Sign In Help
Schneider Electric
HelpSign In
Schneider Electric Exchange
  • Home
  • Collaborate
  • Develop
  • Shop
Home Collaborate Develop Shop Log in or Register Help

Invite a Co-worker

Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel

Invitation Sent

Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
  • Home
  • Collaborate
  • Exchange Community
  • :
  • EcoStruxure IT
  • :
  • EcoStruxure IT forum
  • :
  • Email from address now shows unknown after 4.6.3 update on 550 and 570
Community Menu
  • Forums
    • By Topic
        • EcoStruxure IT
          • EcoStruxure IT forum
        • Industrial Automation
          • Industry Automation and Control Forum
          • Alliance System Integrators Forum
          • Machine Solutions in the Digital Transformation
          • EcoStruxure Automation Expert / IEC 61499 Forum
          • Industrial Edge Computing Forum
          • Level and Pressure Instrumentation Forum
          • Modicon User Group
          • PLC Club Indonesia
          • SEE Automation Club Forum
          • Fabrika ve Makina Otomasyonu Çözümleri
          • Форум по промышленной автоматизации СНГ
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Forum
          • SCADA and Telemetry Devices Forum
        • Power Distribution IEC
          • Power Distribution and Digital
          • Power Standards & Regulations
          • Paneelbouw & Energie Distributie
        • Power Distribution Softwares
          • EcoStruxure Power Design Forum
          • SEE Electrical Building+ Forum
          • LayoutFAST User Group Forum
        • Wireless Information Network Solutions
          • Instrument Area Network
          • Remote Monitoring
          • Tank Level Monitoring
          • Remote Data Collection
        • Solutions for your Business
          • Solutions for Food & Beverage Forum
          • Solutions for Healthcare Forum
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Forum
        • Healthcare
          • Solutions for Healthcare Forum
      • EcoStruxure IT
        • EcoStruxure IT forum
      • Industrial Automation
        • Industry Automation and Control Forum
        • Alliance System Integrators Forum
        • Machine Solutions in the Digital Transformation
        • EcoStruxure Automation Expert / IEC 61499 Forum
        • Industrial Edge Computing Forum
        • Level and Pressure Instrumentation Forum
        • Modicon User Group
        • PLC Club Indonesia
        • SEE Automation Club Forum
        • Fabrika ve Makina Otomasyonu Çözümleri
        • Форум по промышленной автоматизации СНГ
      • SCADA & Telemetry Solutions
        • Geo SCADA Expert Forum
        • SCADA and Telemetry Devices Forum
      • Power Distribution IEC
        • Power Distribution and Digital
        • Power Standards & Regulations
        • Paneelbouw & Energie Distributie
      • Power Distribution Softwares
        • EcoStruxure Power Design Forum
        • SEE Electrical Building+ Forum
        • LayoutFAST User Group Forum
      • Wireless Information Network Solutions
        • Instrument Area Network
        • Remote Monitoring
        • Tank Level Monitoring
        • Remote Data Collection
      • Solutions for your Business
        • Solutions for Food & Beverage Forum
        • Solutions for Healthcare Forum
      • Food & Beverage
        • Solutions for Food & Beverage Forum
      • Healthcare
        • Solutions for Healthcare Forum
  • Blogs
    • By Topic
        • Industrial Automation
          • Industrial Edge Computing Blog
          • Industry 4.0 Blog
          • Industrie du Futur France
        • SCADA & Telemetry Solutions
          • SCADA and Telemetry Blog
        • Power Distribution IEC
          • Power Events & Webinars
          • Power Foundations Blog
        • Power Distribution NEMA
          • NEMA Power Foundations Blog
        • Power Distribution Softwares
          • EcoStruxure Power Design Blog
          • SEE Electrical Building+ Blog
        • Solutions for your Business
          • Solutions for Food & Beverage Blog
          • Solutions for Healthcare Blog
          • Solutions for Retail Blog
        • Community experts & publishers
          • Publishers Community
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Blog
        • Healthcare
          • Solutions for Healthcare Blog
        • Retail
          • Solutions for Retail Blog
      • Industrial Automation
        • Industrial Edge Computing Blog
        • Industry 4.0 Blog
        • Industrie du Futur France
      • SCADA & Telemetry Solutions
        • SCADA and Telemetry Blog
      • Power Distribution IEC
        • Power Events & Webinars
        • Power Foundations Blog
      • Power Distribution NEMA
        • NEMA Power Foundations Blog
      • Power Distribution Softwares
        • EcoStruxure Power Design Blog
        • SEE Electrical Building+ Blog
      • Solutions for your Business
        • Solutions for Food & Beverage Blog
        • Solutions for Healthcare Blog
        • Solutions for Retail Blog
      • Community experts & publishers
        • Publishers Community
      • Food & Beverage
        • Solutions for Food & Beverage Blog
      • Healthcare
        • Solutions for Healthcare Blog
      • Retail
        • Solutions for Retail Blog
  • Ideas
        • Industrial Automation
          • Modicon Ideas & new features
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Ideas
          • SCADA and Telemetry Devices Ideas
  • Knowledge Center
    • Building Automation Knowledge Base
    • Industrial Automation Knowledge Base
    • Industrial Automation How-to videos
    • SCADA & Telemetry Solutions Knowledge Base
    • Digital E-books
    • Success Stories Corner
    • Power Talks
  • Events & Webinars
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Technology Partners
  • Support
    • Ask Exchange
    • Leaderboard
    • Our Community Guidelines
    • Community User Guide
    • How-To & Best Practices
    • More
Join Now
How can we help?
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
50893members
Join Now
244845posts
Join Now

