HELLO I TRY TO ACCESS TO MY DCO CLIENT BUT GENERATE THIS ERROR:
IMPOSSIBLE TO VALIDATE USER CREDENTIALS. SEE THE DETAILS OF
REGISTRATION OF THE APPLICATION
I´M VALIDATE AN ALL SERVICES ARE RUNNING
(CID:126165068)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 12:48 AM
This comment was originally posted on DCIM Support by OMAR ALFREDO CUERVO DONCEL on 2017-10-17
CURRENT VERSION 8.1
(CID:126165244)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 12:48 AM
This answer was originally posted on DCIM Support by Jef Faridi on 2017-10-18
Hi Omar,
It seems you are trying to connect via port 80, but DCO configured to respond using SSL connection (via port 443). You can select the SSL connection in Advanced Settings:
Kind regards
(CID:126165248)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 12:48 AM . Last Modified: 2023-10-22 02:39 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.