Sign In Help
Schneider Electric
HelpSign In
Schneider Electric Exchange
  • Home
  • Collaborate
  • Develop
  • Shop
Home Collaborate Develop Shop Log in or Register Help

Invite a Co-worker

Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel

Invitation Sent

Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
  • Home
  • Collaborate
  • Exchange Community
  • :
  • EcoStruxure IT
  • :
  • EcoStruxure IT forum
  • :
  • Re: DCO & DCE - running command in Linux will impact any service?
Community Menu
  • Forums
    • By Topic
        • EcoStruxure IT
          • EcoStruxure IT forum
        • Industrial Automation
          • Industry Automation and Control Forum
          • Alliance System Integrators Forum
          • Machine Solutions in the Digital Transformation
          • EcoStruxure Automation Expert / IEC 61499 Forum
          • Industrial Edge Computing Forum
          • Level and Pressure Instrumentation Forum
          • Modicon User Group
          • PLC Club Indonesia
          • SEE Automation Club Forum
          • Fabrika ve Makina Otomasyonu Çözümleri
          • Форум по промышленной автоматизации СНГ
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Forum
          • SCADA and Telemetry Devices Forum
        • Power Distribution IEC
          • Power Distribution and Digital
          • Power Standards & Regulations
          • Paneelbouw & Energie Distributie
          • Eldistribution & Fastighetsautomation
        • Power Distribution Softwares
          • EcoStruxure Power Design Forum
          • SEE Electrical Building+ Forum
          • LayoutFAST User Group Forum
        • Wireless Information Network Solutions
          • Instrument Area Network
          • Remote Monitoring
          • Tank Level Monitoring
          • Remote Data Collection
        • Solutions for your Business
          • Solutions for Food & Beverage Forum
          • Solutions for Healthcare Forum
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Forum
        • Healthcare
          • Solutions for Healthcare Forum
      • EcoStruxure IT
        • EcoStruxure IT forum
      • Industrial Automation
        • Industry Automation and Control Forum
        • Alliance System Integrators Forum
        • Machine Solutions in the Digital Transformation
        • EcoStruxure Automation Expert / IEC 61499 Forum
        • Industrial Edge Computing Forum
        • Level and Pressure Instrumentation Forum
        • Modicon User Group
        • PLC Club Indonesia
        • SEE Automation Club Forum
        • Fabrika ve Makina Otomasyonu Çözümleri
        • Форум по промышленной автоматизации СНГ
      • SCADA & Telemetry Solutions
        • Geo SCADA Expert Forum
        • SCADA and Telemetry Devices Forum
      • Power Distribution IEC
        • Power Distribution and Digital
        • Power Standards & Regulations
        • Paneelbouw & Energie Distributie
        • Eldistribution & Fastighetsautomation
      • Power Distribution Softwares
        • EcoStruxure Power Design Forum
        • SEE Electrical Building+ Forum
        • LayoutFAST User Group Forum
      • Wireless Information Network Solutions
        • Instrument Area Network
        • Remote Monitoring
        • Tank Level Monitoring
        • Remote Data Collection
      • Solutions for your Business
        • Solutions for Food & Beverage Forum
        • Solutions for Healthcare Forum
      • Food & Beverage
        • Solutions for Food & Beverage Forum
      • Healthcare
        • Solutions for Healthcare Forum
  • Blogs
    • By Topic
        • Industrial Automation
          • Industrial Edge Computing Blog
          • Industry 4.0 Blog
          • Industrie du Futur France
        • SCADA & Telemetry Solutions
          • SCADA and Telemetry Blog
        • Power Distribution IEC
          • Power Events & Webinars
          • Power Foundations Blog
        • Power Distribution NEMA
          • NEMA Power Foundations Blog
        • Power Distribution Softwares
          • EcoStruxure Power Design Blog
          • SEE Electrical Building+ Blog
        • Solutions for your Business
          • Solutions for Food & Beverage Blog
          • Solutions for Healthcare Blog
          • Solutions for Retail Blog
        • Community experts & publishers
          • Publishers Community
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Blog
        • Healthcare
          • Solutions for Healthcare Blog
        • Retail
          • Solutions for Retail Blog
      • Industrial Automation
        • Industrial Edge Computing Blog
        • Industry 4.0 Blog
        • Industrie du Futur France
      • SCADA & Telemetry Solutions
        • SCADA and Telemetry Blog
      • Power Distribution IEC
        • Power Events & Webinars
        • Power Foundations Blog
      • Power Distribution NEMA
        • NEMA Power Foundations Blog
      • Power Distribution Softwares
        • EcoStruxure Power Design Blog
        • SEE Electrical Building+ Blog
      • Solutions for your Business
        • Solutions for Food & Beverage Blog
        • Solutions for Healthcare Blog
        • Solutions for Retail Blog
      • Community experts & publishers
        • Publishers Community
      • Food & Beverage
        • Solutions for Food & Beverage Blog
      • Healthcare
        • Solutions for Healthcare Blog
      • Retail
        • Solutions for Retail Blog
  • Ideas
        • Industrial Automation
          • Modicon Ideas & new features
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Ideas
          • SCADA and Telemetry Devices Ideas
  • Knowledge Center
    • Building Automation Knowledge Base
    • Industrial Automation Knowledge Base
    • Industrial Automation How-to videos
    • SCADA & Telemetry Solutions Knowledge Base
    • Digital E-books
    • Success Stories Corner
    • Power Talks
  • Events & Webinars
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Technology Partners
  • Support
    • Ask Exchange
    • Leaderboard
    • Our Community Guidelines
    • Community User Guide
    • How-To & Best Practices
    • More
Join Now
How can we help?
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
51304members
Join Now
245511posts
Join Now

