  • How to connect the inputs of a rack ATS to a breaker panel?
Community Menu
  • Forums
    • By Topic
        • EcoStruxure IT
          • EcoStruxure IT forum
        • Industrial Automation
          • Industry Automation and Control Forum
          • Alliance System Integrators Forum
          • Machine Solutions in the Digital Transformation
          • EcoStruxure Automation Expert / IEC 61499 Forum
          • Industrial Edge Computing Forum
          • Level and Pressure Instrumentation Forum
          • Modicon User Group
          • PLC Club Indonesia
          • SEE Automation Club Forum
          • Fabrika ve Makina Otomasyonu Çözümleri
          • Форум по промышленной автоматизации СНГ
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Forum
          • SCADA and Telemetry Devices Forum
        • Power Distribution IEC
          • Power Distribution and Digital
          • Power Standards & Regulations
          • Paneelbouw & Energie Distributie
        • Power Distribution Softwares
          • EcoStruxure Power Design Forum
          • SEE Electrical Building+ Forum
          • LayoutFAST User Group Forum
        • Solutions for your Business
          • Solutions for Food & Beverage Forum
          • Solutions for Healthcare Forum
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Forum
        • Healthcare
          • Solutions for Healthcare Forum
      • EcoStruxure IT
        • EcoStruxure IT forum
      • Industrial Automation
        • Industry Automation and Control Forum
        • Alliance System Integrators Forum
        • Machine Solutions in the Digital Transformation
        • EcoStruxure Automation Expert / IEC 61499 Forum
        • Industrial Edge Computing Forum
        • Level and Pressure Instrumentation Forum
        • Modicon User Group
        • PLC Club Indonesia
        • SEE Automation Club Forum
        • Fabrika ve Makina Otomasyonu Çözümleri
        • Форум по промышленной автоматизации СНГ
      • SCADA & Telemetry Solutions
        • Geo SCADA Expert Forum
        • SCADA and Telemetry Devices Forum
      • Power Distribution IEC
        • Power Distribution and Digital
        • Power Standards & Regulations
        • Paneelbouw & Energie Distributie
      • Power Distribution Softwares
        • EcoStruxure Power Design Forum
        • SEE Electrical Building+ Forum
        • LayoutFAST User Group Forum
      • Solutions for your Business
        • Solutions for Food & Beverage Forum
        • Solutions for Healthcare Forum
      • Food & Beverage
        • Solutions for Food & Beverage Forum
      • Healthcare
        • Solutions for Healthcare Forum
  • Blogs
    • By Topic
        • Industrial Automation
          • Industrial Edge Computing Blog
          • Industry 4.0 Blog
          • Industrie du Futur France
        • SCADA & Telemetry Solutions
          • SCADA and Telemetry Blog
        • Power Distribution IEC
          • Power Events & Webinars
          • Power Foundations Blog
        • Power Distribution NEMA
          • NEMA Power Foundations Blog
        • Power Distribution Softwares
          • EcoStruxure Power Design Blog
          • SEE Electrical Building+ Blog
        • Solutions for your Business
          • Solutions for Food & Beverage Blog
          • Solutions for Healthcare Blog
          • Solutions for Retail Blog
        • Community experts & publishers
          • Publishers Community
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Blog
        • Healthcare
          • Solutions for Healthcare Blog
        • Retail
          • Solutions for Retail Blog
      • Industrial Automation
        • Industrial Edge Computing Blog
        • Industry 4.0 Blog
        • Industrie du Futur France
      • SCADA & Telemetry Solutions
        • SCADA and Telemetry Blog
      • Power Distribution IEC
        • Power Events & Webinars
        • Power Foundations Blog
      • Power Distribution NEMA
        • NEMA Power Foundations Blog
      • Power Distribution Softwares
        • EcoStruxure Power Design Blog
        • SEE Electrical Building+ Blog
      • Solutions for your Business
        • Solutions for Food & Beverage Blog
        • Solutions for Healthcare Blog
        • Solutions for Retail Blog
      • Community experts & publishers
        • Publishers Community
      • Food & Beverage
        • Solutions for Food & Beverage Blog
      • Healthcare
        • Solutions for Healthcare Blog
      • Retail
        • Solutions for Retail Blog
  • Ideas
        • Industrial Automation
          • Modicon Ideas & new features
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Ideas
          • SCADA and Telemetry Devices Ideas
  • Knowledge Center
    • Building Automation Knowledge Base
    • Industrial Automation How-to videos
    • Ask Exchange
    • Digital E-books
    • Success Stories Corner
    • Power Talks
  • Events & Webinars
  • Support
    • User Guide
    • Leaderboard
    • Releases Notes
How can we help?
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
49540members
Join Now
242912posts
Join Now

How to connect the inputs of a rack ATS to a breaker panel?

Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Back to EcoStruxure IT forum
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-04 10:00 PM
0 Likes
6
97
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-04 10:00 PM

How to connect the inputs of a rack ATS to a breaker panel?

