Posted: 2020-07-04 06:34 PM
This question was originally posted on DCIM Support by Fady Iskandar on 2018-06-05
Dear I downloaded the free version of the DCE and installed a Netbot 570 device to which I connected a PDO 160 camera, however, within the monitoring software I can see the Netbotz configured but when I go to the surveillance tab I can not see the camera, I understand that the free version allows the monitoring of a camera. Can you help me?
(CID:132648693)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 06:35 PM
This answer was originally posted on DCIM Support by Tim Richard on 2018-06-12
I believe the Surveillance perspective only works if you license it. You can, however, view a NetBotz camera from the Monitoring perspective, by right-clicking the camera pod in the Device View or Map, select View Device Sensors, and clicking the Camera tab. That will give you a live view.
(CID:132651250)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 06:34 PM
This comment was originally posted on DCIM Support by spezialist on 2018-06-06
Dear Fady Iskandar,
Please show a screenshot from the DCE software and APC Advanced View software with your problem. And then you will be helped much faster 😀.
With respect.
(CID:132648836)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 06:35 PM
This comment was originally posted on DCIM Support by Fady Iskandar on 2018-06-06
ok Thanks.
(CID:132649758)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 06:35 PM
This answer was originally posted on DCIM Support by Tim Richard on 2018-06-12
I believe the Surveillance perspective only works if you license it. You can, however, view a NetBotz camera from the Monitoring perspective, by right-clicking the camera pod in the Device View or Map, select View Device Sensors, and clicking the Camera tab. That will give you a live view.
(CID:132651250)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 06:35 PM
This comment was originally posted on DCIM Support by Fady Iskandar on 2018-06-12
Thanks for the help, I already did it and if it works in this way, however, I would like to be able to visualize the camera from the surveillance perspective. Download the free version 7.5.0 of the DCE and have a POD camera license, I do not understand why I can not see it from the perspective of Surveillance
(CID:132659390)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 06:35 PM . Last Modified: 2023-10-22 01:50 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.