This question was originally posted on DCIM Support by Mate Fekete on 2019-07-11
I have DC version 8.2.12 and using couple UCS Manager integration. I added 2 new systems in External System Configuration which is visible there but not in Unassociated Devices list. See screenshot:
Short explanation for the above: In the left pane you can see in alphabetical order my external systems. -> Unassociated Devices
I went to External System Configuration and sorted in alphabetical order all my external systems and you can see the deviation.
Just for fun I tried to add a new system but it says "System name must be unique". But the system is not listed among Unassociated Devices
As a troubleshooting step I have reset my local cache under /.isxo folder but did not resolve my problem.
(CID:147194440)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 08:36 PM
This comment was originally posted on DCIM Support by Jef Faridi on 2019-07-15
Hi Mate,
Can I ask for a copy of the latest backup file + server logs? so I can take a look.
I will share my =S= box folder with you shortly, thanks
Kind regards
(CID:147195120)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 08:36 PM
This comment was originally posted on DCIM Support by Mate Fekete on 2019-07-18
Hi Jef,
Servers log and latest backup has been uploaded to appbox.
Thanks.
(CID:147196368)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 08:36 PM
This answer was originally posted on DCIM Support by Jef Faridi on 2019-08-06
Hi Mate,
Sorry for the delay - I have studied the provided data set and it seems the integrated external system (PN4-IT-CUCSP009) is added and I could find it in the data base as well, but it is not showing up in "Unassociated Devices" since DCO had not received any data from that server yet.
I would try to re-added it by first removing it from the External Systems Configurations and then adding it and see how it goes. I will also send you a direct message shortly, thanks.
Kind regards
(CID:147202228)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 08:36 PM
This comment was originally posted on DCIM Support by Mate Fekete on 2019-10-09
Hi Jef,
Do you have any update on this problem?
Now I have similar issue like 2 month before: searching for Cisco blade serial numbers DCO doesn't give result, however those are in UCS Manager.
Thanks,
Mate
(CID:149783705)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 08:36 PM
This comment was originally posted on DCIM Support by Jef Faridi on 2019-10-09
Hi Mate,
I think we had already covered this (offline communications) with the conclusion that the external system syncing task was not executed and may needed to be restarted either by rebooting the system or by running the following command "sudo systemctl restart operations".
Kind regards
(CID:149783709)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 08:36 PM
This comment was originally posted on DCIM Support by Mate Fekete on 2019-10-09
Hi Jef,
Yes, we covered but I think it is just a workaround because:
Thanks,
Mate
(CID:149783713)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 08:36 PM
This comment was originally posted on DCIM Support by Jef Faridi on 2019-10-09
Hi Mate,
I do agree, it sounds like a work around. If I recall correctly you were running 8.2.12, if you haven't upgraded yet, would it be possible for you to update and see if that helps, thanks.
Kind regards
(CID:149783789)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 08:36 PM
This comment was originally posted on DCIM Support by Mate Fekete on 2019-10-09
Hi Jef,
I'm keen to update to latest version but straggling with support to get download link.
However I cannot see any UCS related change in the release notes of 8.3.0/8.3.2. Or do you have more info on it?
Regards,
Mate
(CID:149783797)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 08:36 PM
This comment was originally posted on DCIM Support by Jef Faridi on 2019-10-09
Hi Mate,
I don't think there have been specific UCS related changes, but the latest versions usually contains updates. I will contact you directly soon, thanks.
Kind regards
(CID:149783802)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 08:36 PM . Last Modified: 2023-10-22 01:41 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.