EcoStruxure IT forum
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 01:49 AM . Last Modified: 1 week ago
Dear guys,
We have a customer who wants to put the inlet temperature at 10 Celsius degrees and DCO has a limitation in 15,5.
How can we avoid this limitation?
Best regards,
Enric
(CID:105470512)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 01:49 AM . Last Modified: 1 week ago
Hi Enric,
By design, the supply temperature must be between 15.5 and 25 Celsius, that would also be displayed as notification. I don't think we can avoid this limitation, it is hard-coded, but if you wish I can capture a Feature Request for you/customer. Then please send me the customer name by direct email, thanks.
Kind regards
(CID:105470525)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 01:49 AM . Last Modified: 1 week ago
Hi Enric,
By design, the supply temperature must be between 15.5 and 25 Celsius, that would also be displayed as notification. I don't think we can avoid this limitation, it is hard-coded, but if you wish I can capture a Feature Request for you/customer. Then please send me the customer name by direct email, thanks.
Kind regards
(CID:105470525)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 01:49 AM . Last Modified: 2023-10-31 10:49 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.