DCO & DCE - running command in Linux will impact any service?

Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Solved Go to Solution
Back to EcoStruxure IT forum
Solved
Neethi_Pothan
Ensign Neethi_Pothan Ensign
Ensign
‎2020-10-14 04:09 AM
0 Likes
11
1046
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-10-14 04:09 AM

DCO & DCE - running command in Linux will impact any service?

Hi,

 

One of our client has requested for server login credentials to run command on it, as they are integrating DCE & DCO(installed in their server console) with SIM tool(client tool) for collecting Linux/Unix server logs. 

 

Q1. Is it allowed for client to login and perform to run commands for their purpose?

Q2. Would it affect the performance of the DCE & DCO?

Solved! Go to Solution.

Labels
  • Data Center Expert
  • Data Center Operation
  • DCIM Support
Tags (1)
  • Tags:
  • english
Share
Reply

Accepted Solutions
Jef
Commander Jef Commander
Commander
‎2020-10-14 04:31 AM
1 Like
10
1042
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-10-14 04:31 AM

Re: DCO & DCE - running command in Linux will impact any service?

Hi Neethi,

 

For DCE, it is not allowed to access the server.

For DCO (or ITA), it is allowed to access the server, but any additional installations may be the responsibility of the customer. I think it may affect the server performance as well, specially if we are talking about transferring large files (between the systems/servers). Assuming "changes(installations" not affecting the DCO server and its functionality, then demanding jobs such as transferring the large files could be scheduled outside of the normal working hours. Please also note the server may also have its own scheduled jobs (such as daily backups), which should not be interrupted.

Kind regards,

Jef

See Answer In Context

Tags (1)
  • Tags:
  • english
Share
Reply
Jef
Commander Jef Commander
Commander
‎2020-10-15 12:04 AM
0 Likes
6
1003
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-10-15 12:04 AM

Re: DCO & DCE - running command in Linux will impact any service?

Hi Neethi,

It has always been like this that DCE only permits access via desktop client and web/dashboard. All the usual configuration and administrations are designed to be accessible via the desktop client. Logs can be collected from the web interface. This is how it has been designed to work.

