  • Galaxy VS web management page through DCE launch to device
Community Menu
  • Forums
    • By Topic
        • EcoStruxure IT
          • EcoStruxure IT forum
        • Industrial Automation
          • Industry Automation and Control Forum
          • Alliance System Integrators Forum
          • Machine Solutions in the Digital Transformation
          • EcoStruxure Automation Expert / IEC 61499 Forum
          • Industrial Edge Computing Forum
          • Level and Pressure Instrumentation Forum
          • Modicon User Group
          • PLC Club Indonesia
          • SEE Automation Club Forum
          • Fabrika ve Makina Otomasyonu Çözümleri
          • Форум по промышленной автоматизации СНГ
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Forum
          • SCADA and Telemetry Devices Forum
        • Power Distribution IEC
          • Power Distribution and Digital
          • Power Standards & Regulations
          • Paneelbouw & Energie Distributie
        • Power Distribution Softwares
          • EcoStruxure Power Design Forum
          • SEE Electrical Building+ Forum
          • LayoutFAST User Group Forum
        • Solutions for your Business
          • Solutions for Food & Beverage Forum
          • Solutions for Healthcare Forum
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Forum
        • Healthcare
          • Solutions for Healthcare Forum
      • EcoStruxure IT
        • EcoStruxure IT forum
      • Industrial Automation
        • Industry Automation and Control Forum
        • Alliance System Integrators Forum
        • Machine Solutions in the Digital Transformation
        • EcoStruxure Automation Expert / IEC 61499 Forum
        • Industrial Edge Computing Forum
        • Level and Pressure Instrumentation Forum
        • Modicon User Group
        • PLC Club Indonesia
        • SEE Automation Club Forum
        • Fabrika ve Makina Otomasyonu Çözümleri
        • Форум по промышленной автоматизации СНГ
      • SCADA & Telemetry Solutions
        • Geo SCADA Expert Forum
        • SCADA and Telemetry Devices Forum
      • Power Distribution IEC
        • Power Distribution and Digital
        • Power Standards & Regulations
        • Paneelbouw & Energie Distributie
      • Power Distribution Softwares
        • EcoStruxure Power Design Forum
        • SEE Electrical Building+ Forum
        • LayoutFAST User Group Forum
      • Solutions for your Business
        • Solutions for Food & Beverage Forum
        • Solutions for Healthcare Forum
      • Food & Beverage
        • Solutions for Food & Beverage Forum
      • Healthcare
        • Solutions for Healthcare Forum
  • Blogs
    • By Topic
        • Industrial Automation
          • Industrial Edge Computing Blog
          • Industry 4.0 Blog
          • Industrie du Futur France
        • SCADA & Telemetry Solutions
          • SCADA and Telemetry Blog
        • Power Distribution IEC
          • Power Events & Webinars
          • Power Foundations Blog
        • Power Distribution NEMA
          • NEMA Power Foundations Blog
        • Power Distribution Softwares
          • EcoStruxure Power Design Blog
          • SEE Electrical Building+ Blog
        • Solutions for your Business
          • Solutions for Food & Beverage Blog
          • Solutions for Healthcare Blog
          • Solutions for Retail Blog
        • Community experts & publishers
          • Publishers Community
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Blog
        • Healthcare
          • Solutions for Healthcare Blog
        • Retail
          • Solutions for Retail Blog
      • Industrial Automation
        • Industrial Edge Computing Blog
        • Industry 4.0 Blog
        • Industrie du Futur France
      • SCADA & Telemetry Solutions
        • SCADA and Telemetry Blog
      • Power Distribution IEC
        • Power Events & Webinars
        • Power Foundations Blog
      • Power Distribution NEMA
        • NEMA Power Foundations Blog
      • Power Distribution Softwares
        • EcoStruxure Power Design Blog
        • SEE Electrical Building+ Blog
      • Solutions for your Business
        • Solutions for Food & Beverage Blog
        • Solutions for Healthcare Blog
        • Solutions for Retail Blog
      • Community experts & publishers
        • Publishers Community
      • Food & Beverage
        • Solutions for Food & Beverage Blog
      • Healthcare
        • Solutions for Healthcare Blog
      • Retail
        • Solutions for Retail Blog
  • Ideas
        • Industrial Automation
          • Modicon Ideas & new features
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Ideas
          • SCADA and Telemetry Devices Ideas
  • Knowledge Center
    • Building Automation Knowledge Base
    • Industrial Automation How-to videos
    • Ask Exchange
    • Digital E-books
    • Success Stories Corner
    • Power Talks
  • Events & Webinars
  • Support
    • User Guide
    • Leaderboard
    • Releases Notes
How can we help?
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
49299members
Join Now
242527posts
Join Now

Galaxy VS web management page through DCE launch to device

Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Solved Go to Solution
Back to EcoStruxure IT forum
Solved
Gabi
Crewman Gabi
Crewman
‎2020-12-03 04:36 AM
1 Like
5
246
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-12-03 04:36 AM

Galaxy VS web management page through DCE launch to device

Hello,

 

I have a problem when I`m trying to open web management for Galaxy VS with nmc4 card and 6.33.3 firmware 

-connected behind DCE in private network I can access web page 

-from DCE I can monitor through snmp(I see all equipment details)

-from DCE client with launch to device option,see schnieder logo like system log in and after 1 sec the page is refreshing and shows login page(if I`m trying to authentficate I`m receiveing the error cannot connect try again later)

 

also tested with the generated link address on several browsers.....the same

(network settings on manual with valid gateway)

anybody knows something about this problem?

