Hi all, We typically go through proxy... but if we choose to setup IT Gateway to send data to the could directly, is there a list of host names we would use? for getting firewalls opened up, etc.
(CID:131963302)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 05:53 PM . Last Modified: 2 weeks ago
Dear Wes Burhoe,
The answer to your question can be found on page https://ecostruxureit.com/system-requirements/:
Firewall
- Port 443 TCP outbound
- To connect using static IPs, add 40.84.62.190 and 23.99.90.28
If you have any further questions, please ask.
With respect.
(CID:131963320)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 05:53 PM . Last Modified: 2 weeks ago
Dear Wes Burhoe,
The answer to your question can be found on page https://ecostruxureit.com/system-requirements/:
Firewall
- Port 443 TCP outbound
- To connect using static IPs, add 40.84.62.190 and 23.99.90.28
If you have any further questions, please ask.
With respect.
(CID:131963320)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 05:53 PM . Last Modified: 2023-10-22 02:00 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.