This question was originally posted on DCIM Support by Everard Eduard on 2018-08-21


Hello,

A can't connect the inputs (power dependency) of a rack ATS to a breaker in a breaker panel. I can only connect to a rack PDU in the same rack.

This customer installed all ATS's in 2 extra racks.

The power supplies come from 2 breaker panels.

The outputs go to an extra rack PDU in each rack.

Workaround?

Regards

(CID:133373841)

Labels
  • Data Center Operation
Share
  • All forum topics
  • Previous Topic
  • Next Topic
6 Replies 6
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-04 10:00 PM
0 Likes
0
97
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-04 10:00 PM

Re: How to connect the inputs of a rack ATS to a breaker panel?

This answer was originally posted on DCIM Support by Jef Faridi on 2018-08-21


Hi Eduard,

By design rack ATS can only be connected to the possible two rack pdu's in the same rack, eg 1 pair of rack pdu's can connect only one downstream rack ATS.

Unfortunately no reasonable workaround to offer, I guess any workarounds may result additional "problem" (such as adding new device and/or incorrect power capacity calculations ...), sorry.

Kind regards

(CID:133373867)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-04 10:00 PM
0 Likes
2
97
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-04 10:00 PM

Re: How to connect the inputs of a rack ATS to a breaker panel?

This answer was originally posted on DCIM Support by Daniel S. on 2018-08-21


I had the same problem. I got round it by creating a receptacle in the server rack (e.g. a 16A IEC60309 socket, connected to the correct breaker on the panel) and then connecting the ATS to that receptacle. That way, you can have an ATS go straight back to the breaker panel without going through a PDU. You can do that in the rack's power properties page.

(CID:133373934)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-04 10:00 PM
0 Likes
0
97
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-04 10:00 PM

Re: How to connect the inputs of a rack ATS to a breaker panel?

This comment was originally posted on DCIM Support by Everard Eduard on 2018-08-27


I tried your workaround but can't add a receptacle. I used following procedure: 

Is this the procedure you used?

I get an error:

 

 

 

The following url seems not to excist

http://www.schneider-electric.com/ws/ReceptacleTypes

(CID:134023040)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-04 10:00 PM
0 Likes
0
97
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-04 10:00 PM

Re: How to connect the inputs of a rack ATS to a breaker panel?

This comment was originally posted on DCIM Support by Greg Sterling on 2018-08-28


Hello. To be clear, you do not need to add a receptacle type to DCO, you should add a receptacle to the rack which contains the rack based ATS.

From the rack properties view click the power pane and the new button to create a rack based receptacle.

From the popup window you can define the rack based receptacle. The receptacle type is selected from the pull down list in this view. If proper receptacle type is missing then you'd need to use SOAP or curl to add the proper receptacle type to the below list per the procedure which had been pasted above.

Once created you'll see the rack based receptacles in the power dependency properties for the rack based ATS in the same rack.

Regards

GregS

(CID:134023584)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-04 10:00 PM
0 Likes
0
97
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-04 10:00 PM

Re: How to connect the inputs of a rack ATS to a breaker panel?

This answer was originally posted on DCIM Support by Ryan Elliott on 2018-08-22


I have many AP7732 and similar 2U rack mount ATS in my environments.  My work around has been as follows.  I have created a 1U 30A  PDU calling it a "Modified ATS"  I then stack two of them in a 2U space connecting one to a "A" feed PDU and the other to a "B" feed PDU in the rack that they exist.  This allows me to easily dedicate the power path.

(CID:133374217)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-04 10:01 PM
0 Likes
0
97
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-04 10:01 PM

🔒 Closed

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Share
Top Experts
User Count
APC_Steve
Lt. Commander APC_Steve Lt. Commander
2
GavanOB
Lieutenant GavanOB Lieutenant
1
lasalle_1
Crewman lasalle_1
1
Jef
Commander Jef Commander
1
tjlaw
Lieutenant JG tjlaw Lieutenant JG
1
See More Top Experts
Find a Service Provider
Find a certified partner to help you address your integration, installation, maintenance and project needs.
View all Providers
Support

Have a question? Please contact us with details, and we will respond.

Contact Us
FAQ

Look through existing questions to find popular answers.

Learn More
About

Want to know more about Exchange and its possibilities?

Learn More

Full access is just steps away!

Join Exchange for FREE and get unlimited access to our global community of experts.

Connect with Peers & Experts

Discuss challenges in energy and automation with 30,000+ experts and peers.

Get Support in Our Knowledge Base

Find answers in 10,000+ support articles to help solve your product and business challenges.

Ask Questions. Give Solutions

Find peer based solutions to your questions. Provide answers for fellow community members!

Register today for FREE

Register Now

Already have an account?Log in

About Us FAQ Terms & Conditions Privacy Notice Change your cookie settings
©2020, Schneider Electric