EcoStruxure IT forum
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 06:10 PM . Last Modified: 2 weeks ago
How do I register server in HP Moonshot 1500 Chassis, i have 45 server in each Moonshot Chassis?
(CID:131965990)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 06:10 PM . Last Modified: 2 weeks ago
Hi Carsten,
I don't think that is directly possible to model, however I was wondering perhaps using the device custom properties could be useful:
The tool-tip in rack view would also display these properties:
as well as in web-client:
PS. Your 'HP Moonshot 1500 Chassis' doesn't seem to be included in Genome Library, so for the time being you might want to customize one (by taking & customizing a similar device from Genome Library). You might also want to post a request here: http://sxwhelpcenter.ecostruxureit.com/devices , so it can be added in a future Genome update.
Hope this helps,
Kind regards
(CID:131967241)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 06:10 PM . Last Modified: 2 weeks ago
Hi Carsten,
I don't think that is directly possible to model, however I was wondering perhaps using the device custom properties could be useful:
The tool-tip in rack view would also display these properties:
as well as in web-client:
PS. Your 'HP Moonshot 1500 Chassis' doesn't seem to be included in Genome Library, so for the time being you might want to customize one (by taking & customizing a similar device from Genome Library). You might also want to post a request here: http://sxwhelpcenter.ecostruxureit.com/devices , so it can be added in a future Genome update.
Hope this helps,
Kind regards
(CID:131967241)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 06:10 PM . Last Modified: 2 weeks ago
Hi
Thejaswi have anwser me:
Hi, I have processed the HPE Proliant M710X and the HPE moonshot 1500 both in the system. I was unable to find the weight of the HPE Proliant M710X. Hence I have taken the nearest weight value of a similar unit as 20 lbs. You can start using the genomes after our next genome file release, which will be done on last week of every month. If you have any other questions, please let me know. I will be glad to help you. Regards Thejaswi
Thejaswi Manjunatha
BR
Carsten
(CID:132659269)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 06:11 PM . Last Modified: 2023-10-22 02:21 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.