Kind regards,

Jef

See Answer In Context

Tags (1)
  • Tags:
  • english
Share
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
11 Replies 11
Jef
Commander Jef Commander
Commander
‎2020-10-14 04:31 AM
1 Like
10
1043
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-10-14 04:31 AM

Re: DCO & DCE - running command in Linux will impact any service?

Hi Neethi,

 

For DCE, it is not allowed to access the server.

For DCO (or ITA), it is allowed to access the server, but any additional installations may be the responsibility of the customer. I think it may affect the server performance as well, specially if we are talking about transferring large files (between the systems/servers). Assuming "changes(installations" not affecting the DCO server and its functionality, then demanding jobs such as transferring the large files could be scheduled outside of the normal working hours. Please also note the server may also have its own scheduled jobs (such as daily backups), which should not be interrupted.

Kind regards,

Jef

See Answer In Context

Tags (1)
  • Tags:
  • english
Share
Reply
Neethi_Pothan
Ensign Neethi_Pothan Ensign
Ensign
‎2020-10-14 04:49 AM
0 Likes
9
1036
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-10-14 04:49 AM

Re: DCO & DCE - running command in Linux will impact any service?

@Jef 

 

Thanks a lot for quick response and support, Jef! 

Tags (1)
  • Tags:
  • english
Share
Reply
Jef
Commander Jef Commander
Commander
‎2020-10-14 04:54 AM
0 Likes
8
1033
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-10-14 04:54 AM

Re: DCO & DCE - running command in Linux will impact any service?

You are most welcome, Neethi

Kind regards,

Jef

Tags (1)
  • Tags:
  • english
Share
Reply
Neethi_Pothan
Ensign Neethi_Pothan Ensign
Ensign
‎2020-10-14 06:47 AM
0 Likes
7
1024
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-10-14 06:47 AM

Re: DCO & DCE - running command in Linux will impact any service?

@Jef 

Jef, Just a quick clarification, and for understanding, May i know the reason why its not allowed to access server? and are there any other solution for customer for running the server for log collection?

Tags (1)
  • Tags:
  • english
Share
Reply
Jef
Commander Jef Commander
Commander
‎2020-10-15 12:04 AM
0 Likes
6
1004
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-10-15 12:04 AM

Re: DCO & DCE - running command in Linux will impact any service?

Hi Neethi,

It has always been like this that DCE only permits access via desktop client and web/dashboard. All the usual configuration and administrations are designed to be accessible via the desktop client. Logs can be collected from the web interface. This is how it has been designed to work.

Kind regards,

Jef

See Answer In Context

Tags (1)
  • Tags:
  • english
Share
Reply
Neethi_Pothan
Ensign Neethi_Pothan Ensign
Ensign
‎2020-10-15 01:55 AM
0 Likes
5
993
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-10-15 01:55 AM

Re: DCO & DCE - running command in Linux will impact any service?

@Jef 

 

Thanks again for the clarification, Jef! 

Tags (1)
  • Tags:
  • english
Share
Reply
Jef
Commander Jef Commander
Commander
‎2020-10-15 01:58 AM
0 Likes
4
991
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-10-15 01:58 AM

Re: DCO & DCE - running command in Linux will impact any service?

You are welcome, Neethi

Kind regards,

Jef

Tags (1)
  • Tags:
  • english
Share
Reply
Neethi_Pothan
Ensign Neethi_Pothan Ensign
Ensign
‎2020-10-21 12:24 PM
0 Likes
3
953
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-10-21 12:24 PM

Re: DCO & DCE - running command in Linux will impact any service?

HI, 

 

DCO server password was able to be reset successfully by following steps from Resetting-user-password-on-the-DCO-server article, but while client gets the below errors while logging in. 

