Sign In Help
Schneider Electric
HelpSign In
Schneider Electric Exchange
  • Home
  • Collaborate
  • Develop
  • Shop
Home Collaborate Develop Shop Log in or Register Help

Invite a Co-worker

Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel

Invitation Sent

Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
  • Home
  • Collaborate
  • Exchange Community
  • :
  • EcoStruxure IT
  • :
  • EcoStruxure IT forum
  • :
  • How to add NetBotz 750 to DCE
Community Menu
  • Forums
    • By Topic
        • EcoStruxure IT
          • EcoStruxure IT forum
        • Industrial Automation
          • Industry Automation and Control Forum
          • Alliance System Integrators Forum
          • Machine Solutions in the Digital Transformation
          • EcoStruxure Automation Expert / IEC 61499 Forum
          • Industrial Edge Computing Forum
          • Level and Pressure Instrumentation Forum
          • Modicon User Group
          • PLC Club Indonesia
          • SEE Automation Club Forum
          • Fabrika ve Makina Otomasyonu Çözümleri
          • Форум по промышленной автоматизации СНГ
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Forum
          • SCADA and Telemetry Devices Forum
        • Power Distribution IEC
          • Power Distribution and Digital
          • Power Standards & Regulations
          • Paneelbouw & Energie Distributie
        • Power Distribution Softwares
          • EcoStruxure Power Design Forum
          • SEE Electrical Building+ Forum
          • LayoutFAST User Group Forum
        • Solutions for your Business
          • Solutions for Food & Beverage Forum
          • Solutions for Healthcare Forum
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Forum
        • Healthcare
          • Solutions for Healthcare Forum
      • EcoStruxure IT
        • EcoStruxure IT forum
      • Industrial Automation
        • Industry Automation and Control Forum
        • Alliance System Integrators Forum
        • Machine Solutions in the Digital Transformation
        • EcoStruxure Automation Expert / IEC 61499 Forum
        • Industrial Edge Computing Forum
        • Level and Pressure Instrumentation Forum
        • Modicon User Group
        • PLC Club Indonesia
        • SEE Automation Club Forum
        • Fabrika ve Makina Otomasyonu Çözümleri
        • Форум по промышленной автоматизации СНГ
      • SCADA & Telemetry Solutions
        • Geo SCADA Expert Forum
        • SCADA and Telemetry Devices Forum
      • Power Distribution IEC
        • Power Distribution and Digital
        • Power Standards & Regulations
        • Paneelbouw & Energie Distributie
      • Power Distribution Softwares
        • EcoStruxure Power Design Forum
        • SEE Electrical Building+ Forum
        • LayoutFAST User Group Forum
      • Solutions for your Business
        • Solutions for Food & Beverage Forum
        • Solutions for Healthcare Forum
      • Food & Beverage
        • Solutions for Food & Beverage Forum
      • Healthcare
        • Solutions for Healthcare Forum
  • Blogs
    • By Topic
        • Industrial Automation
          • Industrial Edge Computing Blog
          • Industry 4.0 Blog
          • Industrie du Futur France
        • SCADA & Telemetry Solutions
          • SCADA and Telemetry Blog
        • Power Distribution IEC
          • Power Events & Webinars
          • Power Foundations Blog
        • Power Distribution NEMA
          • NEMA Power Foundations Blog
        • Power Distribution Softwares
          • EcoStruxure Power Design Blog
          • SEE Electrical Building+ Blog
        • Solutions for your Business
          • Solutions for Food & Beverage Blog
          • Solutions for Healthcare Blog
          • Solutions for Retail Blog
        • Community experts & publishers
          • Publishers Community
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Blog
        • Healthcare
          • Solutions for Healthcare Blog
        • Retail
          • Solutions for Retail Blog
      • Industrial Automation
        • Industrial Edge Computing Blog
        • Industry 4.0 Blog
        • Industrie du Futur France
      • SCADA & Telemetry Solutions
        • SCADA and Telemetry Blog
      • Power Distribution IEC
        • Power Events & Webinars
        • Power Foundations Blog
      • Power Distribution NEMA
        • NEMA Power Foundations Blog
      • Power Distribution Softwares
        • EcoStruxure Power Design Blog
        • SEE Electrical Building+ Blog
      • Solutions for your Business
        • Solutions for Food & Beverage Blog
        • Solutions for Healthcare Blog
        • Solutions for Retail Blog
      • Community experts & publishers
        • Publishers Community
      • Food & Beverage
        • Solutions for Food & Beverage Blog
      • Healthcare
        • Solutions for Healthcare Blog
      • Retail
        • Solutions for Retail Blog
  • Ideas
        • Industrial Automation
          • Modicon Ideas & new features
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Ideas
          • SCADA and Telemetry Devices Ideas
  • Knowledge Center
    • Building Automation Knowledge Base
    • Industrial Automation How-to videos
    • Ask Exchange
    • Digital E-books
    • Success Stories Corner
    • Power Talks
  • Events & Webinars
  • Support
    • User Guide
    • Leaderboard
    • Releases Notes
How can we help?
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
49346members
Join Now
242603posts
Join Now

How to add NetBotz 750 to DCE

Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Back to EcoStruxure IT forum
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 08:05 PM
0 Likes
5
134
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 08:05 PM

How to add NetBotz 750 to DCE

This question was originally posted on DCIM Support by Matt Wagner on 2019-06-17


Hi,

I've recently set up a NetBotz 750 and two camera pods attached to it. I've tried adding it into DCE in the same way as my other NetBotz devices, however it wont add? The discovery just runs and the device doesn't appear?

