Hi ,
Can some one assist me to understand the dew point sensor value showed on Netbotz camera value with below Humidity & Temperature.
Humidity :40%
Temperature :19.5 ° C
Dew Point : 5.5 ° C
Is this Dew Point value is correct ? Is there a sensor to detect Dew Point or based on Temperature & Humidity Sensor value.
Regards
Shaik Mahboob Ali
(CID:126884616)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 03:04 AM . Last Modified: 2 weeks ago
Dear Shaik,
Please refer our K-base ID: FA158136
https://www.schneider-electric.co.in/en/faqs/FA158136/
Dew-Point Calculations on the NetBotz Appliances
Product Line:
NetBotz
Environment:
NetBotz version 1 and 2
Cause:
Definition: Dew Point is the temperature at which condensations forms
Resolution:
When air comes in contact with a surface that is at or below its Dew Point temperature, condensation will form on that surface.
The following URL explains how the dewpoint is calculated:
http://www.lamtec.com/tb_dew_point_calculator.html
I hope this helps.
Regards,
Bala
(CID:126884620)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 03:04 AM . Last Modified: 2 weeks ago
Dear Shaik,
Please refer our K-base ID: FA158136
https://www.schneider-electric.co.in/en/faqs/FA158136/
Dew-Point Calculations on the NetBotz Appliances
Product Line:
NetBotz
Environment:
NetBotz version 1 and 2
Cause:
Definition: Dew Point is the temperature at which condensations forms
Resolution:
When air comes in contact with a surface that is at or below its Dew Point temperature, condensation will form on that surface.
The following URL explains how the dewpoint is calculated:
http://www.lamtec.com/tb_dew_point_calculator.html
I hope this helps.
Regards,
Bala
(CID:126884620)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 03:05 AM . Last Modified: 2 weeks ago
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 03:05 AM . Last Modified: 2 weeks ago
Try this link..it is working for me.
https://www.lamtec.com/technical-bulletins/dew-point-table/
(CID:126884642)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 03:05 AM . Last Modified: 2023-10-22 01:54 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.