HI
Is there a way to quickly associate multiple devices?
My PDU has 2 inputs (source), 2 outputs (Group), like 2 PDU, but DCE is a device.
I did not find the DCO (8.0) in has 2 input PDU, so the use 2 PDU,
But in the associated equipment, only one,
Can be associated with multiple DCO devices?
I am now creating multiple of virtual sensors, but the name can not be the perfect match, can not be fast association, the matching rules are what? Like "PDU00", "PDU 00"
(CID:108825768)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 06:12 AM . Last Modified: 2 weeks ago
Hi guanyc, thanks for posting. Lets see who can be of assistance here. @community any ideas? Kind regards Ditte
(CID:108825868)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 06:12 AM . Last Modified: 2 weeks ago
Hi Guanyc,
If it shows up as a single device in DCO (under Unassociated Devices > Monitoring > "DCE server" ) then it can only be associated to a single model.
However for a more clear answer it would be great to know more about this PDU (such as make, model, picture, etc.), and what information it has on DCE (screen capture(s) showing the device and its sensor values), and how it's been reported to DCO (from DCE) as a discovered device (again screen capture will be great).
Kind regards
(CID:108826104)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 06:12 AM . Last Modified: 2 weeks ago
HI, Thanks for reply. PDU should be customized products, Some content may be blurred.
WP_20160923_10_07_02_Pro_LI.jpg
WP_20160923_10_07_42_Pro_LI.jpg
(CID:108826475)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 06:12 AM . Last Modified: 2 weeks ago
Hi Guanyc,
Many thanks for sharing the images - If this PDU is connected to the same upstream power source, then you might want to try to model it as a single device/PDU, and in the "Properties > Power > Breaker Panel" settings configure two sets panels:
(just to illustrate a PDU having two Breaker panels, each with 24 panel size and 200 A breaker rating)
The following page contains detail description about configuring breaker panels:
Working with breaker panels
And then you might be able to use branch circuit monitoring, more info:
Configuring branch circuit monitoring
Kind regards
(CID:108826943)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 06:12 AM . Last Modified: 2 weeks ago
HI, Thanks for reply. Unfortunately. Upstream power source PDU is connected to 2 different UPS.
(CID:108827032)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 06:13 AM . Last Modified: 2023-10-31 11:06 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.