I have tried positions 1 and 2 in the sensor, with or without a terminator plug. The only pictures of documentation is when you are daisy chaining, not just one single sensor probe. Please help! The EMU will not see the probe. (Both new units)
(CID:106891667)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 04:47 AM . Last Modified: 1 week ago
HI Mari!
You can set any address from 1 to 8 on the sensor, it's not important in your case. Address must be unique in the chain.
Be sure that you takes sensor in right position when setting address (display up)
Be sure that you use regular Cat5 cables, not crossover and shielded cables (Cat6 or Cat7)
Do you see Err symbols in web interface of appliance?
(CID:106891686)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 04:47 AM . Last Modified: 2023-10-31 11:04 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.