group
          • PLC Club Indonesia
          • SEE Automation Club Forum
          • Fabrika ve Makina Otomasyonu Çözümleri
          • Форум по промышленной автоматизации СНГ
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Forum
          • SCADA and Telemetry Devices Forum
        • Power Distribution IEC
          • Power Distribution and Digital
          • Power Standards & Regulations
          • Paneelbouw & Energie Distributie
        • Power Distribution Softwares
          • EcoStruxure Power Design Forum
          • SEE Electrical Building+ Forum
          • LayoutFAST User Group Forum
        • Solutions for your Business
          • Solutions for Food & Beverage Forum
          • Solutions for Healthcare Forum
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Forum
        • Healthcare
          • Solutions for Healthcare Forum
      • EcoStruxure IT
        • EcoStruxure IT forum
      • Industrial Automation
        • Industry Automation and Control Forum
        • Alliance System Integrators Forum
        • Machine Solutions in the Digital Transformation
        • EcoStruxure Automation Expert / IEC 61499 Forum
        • Industrial Edge Computing Forum
        • Level and Pressure Instrumentation Forum
        • Modicon User Group
        • PLC Club Indonesia
        • SEE Automation Club Forum
        • Fabrika ve Makina Otomasyonu Çözümleri
        • Форум по промышленной автоматизации СНГ
      • SCADA & Telemetry Solutions
        • Geo SCADA Expert Forum
        • SCADA and Telemetry Devices Forum
      • Power Distribution IEC
        • Power Distribution and Digital
        • Power Standards & Regulations
        • Paneelbouw & Energie Distributie
      • Power Distribution Softwares
        • EcoStruxure Power Design Forum
        • SEE Electrical Building+ Forum
        • LayoutFAST User Group Forum
      • Solutions for your Business
        • Solutions for Food & Beverage Forum
        • Solutions for Healthcare Forum
      • Food & Beverage
        • Solutions for Food & Beverage Forum
      • Healthcare
        • Solutions for Healthcare Forum
  • Blogs
    • By Topic
        • Industrial Automation
          • Industrial Edge Computing Blog
          • Industry 4.0 Blog
          • Industrie du Futur France
        • SCADA & Telemetry Solutions
          • SCADA and Telemetry Blog
        • Power Distribution IEC
          • Power Events & Webinars
          • Power Foundations Blog
        • Power Distribution NEMA
          • NEMA Power Foundations Blog
        • Power Distribution Softwares
          • EcoStruxure Power Design Blog
          • SEE Electrical Building+ Blog
        • Solutions for your Business
          • Solutions for Food & Beverage Blog
          • Solutions for Healthcare Blog
          • Solutions for Retail Blog
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Blog
        • Healthcare
          • Solutions for Healthcare Blog
        • Retail
          • Solutions for Retail Blog
      • Industrial Automation
        • Industrial Edge Computing Blog
        • Industry 4.0 Blog
        • Industrie du Futur France
      • SCADA & Telemetry Solutions
        • SCADA and Telemetry Blog
      • Power Distribution IEC
        • Power Events & Webinars
        • Power Foundations Blog
      • Power Distribution NEMA
        • NEMA Power Foundations Blog
      • Power Distribution Softwares
        • EcoStruxure Power Design Blog
        • SEE Electrical Building+ Blog
      • Solutions for your Business
        • Solutions for Food & Beverage Blog
        • Solutions for Healthcare Blog
        • Solutions for Retail Blog
      • Food & Beverage
        • Solutions for Food & Beverage Blog
      • Healthcare
        • Solutions for Healthcare Blog
      • Retail
        • Solutions for Retail Blog
  • Ideas
        • Industrial Automation
          • Modicon Ideas & new features
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Ideas
          • SCADA and Telemetry Devices Ideas
  • Knowledge Center
    • Building Automation Knowledge Base
    • Industrial Automation How-to videos
    • Ask Exchange
    • Digital E-books
    • Success Stories Corner
    • Power Talks
  • Events & Webinars
  • Support
    • User Guide
    • Leaderboard
    • Releases Notes
How can we help?
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
49249members
Join Now
242460posts
Join Now

InRow "ACRP502 and ACRC301S" Fan fault Error!!!

Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Back to EcoStruxure IT forum
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-03 05:35 PM
0 Likes
5
182
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-03 05:35 PM

InRow "ACRP502 and ACRC301S" Fan fault Error!!!

This question was originally posted on DCIM Support by matthew.nq on 2017-07-05


Hello

There are two cooling device which i mentioned in the topic subject. (InRow "ACRP502 and ACRC301S")

Both of those have problem on FAN section (according to the Event Logs).

 

  • For ACRC301S fans start to work after i change device state to "ON" from "Stand By".

           After a mean while the errors appear :

 06/03/2017    05:45:21    Device    RC: Fan Power Supply 2 Error Detected.

 06/03/2017    05:45:15    Device    RC: Fan Power Supply 1 Error Detected.

 06/03/2017    05:43:20    tsreadonly    Configuration change. On / Standby set to On.

 06/03/2017    05:43:13    tsreadonly    Configuration change. Clear Active Alarms set to Yes.

 06/03/2017    05:43:12    Device    RC: Fan Power Supply 2 Error Corrected.

 06/03/2017    05:43:12    Device    RC: Fan Power Supply 1 Error Corrected.

 06/03/2017    05:41:35    tsreadonly    Configuration change. On / Standby set to Standby.

 06/02/2017    14:45:52    Device    RC: Fan Power Supply 2 Error Corrected.

 06/02/2017    14:45:52    Device    RC: Fan Power Supply 1 Error Corrected.

