Hello,
I'm using vCenter integration in DCO. I noticed in vCenter event logs are full with the followings:
MGMT\x_apcdcim is the user which has read only in vCenter. But DCO tries to create a custom host value so wants to write something in vCenter. This appears when I do association between DCO entity and ESXi host which is coming from the integration.
What DCO wants to create as a custom value in vCenter and how can I avoid these errors?
(CID:148343237)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 09:50 PM . Last Modified: 2 weeks ago
Hello Mate
The link which describes the permissions required for the vCenter integration is here: Configuring VMware vCenter integration
I have pasted the info below so you don't have to move to the link. Yes. Once the ESXi host is associated to a device in a rack, DCO will attempt to set a couple of custom properties on the host in vCenter which notes the location of the server. This means when you view the host in vCenter you'll see a property which notes which room, rack, and U location the ESXi host resides.
The VMware vCenter user must have permission to these operations:
Far as I know this can not be turned off.
Regards
Greg Sterling
(CID:148343361)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 09:50 PM . Last Modified: 2 weeks ago
Hello Mate
The link which describes the permissions required for the vCenter integration is here: Configuring VMware vCenter integration
I have pasted the info below so you don't have to move to the link. Yes. Once the ESXi host is associated to a device in a rack, DCO will attempt to set a couple of custom properties on the host in vCenter which notes the location of the server. This means when you view the host in vCenter you'll see a property which notes which room, rack, and U location the ESXi host resides.
The VMware vCenter user must have permission to these operations:
Far as I know this can not be turned off.
Regards
Greg Sterling
(CID:148343361)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 09:50 PM . Last Modified: 2023-10-22 01:42 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.