Sign In Help
Schneider Electric
HelpSign In
Schneider Electric Exchange
  • Home
  • Collaborate
  • Develop
  • Shop
Home Collaborate Develop Shop Log in or Register Help

Invite a Co-worker

Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel

Invitation Sent

Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
  • Home
  • Collaborate
  • Exchange Community
  • :
  • EcoStruxure IT
  • :
  • EcoStruxure IT forum
  • :
  • ETL export not working in 8.2.7 (Merging)
Community Menu
  • Forums
    • By Topic
        • EcoStruxure IT
          • EcoStruxure IT forum
        • Industrial Automation
          • Industry Automation and Control Forum
          • Alliance System Integrators Forum
          • Machine Solutions in the Digital Transformation
          • EcoStruxure Automation Expert / IEC 61499 Forum
          • Industrial Edge Computing Forum
          • Level and Pressure Instrumentation Forum
          • Modicon User Group
          • PLC Club Indonesia
          • SEE Automation Club Forum
          • Fabrika ve Makina Otomasyonu Çözümleri
          • Форум по промышленной автоматизации СНГ
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Forum
          • SCADA and Telemetry Devices Forum
        • Power Distribution IEC
          • Power Distribution and Digital
          • Power Standards & Regulations
          • Paneelbouw & Energie Distributie
        • Power Distribution Softwares
          • EcoStruxure Power Design Forum
          • SEE Electrical Building+ Forum
          • LayoutFAST User Group Forum
        • Solutions for your Business
          • Solutions for Food & Beverage Forum
          • Solutions for Healthcare Forum
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Forum
        • Healthcare
          • Solutions for Healthcare Forum
      • EcoStruxure IT
        • EcoStruxure IT forum
      • Industrial Automation
        • Industry Automation and Control Forum
        • Alliance System Integrators Forum
        • Machine Solutions in the Digital Transformation
        • EcoStruxure Automation Expert / IEC 61499 Forum
        • Industrial Edge Computing Forum
        • Level and Pressure Instrumentation Forum
        • Modicon User Group
        • PLC Club Indonesia
        • SEE Automation Club Forum
        • Fabrika ve Makina Otomasyonu Çözümleri
        • Форум по промышленной автоматизации СНГ
      • SCADA & Telemetry Solutions
        • Geo SCADA Expert Forum
        • SCADA and Telemetry Devices Forum
      • Power Distribution IEC
        • Power Distribution and Digital
        • Power Standards & Regulations
        • Paneelbouw & Energie Distributie
      • Power Distribution Softwares
        • EcoStruxure Power Design Forum
        • SEE Electrical Building+ Forum
        • LayoutFAST User Group Forum
      • Solutions for your Business
        • Solutions for Food & Beverage Forum
        • Solutions for Healthcare Forum
      • Food & Beverage
        • Solutions for Food & Beverage Forum
      • Healthcare
        • Solutions for Healthcare Forum
  • Blogs
    • By Topic
        • Industrial Automation
          • Industrial Edge Computing Blog
          • Industry 4.0 Blog
          • Industrie du Futur France
        • SCADA & Telemetry Solutions
          • SCADA and Telemetry Blog
        • Power Distribution IEC
          • Power Events & Webinars
          • Power Foundations Blog
        • Power Distribution NEMA
          • NEMA Power Foundations Blog
        • Power Distribution Softwares
          • EcoStruxure Power Design Blog
          • SEE Electrical Building+ Blog
        • Solutions for your Business
          • Solutions for Food & Beverage Blog
          • Solutions for Healthcare Blog
          • Solutions for Retail Blog
        • Community experts & publishers
          • Publishers Community
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Blog
        • Healthcare
          • Solutions for Healthcare Blog
        • Retail
          • Solutions for Retail Blog
      • Industrial Automation
        • Industrial Edge Computing Blog
        • Industry 4.0 Blog
        • Industrie du Futur France
      • SCADA & Telemetry Solutions
        • SCADA and Telemetry Blog
      • Power Distribution IEC
        • Power Events & Webinars
        • Power Foundations Blog
      • Power Distribution NEMA
        • NEMA Power Foundations Blog
      • Power Distribution Softwares
        • EcoStruxure Power Design Blog
        • SEE Electrical Building+ Blog
      • Solutions for your Business
        • Solutions for Food & Beverage Blog
        • Solutions for Healthcare Blog
        • Solutions for Retail Blog
      • Community experts & publishers
        • Publishers Community
      • Food & Beverage
        • Solutions for Food & Beverage Blog
      • Healthcare
        • Solutions for Healthcare Blog
      • Retail
        • Solutions for Retail Blog
  • Ideas
        • Industrial Automation
          • Modicon Ideas & new features
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Ideas
          • SCADA and Telemetry Devices Ideas
  • Knowledge Center
    • Building Automation Knowledge Base
    • Industrial Automation How-to videos
    • Ask Exchange
    • Digital E-books
    • Success Stories Corner
    • Power Talks
  • Events & Webinars
  • Support
    • User Guide
    • Leaderboard
    • Releases Notes
How can we help?
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
49539members
Join Now
242888posts
Join Now

