This question was originally posted on DCIM Support by Mashwiz on 2019-09-09
Hi Team,
Kindly, one way of getting IT load if there are no intelligent pdu is to use the ITOptimize and get the server power consumption directly.
However how can I add this data to my PUE calculator on the IT load section.
Thanks.
(CID:148768449)
This answer was originally posted on DCIM Support by Greg Sterling on 2019-09-09
Based on some tests I ran this morning I would say its not possible to use ITO to feed power data from sensors to the PUE calculator. My ITO server does not appear as a source for sensor data for PUE.
I assume the power devices upstream from the racks are not monitored?
It is possible to use an ETL import database as the source for power data in addition to using a tool like data center expert. In this case though you'd need to come up with a mechanism to transfer power readings into the import database.
(CID:148770293)
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.