Sign In Help
Schneider Electric
HelpSign In
Schneider Electric Exchange
  • Home
  • Collaborate
  • Develop
  • Shop
Home Collaborate Develop Shop Log in or Register Help

Invite a Co-worker

Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel

Invitation Sent

Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
  • Home
  • Collaborate
  • Exchange Community
  • :
  • EcoStruxure IT
  • :
  • EcoStruxure IT forum
  • :
  • Re: DCO SNMP returns value not described in documentation
Community Menu
  • Forums
    • By Topic
        • EcoStruxure IT
          • EcoStruxure IT forum
        • Industrial Automation
          • Industry Automation and Control Forum
          • Alliance System Integrators Forum
          • Machine Solutions in the Digital Transformation
          • EcoStruxure Automation Expert / IEC 61499 Forum
          • Industrial Edge Computing Forum
          • Level and Pressure Instrumentation Forum
          • Modicon User Group
          • PLC Club Indonesia
          • SEE Automation Club Forum
          • Fabrika ve Makina Otomasyonu Çözümleri
          • Форум по промышленной автоматизации СНГ
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Forum
          • SCADA and Telemetry Devices Forum
        • Power Distribution IEC
          • Power Distribution and Digital
          • Power Standards & Regulations
          • Paneelbouw & Energie Distributie
          • Eldistribution & Fastighetsautomation
        • Power Distribution Softwares
          • EcoStruxure Power Design Forum
          • SEE Electrical Building+ Forum
          • LayoutFAST User Group Forum
        • Wireless Information Network Solutions
          • Instrument Area Network
          • Remote Monitoring
          • Tank Level Monitoring
          • Remote Data Collection
        • Solutions for your Business
          • Solutions for Food & Beverage Forum
          • Solutions for Healthcare Forum
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Forum
        • Healthcare
          • Solutions for Healthcare Forum
      • EcoStruxure IT
        • EcoStruxure IT forum
      • Industrial Automation
        • Industry Automation and Control Forum
        • Alliance System Integrators Forum
        • Machine Solutions in the Digital Transformation
        • EcoStruxure Automation Expert / IEC 61499 Forum
        • Industrial Edge Computing Forum
        • Level and Pressure Instrumentation Forum
        • Modicon User Group
        • PLC Club Indonesia
        • SEE Automation Club Forum
        • Fabrika ve Makina Otomasyonu Çözümleri
        • Форум по промышленной автоматизации СНГ
      • SCADA & Telemetry Solutions
        • Geo SCADA Expert Forum
        • SCADA and Telemetry Devices Forum
      • Power Distribution IEC
        • Power Distribution and Digital
        • Power Standards & Regulations
        • Paneelbouw & Energie Distributie
        • Eldistribution & Fastighetsautomation
      • Power Distribution Softwares
        • EcoStruxure Power Design Forum
        • SEE Electrical Building+ Forum
        • LayoutFAST User Group Forum
      • Wireless Information Network Solutions
        • Instrument Area Network
        • Remote Monitoring
        • Tank Level Monitoring
        • Remote Data Collection
      • Solutions for your Business
        • Solutions for Food & Beverage Forum
        • Solutions for Healthcare Forum
      • Food & Beverage
        • Solutions for Food & Beverage Forum
      • Healthcare
        • Solutions for Healthcare Forum
  • Blogs
    • By Topic
        • Industrial Automation
          • Industrial Edge Computing Blog
          • Industry 4.0 Blog
          • Industrie du Futur France
        • SCADA & Telemetry Solutions
          • SCADA and Telemetry Blog
        • Power Distribution IEC
          • Power Events & Webinars
          • Power Foundations Blog
        • Power Distribution NEMA
          • NEMA Power Foundations Blog
        • Power Distribution Softwares
          • EcoStruxure Power Design Blog
          • SEE Electrical Building+ Blog
        • Solutions for your Business
          • Solutions for Food & Beverage Blog
          • Solutions for Healthcare Blog
          • Solutions for Retail Blog
        • Community experts & publishers
          • Publishers Community
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Blog
        • Healthcare
          • Solutions for Healthcare Blog
        • Retail
          • Solutions for Retail Blog
      • Industrial Automation
        • Industrial Edge Computing Blog
        • Industry 4.0 Blog
        • Industrie du Futur France
      • SCADA & Telemetry Solutions
        • SCADA and Telemetry Blog
      • Power Distribution IEC
        • Power Events & Webinars
        • Power Foundations Blog
      • Power Distribution NEMA
        • NEMA Power Foundations Blog
      • Power Distribution Softwares
        • EcoStruxure Power Design Blog
        • SEE Electrical Building+ Blog
      • Solutions for your Business
        • Solutions for Food & Beverage Blog
        • Solutions for Healthcare Blog
        • Solutions for Retail Blog
      • Community experts & publishers
        • Publishers Community
      • Food & Beverage
        • Solutions for Food & Beverage Blog
      • Healthcare
        • Solutions for Healthcare Blog
      • Retail
        • Solutions for Retail Blog
  • Ideas
        • Industrial Automation
          • Modicon Ideas & new features
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Ideas
          • SCADA and Telemetry Devices Ideas
  • Knowledge Center
    • Building Automation Knowledge Base
    • Industrial Automation Knowledge Base
    • Industrial Automation How-to videos
    • SCADA & Telemetry Solutions Knowledge Base
    • Digital E-books
    • Success Stories Corner
    • Power Talks
  • Events & Webinars
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Technology Partners
  • Support
    • Ask Exchange
    • Leaderboard
    • Our Community Guidelines
    • Community User Guide
    • How-To & Best Practices
    • More
Join Now
How can we help?
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
51286members
Join Now
245504posts
Join Now