ETL export not working in 8.2.7 (Merging)

Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Solved Go to Solution
Back to EcoStruxure IT forum
Solved
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 04:36 PM
0 Likes
7
86
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 04:36 PM

ETL export not working in 8.2.7 (Merging)

This question was originally posted on DCIM Support by DataCenterServices on 2019-01-28


After upgrading to 8.2.7 my ETL export database is no longer functioning.

The initial ETL export was successful. The error only appears when merging/updating data. The below is the error received:

 

2019-01-28 10:00:02,769 ERROR [0CGZi4oBRhy0fy8dpYeBAQ] [datacenterservices] [org.pentaho.di] (swoAsset_v2.0.0 - Merge) Merge - Unexpected error
2019-01-28 10:00:02,769 ERROR [0CGZi4oBRhy0fy8dpYeBAQ] [datacenterservices] [org.pentaho.di] (swoAsset_v2.0.0 - Merge) Merge - org.pentaho.di.core.exception.KettleException:
Invalid layout detected in input streams, keys and values to merge have to be of identical structure and be in the same place in the rows

The data type of field #16 is not the same as the first row received: you're mixing rows with different layout. Field [ci_max_power_draw Number(15)] does not have the same data type as field [ci_max_power_draw BigNumber(17, 17)].


at org.pentaho.di.trans.steps.mergerows.MergeRows.processRow(MergeRows.java:92)
at org.pentaho.di.trans.step.RunThread.run(RunThread.java:60)
at java.lang.Thread.run(Thread.java:748)
Caused by: org.pentaho.di.core.exception.KettleRowException:
The data type of field #16 is not the same as the first row received: you're mixing rows with different layout. Field [ci_max_power_draw Number(15)] does not have the same data type as field [ci_max_power_draw BigNumber(17, 17)].

at org.pentaho.di.trans.step.BaseStep.safeModeChecking(BaseStep.java:1861)
at org.pentaho.di.trans.steps.mergerows.MergeRows.checkInputLayoutValid(MergeRows.java:265)
at org.pentaho.di.trans.steps.mergerows.MergeRows.processRow(MergeRows.java:88)
... 2 more

2019-01-28 10:00:02,769 INFO [0CGZi4oBRhy0fy8dpYeBAQ] [datacenterservices] [org.pentaho.di] (swoAsset_v2.0.0 - Merge) Merge - Finished processing (I=0, O=0, R=2, W=0, U=0, E=1)
2019-01-28 10:00:02,769 INFO [0CGZi4oBRhy0fy8dpYeBAQ] [datacenterservices] [org.pentaho.di] (swoAsset_v2.0.0 - Merge) swoAsset_v2.0.0 - swoAsset_v2.0.0
2019-01-28 10:00:02,769 INFO [0CGZi4oBRhy0fy8dpYeBAQ] [datacenterservices] [org.pentaho.di] (swoAsset_v2.0.0 - Merge) swoAsset_v2.0.0 - swoAsset_v2.0.0
2019-01-28 10:00:02,769 ERROR [0CGZi4oBRhy0fy8dpYeBAQ] [datacenterservices] [org.pentaho.di] (QuartzSharedThreadPool-1 M/Mur0csSGqQjTGc1EWLlw) swoAsset_v2.0.0 - Errors detected!
2019-01-28 10:00:02,770 ERROR [0CGZi4oBRhy0fy8dpYeBAQ] [datacenterservices] [org.pentaho.di] (QuartzSharedThreadPool-1 M/Mur0csSGqQjTGc1EWLlw) swoAsset_v2.0.0 - Errors detected!


DCO updated from 8.0.2 to 8.2.7.

