Posted: 2020-07-02 10:47 PM
This question was originally posted on DCIM Support by Mashwiz on 2016-01-27
Hi Team,
I am modeling a rack ATS (AP7724) but I can't see the power option to model Feed A and B, also I need to connect the single corded load on the ATS.
Any suggestions?
Regards,
Felix.
(CID:105461477)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 10:47 PM
This answer was originally posted on DCIM Support by Jesper Bjerregård on 2016-01-27
Hi Mashwiz
Power connections to Rack ATS's is not currently supported. You will be able to add them to the rack, but you can not add power connections to them. Only floor mounted ATS's are supported.
Thanks
Jesper
(CID:105461480)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 10:47 PM
This answer was originally posted on DCIM Support by Jesper Bjerregård on 2016-01-27
Hi Mashwiz
Power connections to Rack ATS's is not currently supported. You will be able to add them to the rack, but you can not add power connections to them. Only floor mounted ATS's are supported.
Thanks
Jesper
(CID:105461480)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 10:47 PM
This comment was originally posted on DCIM Support by Hiren Lad on 2016-01-29
hi Mashwiz Also to add to Jespers comment, floor mounted ATS's cannot be adapted to be mounted in a rack. What we have done for a few customers is as follows; - Created a shelf - called the ATS name - Mounted a half size shelf mounted devices (rPDU) and connected to power source A - The same again for power source B I know this is not clean but it does show two power streams connected to the device in the power dependance view
(CID:105461775)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 10:48 PM
This comment was originally posted on DCIM Support by Mashwiz on 2016-01-29
Hi guys, Thank you. Regards, Felix
(CID:105461779)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 10:48 PM . Last Modified: 2023-10-31 11:06 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.