  • I Have Ap9465, How can I monitor it in DCO?
Community Menu
  • Forums
    • By Topic
        • EcoStruxure IT
          • EcoStruxure IT forum
        • Industrial Automation
          • Industry Automation and Control Forum
          • Alliance System Integrators Forum
          • Machine Solutions in the Digital Transformation
          • EcoStruxure Automation Expert / IEC 61499 Forum
          • Industrial Edge Computing Forum
          • Level and Pressure Instrumentation Forum
          • Modicon User Group
          • PLC Club Indonesia
          • SEE Automation Club Forum
          • Fabrika ve Makina Otomasyonu Çözümleri
          • Форум по промышленной автоматизации СНГ
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Forum
          • SCADA and Telemetry Devices Forum
        • Power Distribution IEC
          • Power Distribution and Digital
          • Power Standards & Regulations
          • Paneelbouw & Energie Distributie
        • Power Distribution Softwares
          • EcoStruxure Power Design Forum
          • SEE Electrical Building+ Forum
          • LayoutFAST User Group Forum
        • Solutions for your Business
          • Solutions for Food & Beverage Forum
          • Solutions for Healthcare Forum
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Forum
        • Healthcare
          • Solutions for Healthcare Forum
      • EcoStruxure IT
        • EcoStruxure IT forum
      • Industrial Automation
        • Industry Automation and Control Forum
        • Alliance System Integrators Forum
        • Machine Solutions in the Digital Transformation
        • EcoStruxure Automation Expert / IEC 61499 Forum
        • Industrial Edge Computing Forum
        • Level and Pressure Instrumentation Forum
        • Modicon User Group
        • PLC Club Indonesia
        • SEE Automation Club Forum
        • Fabrika ve Makina Otomasyonu Çözümleri
        • Форум по промышленной автоматизации СНГ
      • SCADA & Telemetry Solutions
        • Geo SCADA Expert Forum
        • SCADA and Telemetry Devices Forum
      • Power Distribution IEC
        • Power Distribution and Digital
        • Power Standards & Regulations
        • Paneelbouw & Energie Distributie
      • Power Distribution Softwares
        • EcoStruxure Power Design Forum
        • SEE Electrical Building+ Forum
        • LayoutFAST User Group Forum
      • Solutions for your Business
        • Solutions for Food & Beverage Forum
        • Solutions for Healthcare Forum
      • Food & Beverage
        • Solutions for Food & Beverage Forum
      • Healthcare
        • Solutions for Healthcare Forum
  • Blogs
    • By Topic
        • Industrial Automation
          • Industrial Edge Computing Blog
          • Industry 4.0 Blog
          • Industrie du Futur France
        • SCADA & Telemetry Solutions
          • SCADA and Telemetry Blog
        • Power Distribution IEC
          • Power Events & Webinars
          • Power Foundations Blog
        • Power Distribution NEMA
          • NEMA Power Foundations Blog
        • Power Distribution Softwares
          • EcoStruxure Power Design Blog
          • SEE Electrical Building+ Blog
        • Solutions for your Business
          • Solutions for Food & Beverage Blog
          • Solutions for Healthcare Blog
          • Solutions for Retail Blog
        • Community experts & publishers
          • Publishers Community
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Blog
        • Healthcare
          • Solutions for Healthcare Blog
        • Retail
          • Solutions for Retail Blog
      • Industrial Automation
        • Industrial Edge Computing Blog
        • Industry 4.0 Blog
        • Industrie du Futur France
      • SCADA & Telemetry Solutions
        • SCADA and Telemetry Blog
      • Power Distribution IEC
        • Power Events & Webinars
        • Power Foundations Blog
      • Power Distribution NEMA
        • NEMA Power Foundations Blog
      • Power Distribution Softwares
        • EcoStruxure Power Design Blog
        • SEE Electrical Building+ Blog
      • Solutions for your Business
        • Solutions for Food & Beverage Blog
        • Solutions for Healthcare Blog
        • Solutions for Retail Blog
      • Community experts & publishers
        • Publishers Community
      • Food & Beverage
        • Solutions for Food & Beverage Blog
      • Healthcare
        • Solutions for Healthcare Blog
      • Retail
        • Solutions for Retail Blog
  • Ideas
        • Industrial Automation
          • Modicon Ideas & new features
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Ideas
          • SCADA and Telemetry Devices Ideas
  • Knowledge Center
    • Building Automation Knowledge Base
    • Industrial Automation How-to videos
    • Ask Exchange
    • Digital E-books
    • Success Stories Corner
    • Power Talks
  • Events & Webinars
  • Support
    • User Guide
    • Leaderboard
    • Releases Notes
How can we help?
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
49523members
Join Now
242869posts
Join Now

I Have Ap9465, How can I monitor it in DCO?

Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Solved Go to Solution
Back to EcoStruxure IT forum
Solved
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-04 10:24 PM
0 Likes
7
160
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-04 10:24 PM

I Have Ap9465, How can I monitor it in DCO?

This question was originally posted on DCIM Support by afsaneh mobin on 2018-08-29


Hello,

My Customer has 3 Ap9465 in different places, I have to monitor all of them by integrating into one DCO, which APC part number I have to use? and how?

Thanks in advance for your help. 

 

Best regards

(CID:134023992)

Solved! Go to Solution.

Labels
  • Data Center Expert
  • Data Center Operation
Share

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-04 10:24 PM
0 Likes
5
160
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-04 10:24 PM

Re: I Have Ap9465, How can I monitor it in DCO?

