Hi We are using DCO 8.2 with capacity but the measured values from AC units are not been used to give an accurate capacity overview.
TIA
Mike
(CID:132649012)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 06:37 PM . Last Modified: 2 weeks ago
Hi Mike,
The Cooling overlay tooltip will display the calculated data/values (based on the setup). However, the associated sensor values (measured data) can be shown in the rack view, as well as being used for 3D temperature map based on "Measured plane".