Sign In Help
Schneider Electric
HelpSign In
Schneider Electric Exchange
  • Home
  • Collaborate
  • Develop
  • Shop
Home Collaborate Develop Shop Log in or Register Help

Invite a Co-worker

Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel

Invitation Sent

Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
  • Home
  • Collaborate
  • Exchange Community
  • :
  • EcoStruxure IT
  • :
  • EcoStruxure IT forum
  • :
  • Re: Dce You can now change the IP addresses of discovered nodes without losing data
Community Menu
  • Forums
    • By Topic
        • EcoStruxure IT
          • EcoStruxure IT forum
        • Industrial Automation
          • Industry Automation and Control Forum
          • Alliance System Integrators Forum
          • Machine Solutions in the Digital Transformation
          • EcoStruxure Automation Expert / IEC 61499 Forum
          • Industrial Edge Computing Forum
          • Level and Pressure Instrumentation Forum
          • Modicon User Group
          • PLC Club Indonesia
          • SEE Automation Club Forum
          • Fabrika ve Makina Otomasyonu Çözümleri
          • Форум по промышленной автоматизации СНГ
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Forum
          • SCADA and Telemetry Devices Forum
        • Power Distribution IEC
          • Power Distribution and Digital
          • Power Standards & Regulations
          • Paneelbouw & Energie Distributie
          • Eldistribution & Fastighetsautomation
        • Power Distribution Softwares
          • EcoStruxure Power Design Forum
          • SEE Electrical Building+ Forum
          • LayoutFAST User Group Forum
        • Wireless Information Network Solutions
          • Instrument Area Network
          • Remote Monitoring
          • Tank Level Monitoring
          • Remote Data Collection
        • Solutions for your Business
          • Solutions for Food & Beverage Forum
          • Solutions for Healthcare Forum
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Forum
        • Healthcare
          • Solutions for Healthcare Forum
      • EcoStruxure IT
        • EcoStruxure IT forum
      • Industrial Automation
        • Industry Automation and Control Forum
        • Alliance System Integrators Forum
        • Machine Solutions in the Digital Transformation
        • EcoStruxure Automation Expert / IEC 61499 Forum
        • Industrial Edge Computing Forum
        • Level and Pressure Instrumentation Forum
        • Modicon User Group
        • PLC Club Indonesia
        • SEE Automation Club Forum
        • Fabrika ve Makina Otomasyonu Çözümleri
        • Форум по промышленной автоматизации СНГ
      • SCADA & Telemetry Solutions
        • Geo SCADA Expert Forum
        • SCADA and Telemetry Devices Forum
      • Power Distribution IEC
        • Power Distribution and Digital
        • Power Standards & Regulations
        • Paneelbouw & Energie Distributie
        • Eldistribution & Fastighetsautomation
      • Power Distribution Softwares
        • EcoStruxure Power Design Forum
        • SEE Electrical Building+ Forum
        • LayoutFAST User Group Forum
      • Wireless Information Network Solutions
        • Instrument Area Network
        • Remote Monitoring
        • Tank Level Monitoring
        • Remote Data Collection
      • Solutions for your Business
        • Solutions for Food & Beverage Forum
        • Solutions for Healthcare Forum
      • Food & Beverage
        • Solutions for Food & Beverage Forum
      • Healthcare
        • Solutions for Healthcare Forum
  • Blogs
    • By Topic
        • Industrial Automation
          • Industrial Edge Computing Blog
          • Industry 4.0 Blog
          • Industrie du Futur France
        • SCADA & Telemetry Solutions
          • SCADA and Telemetry Blog
        • Power Distribution IEC
          • Power Events & Webinars
          • Power Foundations Blog
        • Power Distribution NEMA
          • NEMA Power Foundations Blog
        • Power Distribution Softwares
          • EcoStruxure Power Design Blog
          • SEE Electrical Building+ Blog
        • Solutions for your Business
          • Solutions for Food & Beverage Blog
          • Solutions for Healthcare Blog
          • Solutions for Retail Blog
        • Community experts & publishers
          • Publishers Community
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Blog
        • Healthcare
          • Solutions for Healthcare Blog
        • Retail
          • Solutions for Retail Blog
      • Industrial Automation
        • Industrial Edge Computing Blog
        • Industry 4.0 Blog
        • Industrie du Futur France
      • SCADA & Telemetry Solutions
        • SCADA and Telemetry Blog
      • Power Distribution IEC
        • Power Events & Webinars
        • Power Foundations Blog
      • Power Distribution NEMA
        • NEMA Power Foundations Blog
      • Power Distribution Softwares
        • EcoStruxure Power Design Blog
        • SEE Electrical Building+ Blog
      • Solutions for your Business
        • Solutions for Food & Beverage Blog
        • Solutions for Healthcare Blog
        • Solutions for Retail Blog
      • Community experts & publishers
        • Publishers Community
      • Food & Beverage
        • Solutions for Food & Beverage Blog
      • Healthcare
        • Solutions for Healthcare Blog
      • Retail
        • Solutions for Retail Blog
  • Ideas
        • Industrial Automation
          • Modicon Ideas & new features
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Ideas
          • SCADA and Telemetry Devices Ideas
  • Knowledge Center
    • Building Automation Knowledge Base
    • Industrial Automation Knowledge Base
    • Industrial Automation How-to videos
    • SCADA & Telemetry Solutions Knowledge Base
    • Digital E-books
    • Success Stories Corner
    • Power Talks
  • Events & Webinars
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Technology Partners
  • Support
    • Ask Exchange
    • Leaderboard
    • Our Community Guidelines
    • Community User Guide
    • How-To & Best Practices
    • More
Join Now
How can we help?
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
51086members
Join Now
245145posts
Join Now