 

Webmin.png

 

During multiple try, it sometimes go to next page and gives below error.

webpage.png

If client access via telnet port 10000, its also showing open.

 

Could you please help on this?

Tags (1)
  • Tags:
  • english
Share
Reply
gsterling
Lt. Commander gsterling Lt. Commander
Lt. Commander
‎2020-10-21 01:00 PM
0 Likes
2
950
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-10-21 01:00 PM

Re: DCO & DCE - running command in Linux will impact any service?

Hello Neethi

 

This is a CentOS installation? You mentioned you reset the user password for DCO, so you reset the root user's password for the DCO server?

 

I assume you are able to successfully logon to the DCO server via SSH using a tool like putty? Direct logon to the CentOS OS as root is not normally allowed unless you overrode that security setting.

 

Assuming this is a CentOS installation, there is usually a separate user account which is defined during installation and used as the administrator. This username should be in the /etc/passwd file near its end ... the name of the user is set by the customer during installation so there's no default username I could suggest you look for.

 

If you find that user, are you able to logon to webmin using that user account?

 

Regards

 

Greg Sterling

Tags (1)
  • Tags:
  • english
Share
Reply
Neethi_Pothan
Ensign Neethi_Pothan Ensign
Ensign
‎2020-11-17 08:59 AM
0 Likes
1
792
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-11-17 08:59 AM

Re: DCO & DCE - running command in Linux will impact any service?

@gsterling Hi Greg,

 

This is CentOS installation. Im attaching the file of screenshots which client has shared during reset and after reset of root password. Please have a look at it.

Meantime, I will check with client to find the user details from  /etc/passwd , which you mentioned in the earlier post. 

 

Please do suggest if you find any solutions from the screenshot.

Attachments
Tags (1)
  • Tags:
  • english
Share
Reply
gsterling
Lt. Commander gsterling Lt. Commander
Lt. Commander
‎2020-11-17 01:34 PM
0 Likes
0
786
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-11-17 01:34 PM

Re: DCO & DCE - running command in Linux will impact any service?

Hello Neethi

 

Please note, in default DCO/ITA installations on CentOS direct logon to the console is not permitted. There is an entry in the sshd_config file which states "PermitRootLogin no" which means root cannot logon to the console.

 

So there should be another user account in your /etc/passwd file which you can use to ssh to your server and then "sudo" to root.

 

On many systems customers add an "apc" user, but it could be anything. I can tell you users "dcoplat", "dcojboss", and "postgres" are reserved for the installer in the passwd file so its not one of those.

 

The userid field for the user is likely 1000 or greater unless it was manually created.

 

Regards

 

Greg Sterling

Tags (1)
  • Tags:
  • english
Share
Reply
Top Experts
User Count
Jef
Commander Jef Commander
41
APC_Steve
Lt. Commander APC_Steve Lt. Commander
24
gsterling
Lt. Commander gsterling Lt. Commander
20
Cory_McDonald
Lieutenant Cory_McDonald Lieutenant
13
GavanOB
Lieutenant GavanOB Lieutenant
7
See More Top Experts
Find a Service Provider
Find a certified partner to help you address your integration, installation, maintenance and project needs.
View all Providers
Support

Have a question? Please contact us with details, and we will respond.

Contact Us
FAQ

Look through existing questions to find popular answers.

Learn More
About

Want to know more about Exchange and its possibilities?

Learn More

Full access is just steps away!

Join Exchange for FREE and get unlimited access to our global community of experts.

Connect with Peers & Experts

Discuss challenges in energy and automation with 30,000+ experts and peers.

Get Support in Our Knowledge Base

Find answers in 10,000+ support articles to help solve your product and business challenges.

Ask Questions. Give Solutions

Find peer based solutions to your questions. Provide answers for fellow community members!

Register today for FREE

Register Now

Already have an account?Log in

About Us FAQ Terms & Conditions Privacy Notice Change your cookie settings
©2020, Schneider Electric