How to find MAC address on a smartslot belonging to UPS Galaxy VS.

Highlighted
Crewman

How to find MAC address on a smartslot belonging to UPS Galaxy VS.

Sorry for the basic question, I ask for your support.

 

How to find MAC address on a smartslot belonging to UPS Galaxy VS. / Thank you in advance.

1 REPLY 1
Highlighted
Ensign

Re: How to find MAC address on a smartslot belonging to UPS Galaxy VS.

Hi Victor,

 

At the moment the GVS does not report it's MAC address to DCE, but an easy way would be to ping it and then check the arp table. (only works from the same subnet)

 

Ping 192.168.0.1

arp -a

 

arp.png

 

-Gavan

 

APC by Schneider Electric