Dce You can now change the IP addresses of discovered nodes without losing data

Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Solved Go to Solution
Back to EcoStruxure IT forum
Solved
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 01:19 PM
0 Likes
7
160
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 01:19 PM

Dce You can now change the IP addresses of discovered nodes without losing data

This question was originally posted on DCIM Support by Gianluca Bertuletti on 2018-10-24


Hi All

someone can explain how does it work "You can now change the IP addresses of discovered nodes without losing data"

thanks

(CID:134688419)

Solved! Go to Solution.

Labels
  • Data Center Expert
Share

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 01:19 PM
0 Likes
5
160
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 01:19 PM

Re: Dce You can now change the IP addresses of discovered nodes without losing data

This answer was originally posted on DCIM Support by Law TJ on 2018-10-24


Hi, 

Previous version OF DCE, when your device changes ip, you will need to rediscover the device and add into DCE. This 'existing device' will be seen as new device in DCE and you will lost the device data, if you delete the device with its old IP.

For new DCE, you can change your device IP under device settings and the data logging will continue with the new IP. 

Hope this helps. 

(CID:134688524)

See Answer In Context

Share
  • All forum topics
  • Previous Topic
  • Next Topic
7 Replies 7
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 01:19 PM
0 Likes
5
161
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 01:19 PM

Re: Dce You can now change the IP addresses of discovered nodes without losing data

This answer was originally posted on DCIM Support by Law TJ on 2018-10-24


Hi, 

Previous version OF DCE, when your device changes ip, you will need to rediscover the device and add into DCE. This 'existing device' will be seen as new device in DCE and you will lost the device data, if you delete the device with its old IP.

For new DCE, you can change your device IP under device settings and the data logging will continue with the new IP. 

Hope this helps. 

(CID:134688524)

See Answer In Context

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 01:19 PM
0 Likes
0
160
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 01:19 PM

Re: Dce You can now change the IP addresses of discovered nodes without losing data

This comment was originally posted on DCIM Support by Stephen Wellings on 2018-10-24


When did that become an option?  In 7.6.0?

(CID:134688610)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 01:19 PM
0 Likes
0
160
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 01:19 PM

Re: Dce You can now change the IP addresses of discovered nodes without losing data

This comment was originally posted on DCIM Support by Gianluca Bertuletti on 2018-10-24


Hi

if im going to change ip address of a device, i have to discover the new ip and delete the other one. is that correct?

the only thing that remains is history with new Dce.

but i have to re-create all the threshold

(CID:134688634)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 01:20 PM
0 Likes
0
160
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 01:20 PM

Re: Dce You can now change the IP addresses of discovered nodes without losing data

This comment was originally posted on DCIM Support by Steven Marchetti on 2018-10-24


Hi Gianluca,

No, you do not re-discover the device. As Law TJ mentioned, you simply need to change your device IP under device settings. If you delete the device and re-add it or re-add it under the new IP, you will either lose the old data or not be able to sync the old and new data, you'd have 2 devices.

You simply go to the device scan settings and replace the old IP with the new IP:

Each device must be done individually in this dialog box.


Stephen Wellings, yes it is new to 7.6.


Thanks,

Steve



(CID:134688677)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 01:20 PM
0 Likes
0
160
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 01:20 PM

Re: Dce You can now change the IP addresses of discovered nodes without losing data

This comment was originally posted on DCIM Support by Law TJ on 2018-10-24


Thanks Steve for the detailed answer. 

(CID:134688709)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 01:20 PM
0 Likes
0
160
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 01:20 PM

Re: Dce You can now change the IP addresses of discovered nodes without losing data

This comment was originally posted on DCIM Support by Christopherus Laurentius on 2018-10-25


+1 on this very useful feature.

A short video or GIF of that would be great....😉

(CID:134689094)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 01:20 PM
0 Likes
0
160
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 01:20 PM

🔒 Closed

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Share
Top Experts
User Count
Jef
Commander Jef Commander
41
APC_Steve
Lt. Commander APC_Steve Lt. Commander
23
gsterling
Lt. Commander gsterling Lt. Commander
20
Cory_McDonald
Lieutenant Cory_McDonald Lieutenant
13
GavanOB
Lieutenant GavanOB Lieutenant
7
See More Top Experts
Find a Service Provider
Find a certified partner to help you address your integration, installation, maintenance and project needs.
View all Providers
Support

Have a question? Please contact us with details, and we will respond.

Contact Us
FAQ

Look through existing questions to find popular answers.

Learn More
About

Want to know more about Exchange and its possibilities?

Learn More

Full access is just steps away!

Join Exchange for FREE and get unlimited access to our global community of experts.

Connect with Peers & Experts

Discuss challenges in energy and automation with 30,000+ experts and peers.

Get Support in Our Knowledge Base

Find answers in 10,000+ support articles to help solve your product and business challenges.

Ask Questions. Give Solutions

Find peer based solutions to your questions. Provide answers for fellow community members!

Register today for FREE

Register Now

Already have an account?Log in

About Us FAQ Terms & Conditions Privacy Notice Change your cookie settings
©2020, Schneider Electric