Has anyone had success adding Liebert UPS units into Struxureware DCE?
(CID:129406010)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 03:10 PM . Last Modified: 3 weeks ago
Hi,
Yes. You may search for your UPS model's DDF in Device support. If the model you are looking for is not in the list, you can request the DDF in the same link as well. Do follow the procedure to request new DDF.
(CID:129406350)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 03:10 PM . Last Modified: 3 weeks ago
Hi,
Yes. You may search for your UPS model's DDF in Device support. If the model you are looking for is not in the list, you can request the DDF in the same link as well. Do follow the procedure to request new DDF.
(CID:129406350)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 03:10 PM . Last Modified: 3 weeks ago
Would you please someone share the experience of the following issue.
the Emerson Liebert APM model's DDF file has been downloaded and imported to DCE; however, the DCE cannot detect the UPS after we installed the new network card in UPS. Is there any step that we can try ?
New Network Card Info.: UF-SNMP810 SNMP Card
(CID:132666165)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 03:10 PM . Last Modified: 3 weeks ago
Dear Eva,
From your question:
...however, the DCE cannot detect the UPS after we installed the new network card in UPS.
Tell us, please, what model of NMC did you have before? With the old model NMC, DCE software worked fine?
With respect.
(CID:132666186)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 03:10 PM . Last Modified: 3 weeks ago
On the Liebert web interface, under SNMP access, we had to add the DCE ip address to allow SNMP access.
(CID:132666446)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 03:10 PM . Last Modified: 3 weeks ago
Hi,
You may want to check the settings in ups side whether the firmware for the snmp card replaced matches the current firmware setting of the ups?
I have one case where they did something in the firmware, the oid changes and ddf unable to read the values from ups.
Thanks and regards.
(CID:132666545)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 03:10 PM . Last Modified: 3 weeks ago
Hi All,
Thank you for your help. The issue has been solved as I.T. did the set module in network.
(CID:132666643)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 03:10 PM . Last Modified: 2023-10-22 02:15 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.