Hi Everyone:
By customer requirement we need to deploy GVX, enabled for 18 programmable dry contact. As I understand it is ready for 12 total (6 configurable). I know there is AP9810 for dry contact.
Could you give us a clue to get 18 total configurable, maybe a kind of hub to extend dry contact numbers.
Thank you in advance.
Solved! Go to Solution.
Hi,
Just sharing my thoughts:
1. 2 optional NMC + AP9810 and IO relay from UPS's IO Cabinet (6 programmable).
- Not sure if can support 2 x NMC with 2x AP9810?
2. Get a Modbus controller with programmable output relay. Modbus controller will poll the data from UPS and trigger 18 output relays.
BR,
TJ
Hi,
Just sharing my thoughts:
1. 2 optional NMC + AP9810 and IO relay from UPS's IO Cabinet (6 programmable).
- Not sure if can support 2 x NMC with 2x AP9810?
2. Get a Modbus controller with programmable output relay. Modbus controller will poll the data from UPS and trigger 18 output relays.
BR,
TJ