 06/01/2017    09:20:30    Device    RC: Fan Power Supply 1 Error Detected.

 06/01/2017    09:20:24    Device    RC: Fan Power Supply 2 Error Detected.

 06/01/2017    09:18:30    tsreadonly    Configuration change. On / Standby set to On.

====================================================================================

  • For ACRP502 fans do not start to work after i change device state to "ON" from "Stand By".

          The events appear this how:

 

06/03/2017    14:39:49    System: Coldstart.

06/02/2017    18:44:18    InRow RP: Cooling failure no longer exists.

06/02/2017    18:44:14    InRow RP: Unit control set to Standby.

06/02/2017    18:43:19    InRow RP: Relay output abnormal state exists.

06/02/2017    18:43:17    InRow RP: Cooling failure exists.

06/02/2017    18:43:16    InRow RP: Fan 3 fault exists.

06/02/2017    18:43:16    InRow RP: Fan 2 fault exists.

06/02/2017    18:43:16    InRow RP: Fan 1 fault exists.

06/02/2017    18:43:08    System: Network service started. System IP is 192.168.0.85 from previous settings.

06/02/2017    18:42:12    InRow RP: Unit control set to On .

06/02/2017    18:41:55    InRow RP: Controller Reset - Cold Start because of a unknown reason.

06/02/2017    18:41:55    InRow RP: Internal communication established.

06/02/2017    18:41:37    System: Coldstart.

====================================================================================

Now whats wrong with these two Cooling devices?!

(CID:122685458)

Labels
  • DCIM Support
Tags (1)
  • Tags:
  • Cooling Optimize
Share
  • All forum topics
  • Previous Topic
  • Next Topic
5 Replies 5
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-03 05:35 PM
0 Likes
3
182
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-03 05:35 PM

Re: InRow "ACRP502 and ACRC301S" Fan fault Error!!!

This answer was originally posted on DCIM Support by spezialist on 2017-07-05


Hi matthew.nq,

Both of the above problems, in my opinion, are associated with equipment malfunctions, which can identify and repair local techsupport of Schneider Electric. And, your case is not a single one: see a successful solution of a similar problem, for example, in the topic .

With respect.

(CID:122685477)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-03 05:35 PM
0 Likes
0
182
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-03 05:35 PM

Re: InRow "ACRP502 and ACRC301S" Fan fault Error!!!

This comment was originally posted on DCIM Support by matthew.nq on 2017-07-05


Thank you for your quick answers.

😀

First : I read that topic you mentioned above,but is this the way that i can fix the issue:
We have changed with other (working without alarms) Rectifiers and alarms disappears.

How should I do that?

==================

Second: For the ACRP502,how could I fix its issue?

It doesn't start any more and has 4 error, 3 error for Fan Fault , 1 error is CRITICAL Cooling failure.

how about that?

==================

According to records,we have ACRC103 (the model which discontinued) and has the same problem,Schneider Electric suggested to change the ELECTRICAL BOARD,and the issue has been solved.

Whats your opinion?
Should we change the Electrical Board in both of these products?
Or we should change the rectifiers ?!

I'm a little bit confused.

☹️

 

(CID:122685481)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-03 05:36 PM
0 Likes
0
182
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-03 05:36 PM

Re: InRow "ACRP502 and ACRC301S" Fan fault Error!!!

This comment was originally posted on DCIM Support by spezialist on 2017-07-05


Unfortunately, both of these problems are hardware malfunctions, that you can not solve on your own. And DCIM support also does not help you.

You can only help local techsupport, which has the necessary spare parts for these devices.

Or, if you already have the necessary spare parts and experience in repairing this equipment, then probably you will be able to do it yourself.

I hope, I clearly explained.

With respect.

(CID:122685528)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-03 05:36 PM
0 Likes
0
182
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-03 05:36 PM

Re: InRow "ACRP502 and ACRC301S" Fan fault Error!!!

This comment was originally posted on DCIM Support by spezialist on 2017-07-05


Whats your opinion?
Should we change the Electrical Board in both of these products?
Or we should change the rectifiers ?!

I'm a little bit confused.

Again, this question can only be answered after a detailed diagnosis of your equipment to find out exactly what is causing the malfunction. It can not be remotely done.

With respect.

(CID:122685537)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-03 05:36 PM
0 Likes
0
182
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-03 05:36 PM

🔒 Closed

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Share
Top Experts
User Count
APC_Steve
Lt. Commander APC_Steve Lt. Commander
2
MateFekete
Crewman MateFekete
1
GavanOB
Lieutenant GavanOB Lieutenant
1
lasalle_1
Crewman lasalle_1
1
Jef
Commander Jef Commander
1
See More Top Experts
Find a Service Provider
Find a certified partner to help you address your integration, installation, maintenance and project needs.
View all Providers
Support

Have a question? Please contact us with details, and we will respond.

Contact Us
FAQ

Look through existing questions to find popular answers.

Learn More
About

Want to know more about Exchange and its possibilities?

Learn More

Full access is just steps away!

Join Exchange for FREE and get unlimited access to our global community of experts.

Connect with Peers & Experts

Discuss challenges in energy and automation with 30,000+ experts and peers.

Get Support in Our Knowledge Base

Find answers in 10,000+ support articles to help solve your product and business challenges.

Ask Questions. Give Solutions

Find peer based solutions to your questions. Provide answers for fellow community members!

Register today for FREE

Register Now

Already have an account?Log in

About Us FAQ Terms & Conditions Privacy Notice Change your cookie settings
©2020, Schneider Electric