Email from address now shows unknown after 4.6.3 update on 550 and 570

Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Solved Go to Solution
Back to EcoStruxure IT forum
Solved
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 05:09 PM
0 Likes
8
100
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 05:09 PM

Email from address now shows unknown after 4.6.3 update on 550 and 570

This question was originally posted on DCIM Support by Mark Sacharoff on 2019-02-14


After the latest firmware upgrade to 4.6.3 on my 550 and 570 units, I am not seeing the normal "From" address shown here as an example: Main Door <NetBotz_CH-1@xxx.xxx>, I now get "UNKNOWN". Tried changing the email address to something different and I am still getting the same results. Spoke to email admin and he believes that the units are not populating the "From" field correctly. Has anyone else sen this problem before?

 

(CID:140217117)

Solved! Go to Solution.

Labels
  • NetBotz
Tags (1)
  • Tags:
  • bug
Share

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 05:09 PM
0 Likes
3
100
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 05:09 PM

Re: Email from address now shows unknown after 4.6.3 update on 550 and 570

This answer was originally posted on DCIM Support by Steven Marchetti on 2019-02-14


Hi Mark,

 

This is a known issue and will be resolved in version 4.6.4, due out soon. It has been noted in k-base FA365716.

 

Thanks,

Steve

(CID:140217134)

See Answer In Context

Share
  • All forum topics
  • Previous Topic
  • Next Topic
8 Replies 8
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 05:09 PM
0 Likes
2
100
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 05:09 PM

Re: Email from address now shows unknown after 4.6.3 update on 550 and 570

This answer was originally posted on DCIM Support by Scott Rymeski on 2019-02-14


Hello Mark,

 

This issue was created in the v 4.6.3 release and will be fixed in the next rev - v 4.6.4 - estimated to release within a few months time.

 

-Scott

 

 

(CID:140217127)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 05:09 PM
0 Likes
0
100
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 05:09 PM

Re: Email from address now shows unknown after 4.6.3 update on 550 and 570

This comment was originally posted on DCIM Support by nanoman on 2019-02-14


It would really be great if they could also update sending periodic reports via SFTP  (in addition to, or in place of FTP) in upcoming release.

