This question was originally posted on DCIM Support by Krista Flynn on 2019-01-03
Someone suggested that I needed to update the DCE to 7.6, which would give me the most current DDFs. I have updated the DCE to 7.6 and also updated the PDU firmware and I still don't see the kVA sensor.
(CID:137729412)
This answer was originally posted on DCIM Support by Steven Marchetti on 2019-01-03
Hi Krista,
I checked an AP7911B via SNMP using the following OID:
hardware.rPDU2.rPDU2Phase.rPDU2PhaseStatusTable.rPDU2PhaseStatusEntry.rPDU2PhaseStatusVoltage
The return was a -1. This indicates that voltage is not supported by this device. Without voltage, you can not get wattage. The DDF can not calculate it outside of the device as it will do in some instances. The device does support current, but not wattage or voltage.
rPDU2PhaseStatusPower also reports a -1
It simply appears that this device does not support a watt or KW sensor.
Thanks,
Steve
(CID:137729428)
This comment was originally posted on DCIM Support by spezialist on 2019-02-09
Dear Krista Flynn,
Tell us, please, did you solve your question or not?
With respect.
(CID:139693981)
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.