Is the procedure different for adding the new device in?

Thanks

Matt

(CID:145424940)

Labels
  • Data Center Expert
  • NetBotz
Share
  • All forum topics
  • Previous Topic
  • Next Topic
5 Replies 5
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 08:05 PM
0 Likes
0
134
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 08:05 PM

Re: How to add NetBotz 750 to DCE

This answer was originally posted on DCIM Support by Jakub Porebski on 2019-06-17


I had the same problem and had to reach out to support. Below worked for me.

Also it might be worth updating the netbotz firmware. Good luck!

 

Issue:

You cannot use the Netbotz Web UI password to download the essential Device Definition (DDF) file for the Rack Monitor 750 in StruxureWare Data Center Expert (DCE).

Product Line:

NetBotz

StruxureWare Data Center Expert

Environment:

NetBotz 5.x

NetBotx 750

StruxureWare Data Center Expert 7.6 and higher

Cause:

You must use the Netbotz Root account user name and password to download the Essential Alerts Device Definition File (DDF) for the Rack Monitor 750. The Essential Alerts DDF is a secondary DDF used by DCE that defines the pre-configured alarms for which DCE will alert.

Resolution:

Use the Netbotz Root account user name and password to download the DDF. The default user name is root. You set the password on first use.

 

Please refer to the Netbotz Installation Manual on page 13 that details the 'Types of User Account'

https://www.apc.com/salestools/HLAE-AUPJSL/HLAE-AUPJSL_R3_EN.pdf

NOTE:  You must enable and configure SNMP on the Netbotz before DCE can discover the appliance.  See page 37 in the User Guide for instructions https://www.apc.com/salestools/HLAE-AUVRS9/HLAE-AUVRS9_R2_EN.pdf

 

Finally, I can see from the Netbotz product page that the current DDF version is v4.0.0

https://www.apc.com/shop/ie/en/products//P-SFNBDDF400



(CID:145424952)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 08:05 PM
0 Likes
2
134
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 08:05 PM

Re: How to add NetBotz 750 to DCE

This answer was originally posted on DCIM Support by Steven Marchetti on 2019-06-17


Hi Matt,

the 750 is added to DCE as an SNMP device. 

Jakub’s suggestion as also important. 

Please note that until BotzWare 5.2 and DCE 7.7, the cameras are not yet supported. 

 

Steve. 

(CID:145425037)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 08:05 PM
0 Likes
0
134
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 08:05 PM

Re: How to add NetBotz 750 to DCE

This comment was originally posted on DCIM Support by Miguel angel solans on 2019-06-17


Steven

BotzWare 5.2 and DCE 7.7, when are going to be ?


(CID:145425085)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 08:06 PM
0 Likes
0
134
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 08:06 PM

Re: How to add NetBotz 750 to DCE

This comment was originally posted on DCIM Support by Steven Marchetti on 2019-06-18


Hi Miguel,

i have no firm dates at this time. I know it was planned to be July but that can still change so I don’t want to give you something specific. 

 

Steve. 

(CID:145425143)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 08:06 PM
0 Likes
0
134
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 08:06 PM

🔒 Closed

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Share
Top Experts
User Count
APC_Steve
Lt. Commander APC_Steve Lt. Commander
2
MateFekete
Crewman MateFekete
1
GavanOB
Lieutenant GavanOB Lieutenant
1
lasalle_1
Crewman lasalle_1
1
Jef
Commander Jef Commander
1
See More Top Experts
Find a Service Provider
Find a certified partner to help you address your integration, installation, maintenance and project needs.
View all Providers
Support

Have a question? Please contact us with details, and we will respond.

Contact Us
FAQ

Look through existing questions to find popular answers.

Learn More
About

Want to know more about Exchange and its possibilities?

Learn More

Full access is just steps away!

Join Exchange for FREE and get unlimited access to our global community of experts.

Connect with Peers & Experts

Discuss challenges in energy and automation with 30,000+ experts and peers.

Get Support in Our Knowledge Base

Find answers in 10,000+ support articles to help solve your product and business challenges.

Ask Questions. Give Solutions

Find peer based solutions to your questions. Provide answers for fellow community members!

Register today for FREE

Register Now

Already have an account?Log in

About Us FAQ Terms & Conditions Privacy Notice Change your cookie settings
©2020, Schneider Electric