Data Center Expert - How to Enable Surveillance for a NetBotz Camera
EcoStruxure IT forum
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
1) Log into the StruxureWare Data Center Expert Client.
2) Ensure that the NetBotz Appliance with the Attached camera is showing within StruxureWare Data Center Expert. If it has not been discovered yet, please reference FA177081.
3) Each NetBotz Camera requires one Surveillance license. You can verify the licensing that you have installed by: System Menu > Server Administration Settings > License Keys. There will be a specific License Type of StruxureWare Data Center Expert Surveillance Pack along with a node count and used node count for that license.
4) Select the Surveillance perspective.
5) Right click on one of the camera thumbnails and select Surveillance Settings. *TIP: You can select multiple thumbnails by CTRL+click or SHIFT+click on the camera images.
6) Mark the check box for License Camera.
7) Enter the StruxureWare Data Center Expert Server's IP address and configure the security, if the appliance was discovered using SSL or if the NetBotz can only communicate using SSL.
😎 Select the Post Mode that you would like to record the Surveillance clips for. There are other options to configure, if deemed necessary.