This answer was originally posted on DCIM Support by Jef Faridi on 2018-08-29


Hi Afsaneh,

If those units (AP9465 / StruxureWare Data Center Expert) are operational and accessible from the DCO side, then they can be integrated in DCO (desktop client) System Setup (1) > External System Configuration (2),  click on "Add server" (3) and Select "StruxureWare Data Center Expert" (4), "Next" and then continue the configuration.

Read more here: Configuring external system integration

And for network ports/firewall port details, please see the fooling page: StruxureWare Data Center Operation Network Firewall Port Details

Kind regards

(CID:134024141)

See Answer In Context

Share
  • All forum topics
  • Previous Topic
  • Next Topic
7 Replies 7
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-04 10:24 PM
0 Likes
5
161
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-04 10:24 PM

Re: I Have Ap9465, How can I monitor it in DCO?

This answer was originally posted on DCIM Support by Jef Faridi on 2018-08-29


Hi Afsaneh,

If those units (AP9465 / StruxureWare Data Center Expert) are operational and accessible from the DCO side, then they can be integrated in DCO (desktop client) System Setup (1) > External System Configuration (2),  click on "Add server" (3) and Select "StruxureWare Data Center Expert" (4), "Next" and then continue the configuration.

Read more here: Configuring external system integration

And for network ports/firewall port details, please see the fooling page: StruxureWare Data Center Operation Network Firewall Port Details

Kind regards

(CID:134024141)

See Answer In Context

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-04 10:24 PM
0 Likes
0
160
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-04 10:24 PM

Re: I Have Ap9465, How can I monitor it in DCO?

This comment was originally posted on DCIM Support by afsaneh mobin on 2018-09-01


Dear Jef,

Thank you so much for your answer. Could you please tell me the part number of DCO? and the quantities of the node is it important to choose the part number of DCO for buying?

As a qualify, the first data center has 30 node (IP equipment), the second data center has 50 nodes, and the third data center has at least 100 nodes. Is it important as an option for choosing DCO part number? or just the quantities of Rack is important? like this:

 

(CID:134025483)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-04 10:24 PM
0 Likes
0
160
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-04 10:24 PM

Re: I Have Ap9465, How can I monitor it in DCO?

This comment was originally posted on DCIM Support by Jef Faridi on 2018-09-03


Hi Afsaneh,

You are most welcome.

In DCO licenses are Rack based, eg. it counts the number of racks in your setup. For example if you have 96 racks in your data center and would like them to be modeled in DCO, then you would need 100 racks license. You can add more when needed.

For more info, please visit the following page: Managing licenses, in particular the section "About DCO licenses".

Kind regards

(CID:134025495)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-04 10:24 PM
0 Likes
0
160
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-04 10:24 PM

Re: I Have Ap9465, How can I monitor it in DCO?

This comment was originally posted on DCIM Support by afsaneh mobin on 2018-09-03


Dear Jef,

Thank you for your answer. Unfortunately, those Ap9465 are basic, so could I integrate them in dco or not? Is it necessary to change hem from basic to operation due to integrating into dco? 

And one more question, AP94VMACT has the operation option and can I integrate it into DCO? or is the same as AP9465 basic?

 

Best Regards.

(CID:134026009)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-04 10:24 PM
0 Likes
0
160
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-04 10:24 PM

Re: I Have Ap9465, How can I monitor it in DCO?

This comment was originally posted on DCIM Support by Jef Faridi on 2018-09-04


Hi Afsaneh,

Both physical and virtual DCE appliance can be integrated in DCO (as external system).

AP9465 is a DCE physical machine (basic model) and can be integrated in DCO.

AP94VMCT is a product name for DCE Virtual machine, that can also be integrated in DCO (as external system).

Both physical DCE and virtual DCE would need to be installed/setup first (DCE software installation and setup), so the DCE server(s) can monitor you data center.

When your DCE (regardless of being physical or virtual machine) is setup and working, then you can integrate the DCE server(s) with you DCO.

Kind regards

(CID:134026024)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-04 10:24 PM
0 Likes
0
160
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-04 10:24 PM

Re: I Have Ap9465, How can I monitor it in DCO?

This comment was originally posted on DCIM Support by afsaneh mobin on 2018-09-16


Dear Jef,

Could you please help me to choose a part number? I do not have a DCO right now and I need it, but I don't know which part number would be used.

There are 450 Racks, I searched and I found AP900500 as a result for dco but it is a license, I don't know that we need a hardware for running DCO or not? Does it need an ap9475 for activating ap900500 license?

Best regards

(CID:134032397)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-04 10:25 PM
0 Likes
0
160
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-04 10:25 PM

🔒 Closed

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Share
Top Experts
User Count
APC_Steve
Lt. Commander APC_Steve Lt. Commander
2
GavanOB
Lieutenant GavanOB Lieutenant
1
lasalle_1
Crewman lasalle_1
1
Jef
Commander Jef Commander
1
tjlaw
Lieutenant JG tjlaw Lieutenant JG
1
See More Top Experts
Find a Service Provider
Find a certified partner to help you address your integration, installation, maintenance and project needs.
View all Providers
Support

Have a question? Please contact us with details, and we will respond.

Contact Us
FAQ

Look through existing questions to find popular answers.

Learn More
About

Want to know more about Exchange and its possibilities?

Learn More

Full access is just steps away!

Join Exchange for FREE and get unlimited access to our global community of experts.

Connect with Peers & Experts

Discuss challenges in energy and automation with 30,000+ experts and peers.

Get Support in Our Knowledge Base

Find answers in 10,000+ support articles to help solve your product and business challenges.

Ask Questions. Give Solutions

Find peer based solutions to your questions. Provide answers for fellow community members!

Register today for FREE

Register Now

Already have an account?Log in

About Us FAQ Terms & Conditions Privacy Notice Change your cookie settings
©2020, Schneider Electric