 

Thanks

Solved! Go to Solution.

Labels
  • Data Center Expert
Tags (1)
  • Tags:
  • english
Share
Reply

Accepted Solutions
Shaun
Ensign Shaun Ensign
Ensign
‎2020-12-03 04:43 AM
1 Like
4
243
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-12-03 04:43 AM

Re: Galaxy VS web management page through DCE launch to device

Hi @Gabi,

 

This is a known issue we're working to address in a future DCE release.  For now, the best workaround I've found is to avail of the SOCKS proxy functionality available in the DCE (in Server Administration Settings -> Server Access).

 

It's not as seamless as the Launch to Device functionality, but the only way I've found to restore that is to move the device to the public side of the DCE.  Of course, we're working to improve this in the future.

 

See Answer In Context

Tags (1)
  • Tags:
  • english
Share
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
5 Replies 5
Shaun
Ensign Shaun Ensign
Ensign
‎2020-12-03 04:43 AM
1 Like
4
244
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-12-03 04:43 AM

Re: Galaxy VS web management page through DCE launch to device

Hi @Gabi,

 

This is a known issue we're working to address in a future DCE release.  For now, the best workaround I've found is to avail of the SOCKS proxy functionality available in the DCE (in Server Administration Settings -> Server Access).

 

It's not as seamless as the Launch to Device functionality, but the only way I've found to restore that is to move the device to the public side of the DCE.  Of course, we're working to improve this in the future.

 

See Answer In Context

Tags (1)
  • Tags:
  • english
Share
Reply
Gabi
Crewman Gabi
Crewman
‎2020-12-04 12:12 AM
0 Likes
0
216
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-12-04 12:12 AM

Re: Galaxy VS web management page through DCE launch to device

Hi Shaun,

Thanks for answer…..For this client is not a solution to expose equipment in the public interface because of the security policy

 

I hope this will be fixed in the new release of DCE.....even if will take couple of month until is available

Tags (1)
  • Tags:
  • english
Share
Reply
Joann
Joann
Cadet
‎2020-12-13 09:59 PM
0 Likes
2
122
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-12-13 09:59 PM

Re: Galaxy VS web management page through DCE launch to device

 Thanks for the update and quick reply. I'll be sure to keep an eye on this thread. Looking for the same issue. Bumped into your thread. Thanks for creating it. Looking forward for solution.

mygreatlakes
Tags (1)
  • Tags:
  • english
Share
Reply
Gabi
Crewman Gabi
Crewman
7 hours ago
0 Likes
1
7
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
7 hours ago

Re: Galaxy VS web management page through DCE launch to device

up

 

seems like DCE 7.8.1 does not come with the fix for NMC4

from release paper is fixing something regarding NMC2

 

does anyone tested this?

Tags (1)
  • Tags:
  • english
Share
Reply
Shaun
Ensign Shaun Ensign
Ensign
7 hours ago
0 Likes
0
5
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
7 hours ago

Re: Galaxy VS web management page through DCE launch to device

Hi @Gabi,

 

This is correct - this fix isn't in 7.8.1.  I don't want to get into too much detail, but it's not an oversight, there's a technical limitation that needs to be overcome first.

 

I'm hoping (but not promising!) we'll see it in 7.9.0 or 7.9.1, as this should remove the limitation that's currently blocking.  But as always, it'll come down to time vs priorities, and 7.9.x is a very busy roadmap.

Tags (1)
  • Tags:
  • english
Share
Reply
Top Experts
User Count
APC_Steve
Lt. Commander APC_Steve Lt. Commander
2
MateFekete
Crewman MateFekete
1
GavanOB
Lieutenant GavanOB Lieutenant
1
lasalle_1
Crewman lasalle_1
1
Jef
Commander Jef Commander
1
See More Top Experts
Find a Service Provider
Find a certified partner to help you address your integration, installation, maintenance and project needs.
View all Providers
Support

Have a question? Please contact us with details, and we will respond.

Contact Us
FAQ

Look through existing questions to find popular answers.

Learn More
About

Want to know more about Exchange and its possibilities?

Learn More

Full access is just steps away!

Join Exchange for FREE and get unlimited access to our global community of experts.

Connect with Peers & Experts

Discuss challenges in energy and automation with 30,000+ experts and peers.

Get Support in Our Knowledge Base

Find answers in 10,000+ support articles to help solve your product and business challenges.

Ask Questions. Give Solutions

Find peer based solutions to your questions. Provide answers for fellow community members!

Register today for FREE

Register Now

Already have an account?Log in

About Us FAQ Terms & Conditions Privacy Notice Change your cookie settings
©2020, Schneider Electric