Sign In Help
Schneider Electric
HelpSign In
Schneider Electric Exchange
  • Home
  • Collaborate
  • Develop
  • Shop
Home Collaborate Develop Shop Log in or Register Help

Invite a Co-worker

Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel

Invitation Sent

Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
  • Home
  • Collaborate
  • Exchange Community
  • :
  • EcoStruxure IT
  • :
  • EcoStruxure IT forum
  • :
  • HID access cards security
Community Menu
  • Forums
    • By Topic
        • EcoStruxure IT
          • EcoStruxure IT forum
        • Industrial Automation
          • Industry Automation and Control Forum
          • Alliance System Integrators Forum
          • Machine Solutions in the Digital Transformation
          • EcoStruxure Automation Expert / IEC 61499 Forum
          • Industrial Edge Computing Forum
          • Level and Pressure Instrumentation Forum
          • Modicon User Group
          • PLC Club Indonesia
          • SEE Automation Club Forum
          • Fabrika ve Makina Otomasyonu Çözümleri
          • Форум по промышленной автоматизации СНГ
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Forum
          • SCADA and Telemetry Devices Forum
        • Power Distribution IEC
          • Power Distribution and Digital
          • Power Standards & Regulations
          • Paneelbouw & Energie Distributie
        • Power Distribution Softwares
          • EcoStruxure Power Design Forum
          • SEE Electrical Building+ Forum
          • LayoutFAST User Group Forum
        • Solutions for your Business
          • Solutions for Food & Beverage Forum
          • Solutions for Healthcare Forum
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Forum
        • Healthcare
          • Solutions for Healthcare Forum
      • EcoStruxure IT
        • EcoStruxure IT forum
      • Industrial Automation
        • Industry Automation and Control Forum
        • Alliance System Integrators Forum
        • Machine Solutions in the Digital Transformation
        • EcoStruxure Automation Expert / IEC 61499 Forum
        • Industrial Edge Computing Forum
        • Level and Pressure Instrumentation Forum
        • Modicon User Group
        • PLC Club Indonesia
        • SEE Automation Club Forum
        • Fabrika ve Makina Otomasyonu Çözümleri
        • Форум по промышленной автоматизации СНГ
      • SCADA & Telemetry Solutions
        • Geo SCADA Expert Forum
        • SCADA and Telemetry Devices Forum
      • Power Distribution IEC
        • Power Distribution and Digital
        • Power Standards & Regulations
        • Paneelbouw & Energie Distributie
      • Power Distribution Softwares
        • EcoStruxure Power Design Forum
        • SEE Electrical Building+ Forum
        • LayoutFAST User Group Forum
      • Solutions for your Business
        • Solutions for Food & Beverage Forum
        • Solutions for Healthcare Forum
      • Food & Beverage
        • Solutions for Food & Beverage Forum
      • Healthcare
        • Solutions for Healthcare Forum
  • Blogs
    • By Topic
        • Industrial Automation
          • Industrial Edge Computing Blog
          • Industry 4.0 Blog
          • Industrie du Futur France
        • SCADA & Telemetry Solutions
          • SCADA and Telemetry Blog
        • Power Distribution IEC
          • Power Events & Webinars
          • Power Foundations Blog
        • Power Distribution NEMA
          • NEMA Power Foundations Blog
        • Power Distribution Softwares
          • EcoStruxure Power Design Blog
          • SEE Electrical Building+ Blog
        • Solutions for your Business
          • Solutions for Food & Beverage Blog
          • Solutions for Healthcare Blog
          • Solutions for Retail Blog
        • Community experts & publishers
          • Publishers Community
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Blog
        • Healthcare
          • Solutions for Healthcare Blog
        • Retail
          • Solutions for Retail Blog
      • Industrial Automation
        • Industrial Edge Computing Blog
        • Industry 4.0 Blog
        • Industrie du Futur France
      • SCADA & Telemetry Solutions
        • SCADA and Telemetry Blog
      • Power Distribution IEC
        • Power Events & Webinars
        • Power Foundations Blog
      • Power Distribution NEMA
        • NEMA Power Foundations Blog
      • Power Distribution Softwares
        • EcoStruxure Power Design Blog
        • SEE Electrical Building+ Blog
      • Solutions for your Business
        • Solutions for Food & Beverage Blog
        • Solutions for Healthcare Blog
        • Solutions for Retail Blog
      • Community experts & publishers
        • Publishers Community
      • Food & Beverage
        • Solutions for Food & Beverage Blog
      • Healthcare
        • Solutions for Healthcare Blog
      • Retail
        • Solutions for Retail Blog
  • Ideas
        • Industrial Automation
          • Modicon Ideas & new features
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Ideas
          • SCADA and Telemetry Devices Ideas
  • Knowledge Center
    • Building Automation Knowledge Base
    • Industrial Automation How-to videos
    • Ask Exchange
    • Digital E-books
    • Success Stories Corner
    • Power Talks
  • Events & Webinars
  • Support
    • User Guide
    • Leaderboard
    • Releases Notes
How can we help?
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
49540members
Join Now
242912posts
Join Now

HID access cards security

Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Solved Go to Solution
Back to EcoStruxure IT forum
Solved
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 04:49 PM
0 Likes
5
114
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 04:49 PM

HID access cards security

This question was originally posted on DCIM Support by mike sutton on 2019-02-04


Hi I wonder if someone can give me some advice please, 

We have a client who has multiple locations with Botz 170 rack access kits fitted and also Botz 250 rack access kits fitted and the following question has arisen during a security check:

"In a security review it has been made apparent that some proximity cards are not secure and can be easily cloned. I have been asked to see if the APC cards we use have any sort of security on them to help prevent this."

