DDF for APV9601

Highlighted

DDF for APV9601

This question was originally posted on DCIM Support by Evgeny Razdobarov on 2020-01-21


Hi Team!

I'm wondering if there is a DDF for Easy UPS SRV series with SNMP card APV9601?

(CID:153944467)

7 REPLIES 7
Highlighted

Re: DDF for APV9601

This answer was originally posted on DCIM Support by GavOB on 2020-01-21


Hi Evgeny Razdobarov

 

The APV9601 (SNMP card for single phase EasyUPS) does not require a DDF as it uses the generic UPS DDF.

 

-Gavan

(CID:153944503)

Highlighted

Re: DDF for APV9601

This answer was originally posted on DCIM Support by spezialist on 2020-01-21


Dear Evgeny Razdobarov,

According to Mian Aqeel good answer from post :

Found a solution from one of my colleague.

APC Easy UPS Online SNMP Card
 APV9601 
  • Remote monitoring and control of an individual UPS by connecting it directly to the network.

  • Integrates with StruxureWare Data Center Expert :An IT-ready, scalable access monitoring system that collects, organizes, and distributes critical alerts, surveillance video and key information, providing a unified view of complex physical infrastructure environments from anywhere on the network

That is, the latest version of DCE-7.8.0, for example, already has built-in support for this SNMP card: there is no need to import a separate DDF-file.

With respect.

(CID:153944512)

Highlighted

Re: DDF for APV9601

This comment was originally posted on DCIM Support by Evgeny Razdobarov on 2020-01-21


Thanks, it is perfectly clear!

(CID:153944560)

Highlighted

Re: DDF for APV9601

This comment was originally posted on DCIM Support by spezialist on 2020-01-21


Ok, thanks for the good feedback.

(CID:153944572)

Highlighted

Re: DDF for APV9601

This answer was originally posted on DCIM Support by Mian Aqeel on 2020-01-21


Hi @GavOB hope you are good, and found answers above,

Here are some problems i faced during integration and want to share it with you,

(CID:153944674)

Highlighted

Re: DDF for APV9601

This answer was originally posted on DCIM Support by Valentin Kozlov on 2020-01-21


Just leave it here:

Easy UPS 3S SNMP card uses ppc DDF file.

So if your DCE's version is lower than 7.8, you need to go to DDF page and search for "PPC UPSMate UPS" DDF file.

Note: If you are using the latest DA807 SNMP card in your Easy UPS 3S, then please ensure to enable SNMP version 3 on the SNMP card before discovering it in DCE software. SNMP version 1 is not supported in DA807 type card

(CID:153944773)

Highlighted

🔒 Closed

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.