Just a request/musing.

(CID:140217181)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 05:09 PM
0 Likes
0
100
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 05:09 PM

Re: Email from address now shows unknown after 4.6.3 update on 550 and 570

This comment was originally posted on DCIM Support by Steven Marchetti on 2019-02-14


Hi Nanoman,

This is a different issue so should be discussed on a separate thread... and as discussed in our previous conversation here:

it has already been entered as an enhancement request .

 

Steve

(CID:140217195)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 05:09 PM
0 Likes
3
101
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 05:09 PM

Re: Email from address now shows unknown after 4.6.3 update on 550 and 570

This answer was originally posted on DCIM Support by Steven Marchetti on 2019-02-14


Hi Mark,

 

This is a known issue and will be resolved in version 4.6.4, due out soon. It has been noted in k-base FA365716.

 

Thanks,

Steve

(CID:140217134)

See Answer In Context

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 05:09 PM
0 Likes
0
100
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 05:09 PM

Re: Email from address now shows unknown after 4.6.3 update on 550 and 570

This comment was originally posted on DCIM Support by Mark Sacharoff on 2019-02-14


Thank you both for the quick reply. I did not see the k-base FA365716 notes. In that k-base if has a reference to k-base FA367489 to downgrade but the link is broken. Is there a link has the proper instructions to follow so I can downgrade. Need the "From" address working since we have the alerts going to specific folders for sorting reasons.

(CID:140217427)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 05:09 PM
0 Likes
0
100
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 05:09 PM

Re: Email from address now shows unknown after 4.6.3 update on 550 and 570

This comment was originally posted on DCIM Support by Steven Marchetti on 2019-02-14


Hi Mark,

 

I'm not sure which link in which FAQ is broken, they all appeared to work for me. The firmware link was to the generic firmware download page so if that's what you were seeing, that was on purpose. It was meant to allow for other firmware versions to be chosen as that second (linked) k-base is not specific to the issue at hand. If you want version 4.6.2, I copied the link below and verifies that I could download the firmware fie:

https://www.apc.com/us/en/tools/download/download.cfm?sw_sku=SFNBZ462&software_id=MFOI-ATYUGT&family...

 

Steve

(CID:140217422)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 05:09 PM
0 Likes
0
100
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 05:09 PM

Re: Email from address now shows unknown after 4.6.3 update on 550 and 570

This comment was originally posted on DCIM Support by Mark Sacharoff on 2019-02-14


Thank you Steve. This link worked and will follow the instructions for downgrading our units on a maintenance window hopefully soon.

(CID:140217429)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 05:09 PM
0 Likes
0
100
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 05:09 PM

🔒 Closed

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Share
Top Experts
User Count
Jef
Commander Jef Commander
40
APC_Steve
Lt. Commander APC_Steve Lt. Commander
23
gsterling
Lt. Commander gsterling Lt. Commander
20
Cory_McDonald
Lieutenant Cory_McDonald Lieutenant
13
GavanOB
Lieutenant GavanOB Lieutenant
7
See More Top Experts
Find a Service Provider
Find a certified partner to help you address your integration, installation, maintenance and project needs.
View all Providers
Support

Have a question? Please contact us with details, and we will respond.

Contact Us
FAQ

Look through existing questions to find popular answers.

Learn More
About

Want to know more about Exchange and its possibilities?

Learn More

Full access is just steps away!

Join Exchange for FREE and get unlimited access to our global community of experts.

Connect with Peers & Experts

Discuss challenges in energy and automation with 30,000+ experts and peers.

Get Support in Our Knowledge Base

Find answers in 10,000+ support articles to help solve your product and business challenges.

Ask Questions. Give Solutions

Find peer based solutions to your questions. Provide answers for fellow community members!

Register today for FREE

Register Now

Already have an account?Log in

About Us FAQ Terms & Conditions Privacy Notice Change your cookie settings
©2020, Schneider Electric