Database Driver:  net.sourceforge.jtds.jdbc.Driver

Dialect: org.hibernate.dialect.PostgreSQL94Dialect / SQLServerUnicodeDialect

DB Destination: MS SQL Server 2017

(CID:138810569)

Solved! Go to Solution.

Labels
  • Data Center Operation
Share

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 04:37 PM
0 Likes
2
86
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 04:37 PM

Re: ETL export not working in 8.2.7 (Merging)

This answer was originally posted on DCIM Support by Jef Faridi on 2019-01-29


Hi (DataCenterServices),

This seems to be a known issue, where an ETL export to SQL server may fail after the second transformation.

This issue is fixed in the latest version of DCO (currently 8.2.12),

Kind regards

(CID:138810772)

See Answer In Context

Share
  • All forum topics
  • Previous Topic
  • Next Topic
7 Replies 7
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 04:36 PM
0 Likes
2
86
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 04:36 PM

Re: ETL export not working in 8.2.7 (Merging)

This answer was originally posted on DCIM Support by Ed Tarento on 2019-01-29


I usually see advice to delete the External system, then delete the export DB, then recreate export DB and then the  external system.  That has solved many issue for me in the past.

Cheers

Ed

(CID:138810660)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 04:36 PM
0 Likes
0
86
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 04:36 PM

Re: ETL export not working in 8.2.7 (Merging)

This comment was originally posted on DCIM Support by Greg Sterling on 2019-01-29


Are you by chance exporting to an external ETL database, perhaps a MS-SQL version by chance?

Regards

Greg Sterling

(CID:138810679)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 04:36 PM
0 Likes
0
86
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 04:36 PM

Re: ETL export not working in 8.2.7 (Merging)

This comment was originally posted on DCIM Support by Greg Sterling on 2019-01-29


Yes, sorry. I see you mentioned its an external ETL ms-sql database. There may be a transformation update which can be provided to resolve this issue. I have seen this at least one other customer. I'll ask dev if there's a file which can be shared.

A fix for this should also be in the latest DCO release, 8.2.12.

Regards

Greg Sterling

(CID:138810680)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 04:37 PM
0 Likes
2
87
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 04:37 PM

Re: ETL export not working in 8.2.7 (Merging)

This answer was originally posted on DCIM Support by Jef Faridi on 2019-01-29


Hi (DataCenterServices),

This seems to be a known issue, where an ETL export to SQL server may fail after the second transformation.

This issue is fixed in the latest version of DCO (currently 8.2.12),

Kind regards

(CID:138810772)

See Answer In Context

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 04:37 PM
0 Likes
0
86
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 04:37 PM

Re: ETL export not working in 8.2.7 (Merging)

This comment was originally posted on DCIM Support by DataCenterServices on 2019-01-30


Thanks for the input. Upgrading DCO from 8.2.7 to 8.2.12 resolved the ETL issue. 

 

Best

(CID:138811665)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 04:37 PM
0 Likes
0
86
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 04:37 PM

Re: ETL export not working in 8.2.7 (Merging)

This comment was originally posted on DCIM Support by Jef Faridi on 2019-01-30


Sounds great! many thanks for the update.

Kind regards

(CID:138811667)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 04:37 PM
0 Likes
0
86
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 04:37 PM

🔒 Closed

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Share
Top Experts
User Count
APC_Steve
Lt. Commander APC_Steve Lt. Commander
2
GavanOB
Lieutenant GavanOB Lieutenant
1
lasalle_1
Crewman lasalle_1
1
Jef
Commander Jef Commander
1
tjlaw
Lieutenant JG tjlaw Lieutenant JG
1
See More Top Experts
Find a Service Provider
Find a certified partner to help you address your integration, installation, maintenance and project needs.
View all Providers
Support

Have a question? Please contact us with details, and we will respond.

Contact Us
FAQ

Look through existing questions to find popular answers.

Learn More
About

Want to know more about Exchange and its possibilities?

Learn More

Full access is just steps away!

Join Exchange for FREE and get unlimited access to our global community of experts.

Connect with Peers & Experts

Discuss challenges in energy and automation with 30,000+ experts and peers.

Get Support in Our Knowledge Base

Find answers in 10,000+ support articles to help solve your product and business challenges.

Ask Questions. Give Solutions

Find peer based solutions to your questions. Provide answers for fellow community members!

Register today for FREE

Register Now

Already have an account?Log in

About Us FAQ Terms & Conditions Privacy Notice Change your cookie settings
©2020, Schneider Electric