Hello,
Is there possibility to install a start button for a generator into a DCE?
It should be something like door handle command on Netbotz 250 & I am acctualy thinking of conecting generator instead of the door handle 😀
(CID:135433378)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 02:05 PM
This answer was originally posted on DCIM Support by Cory McDonald on 2018-11-15
Hello Boris,
Sorry, that is not currently possible. The only things that Data Center Expert can control are NetBotz Rack Access and APC Switched Rack PDU Outlets.
Kind Regards,
Cory
(CID:135433423)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 02:05 PM
This answer was originally posted on DCIM Support by Cory McDonald on 2018-11-15
Hello Boris,
Sorry, that is not currently possible. The only things that Data Center Expert can control are NetBotz Rack Access and APC Switched Rack PDU Outlets.
Kind Regards,
Cory
(CID:135433423)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 02:05 PM
This comment was originally posted on DCIM Support by Boris Majdandzic on 2018-11-15
Hi Cory,
Is it possible to control dry contacts on Netbotz??? I can use them to send command to a generator.
(CID:135433450)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 02:05 PM
This comment was originally posted on DCIM Support by Boris Majdandzic on 2018-11-15
Maybe to send this as feature request.
(CID:135433451)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 02:06 PM
This comment was originally posted on DCIM Support by Cory McDonald on 2018-11-15
You can submit feature requests under: Resources Menu > Feature Requests.
The NetBotz 250 has a relay that you can control via it's web interface. Note that this will not be able to be done through Data Center Expert. It must be done via the web interface of the NetBotz 250.
I am not aware if it has been tested or not, but the following design may also affect the NetBotz 250:
http://www.apc.com/us/en/faqs/FA158337/
Kind Regards,
Cory
(CID:135433477)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 02:06 PM
This comment was originally posted on DCIM Support by Boris Majdandzic on 2018-11-15
OK, thanks for the info.
(CID:135433483)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 02:06 PM . Last Modified: 2023-10-22 02:07 AM