Follow along for an enriching discussion with our CEO, Peter Herweck, and industry leaders for a captivating Global Keynote at #InnovationSummit Paris 2024. Watch recording and join the #ImpactMaker movement!️
Data Center Expert - Customize Email Notifications
EcoStruxure IT forum
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-0306:21 AM. Last Modified:
2 weeks ago
Data Center Expert - Customize Email Notifications
In order to customize email notifications, you would need to use the Short Message Email Option. Below is a quick how-to guide to creating and customizing a new Short Message Email alert.
1) Open the StruxureWare Data Center Expert client.
2) Alarm Configuration Menu > Manage Alarm Actions.
3) Create...
4) Send Short message Email... > Next.
5) Provide an SMS E-mail Action Name and add in the emails that you would like it to go to.
6) The Subject and message fields can be customized using a defined list of macros that are available:
An example of macro usage with their results is listed below. Text, including spaces within the email will be kept when the information is emailed out.