Can anyone shed any light on this??

 

TIA 

Mike

(CID:139691809)

Solved! Go to Solution.

Labels
  • Data Center Expert
  • NetBotz
Share

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 04:49 PM
0 Likes
2
114
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 04:49 PM

Re: HID access cards security

This answer was originally posted on DCIM Support by Steven Marchetti on 2019-02-04


Hi Mike,

 

The cards we use are HID H10301. We purchase them HID and do not make our own. I do not have any further model information. I do know that some cards can have extra information written to them but all that the NetBotz device reads is the card number. If you can read the card and you have another card with that number, or, you can write that card number, you would be able to use that for access. I can tell you that although other information is writable, I do not believe that by default the card's ID number is editable.

In any case, I will forward your concerns on to my engineers to see if they have a better answer for you. I'll get back when I hear more.

 

Thanks,

Steve 

(CID:139691884)

See Answer In Context

Share
  • All forum topics
  • Previous Topic
  • Next Topic
5 Replies 5
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 04:49 PM
0 Likes
0
114
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 04:49 PM

Re: HID access cards security

This comment was originally posted on DCIM Support by mike sutton on 2019-02-04


They have sent me the following link containing info about this 

https://www.getkisi.com/blog/hid-keycard-readers-hacked-using-wiegand-protocol-vulnerability

 

(CID:139691880)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 04:49 PM
0 Likes
2
115
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 04:49 PM

Re: HID access cards security

This answer was originally posted on DCIM Support by Steven Marchetti on 2019-02-04


Hi Mike,

 

The cards we use are HID H10301. We purchase them HID and do not make our own. I do not have any further model information. I do know that some cards can have extra information written to them but all that the NetBotz device reads is the card number. If you can read the card and you have another card with that number, or, you can write that card number, you would be able to use that for access. I can tell you that although other information is writable, I do not believe that by default the card's ID number is editable.

In any case, I will forward your concerns on to my engineers to see if they have a better answer for you. I'll get back when I hear more.

 

Thanks,

Steve 

(CID:139691884)

See Answer In Context

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 04:49 PM
0 Likes
0
114
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 04:49 PM

Re: HID access cards security

This comment was originally posted on DCIM Support by Steven Marchetti on 2019-02-07


Hi Mike,

 

Product management responded to me stating:

While 125 kHz cards are still the most commonly used badge access solution, there are known cloning methods, as indicated in the blog you’ve linked. We introduced the NBACS1356 in 2017 so our customers would have access to a 13.56 MHz cards solution, which is more resilient to cloning attempts, in addition to the standard 125 kHz (NBACS125) solution. The NBPD0170 pods currently only support 125 kHz handles but we plan on introducing 13.56MHz in a pod option as well.

(CID:139693295)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 04:49 PM
0 Likes
0
114
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 04:49 PM

Re: HID access cards security

This comment was originally posted on DCIM Support by Andrey Ivashov on 2019-02-11


introducing 13.56MHz in a pod option as well - this is the good news!

The mentioned resource https://www.getkisi.com is very informative.

As I understand the NetBotz 250 13.56MHz and Corporate 1000 (HID) is the best choice considering security by the moment.

 Recently I was looking for the cards that support both 135KHz and 13.56MHz in a single form-factor. Found several proposals locally and with international shipping. They can clone almost everything and it's the whole industry problem not NetBotz. A good point that my customer now uses a single badge to access "old" and "new" racks.

(CID:139694349)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 04:49 PM
0 Likes
0
114
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 04:49 PM

🔒 Closed

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Share
Top Experts
User Count
APC_Steve
Lt. Commander APC_Steve Lt. Commander
2
GavanOB
Lieutenant GavanOB Lieutenant
1
lasalle_1
Crewman lasalle_1
1
Jef
Commander Jef Commander
1
tjlaw
Lieutenant JG tjlaw Lieutenant JG
1
See More Top Experts
Find a Service Provider
Find a certified partner to help you address your integration, installation, maintenance and project needs.
View all Providers
Support

Have a question? Please contact us with details, and we will respond.

Contact Us
FAQ

Look through existing questions to find popular answers.

Learn More
About

Want to know more about Exchange and its possibilities?

Learn More

Full access is just steps away!

Join Exchange for FREE and get unlimited access to our global community of experts.

Connect with Peers & Experts

Discuss challenges in energy and automation with 30,000+ experts and peers.

Get Support in Our Knowledge Base

Find answers in 10,000+ support articles to help solve your product and business challenges.

Ask Questions. Give Solutions

Find peer based solutions to your questions. Provide answers for fellow community members!

Register today for FREE

Register Now

Already have an account?Log in

About Us FAQ Terms & Conditions Privacy Notice Change your cookie settings
©2020, Schneider Electric