DCO SNMP returns value not described in documentation

Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Back to EcoStruxure IT forum
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 06:14 PM
0 Likes
14
168
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 06:14 PM

DCO SNMP returns value not described in documentation

This question was originally posted on DCIM Support by Olegas Domanskis on 2019-03-22


Hello

OID 1.3.6.1.4.1.318.1.2.2.1.4.0 returns value 13, but in documentation there is only values from 1 to 5 (https://sxwhelpcenter.ecostruxureit.com/display/public/UADCO8x/DCO+SNMP+status+codes)

What does that value mean? 😀

(CID:141265959)

Labels
  • Data Center Operation
Share
  • All forum topics
  • Previous Topic
  • Next Topic
14 Replies 14
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 06:14 PM
0 Likes
0
168
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 06:14 PM

Re: DCO SNMP returns value not described in documentation

This comment was originally posted on DCIM Support by Ed Tarento on 2019-03-22


Hi

what device is it and what FW version?

(CID:141267498)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 06:14 PM
0 Likes
0
168
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 06:14 PM

Re: DCO SNMP returns value not described in documentation

This comment was originally posted on DCIM Support by Olegas Domanskis on 2019-03-22


It's DCO server itself

StruxureWare Data Center Operation Server: 8.2.12-80089-33a247

(CID:141267500)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 06:14 PM
0 Likes
0
168
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 06:14 PM

Re: DCO SNMP returns value not described in documentation

This comment was originally posted on DCIM Support by Ed Tarento on 2019-03-23


A mystery to me too.

General and essential services (OID .1.3.6.1.4.1.318.1.2.2.1.4.0)

May Jef Faridi can shed some light

(CID:141267502)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 06:15 PM
0 Likes
7
168
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 06:15 PM

Re: DCO SNMP returns value not described in documentation

This answer was originally posted on DCIM Support by Jef Faridi on 2019-03-25


Hi Olegas (& Ed),

DCO only knows those status codes described here: https://sxwhelpcenter.ecostruxureit.com/display/public/UADCO8x/DCO+SNMP+status+codes

and the rest might be specific to ddf.

Kind regards

 

---

 

Update:

Hi Olegas & Andrew,

Both issues, eg OID 1.3.6.1.4.1.318.1.2.2.1.4.0 returning 13 and the mis-notification of DCO in DCE, are related and fixed in the next release version (expected release within a few weeks time)

Thanks

Kind regards

(CID:141266497)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 06:15 PM
0 Likes
0
168
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 06:15 PM

Re: DCO SNMP returns value not described in documentation

This comment was originally posted on DCIM Support by Olegas Domanskis on 2019-03-25


But how we can monitor DCO General and Essential services if it returns unknown code? To what ddf the value is specific?

(CID:141266513)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 06:15 PM
0 Likes
0
168
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 06:15 PM

Re: DCO SNMP returns value not described in documentation

This comment was originally posted on DCIM Support by Jef Faridi on 2019-03-25


Hi Olegas,

I'm currently looking into this - will get back to you soon, thanks,

Kind regards

(CID:141266614)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 06:15 PM
0 Likes
0
168
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 06:15 PM

Re: DCO SNMP returns value not described in documentation

This comment was originally posted on DCIM Support by Jef Faridi on 2019-03-26


Hi Olegas,

Many thanks for the clarification - I was assuming that you were getting 13 different status codes. However, done some investigations and tests, this seems to be a bug that's fixed in the next release version. (release date is not known yet, but expected to be within a few weeks time).

Kind regards

(CID:141267176)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 06:15 PM
0 Likes
0
168
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 06:15 PM

Re: DCO SNMP returns value not described in documentation

This comment was originally posted on DCIM Support by Olegas Domanskis on 2019-03-26


Hello

Thanks. But before the release how can we interpret status 13? As something bad or ignore it?

(CID:141267191)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 06:15 PM
0 Likes
0
168
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 06:15 PM

Re: DCO SNMP returns value not described in documentation

This comment was originally posted on DCIM Support by Jef Faridi on 2019-03-26


Hi Olegas,

In my tests, it reruns 13 both when the application status is running and also when it is down. I would not ignore it, but preferably would check the DCO webmin interface that would display correctly the server status.

Kind regards

(CID:141267198)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 06:15 PM
0 Likes
0
168
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 06:15 PM

Re: DCO SNMP returns value not described in documentation

This comment was originally posted on DCIM Support by Olegas Domanskis on 2019-03-26


you mean these statuses?

(CID:141267210)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 06:15 PM
0 Likes
0
168
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 06:15 PM

Re: DCO SNMP returns value not described in documentation

This comment was originally posted on DCIM Support by Jef Faridi on 2019-03-26


Yes, that's right.

Kind regards

(CID:141267214)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 06:15 PM
0 Likes
0
168
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 06:15 PM

Re: DCO SNMP returns value not described in documentation

This comment was originally posted on DCIM Support by Andrew Stoakes on 2019-03-27


I have the same issue. I have added my DCO server to DCE to monitor but it is always showing in error. The status code that i get is 13 for OID .1.3.6.1.4.1.318.1.2.2.1.4.0 (Status). 

All 3 services are running and showing as "Running" in DCE but the status in the DCE console shows as "Error". 

I also note that the backup status is 13 which is also not a listed value

(CID:141267504)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 06:15 PM
0 Likes
0
168
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 06:15 PM

Re: DCO SNMP returns value not described in documentation

This comment was originally posted on DCIM Support by Jef Faridi on 2019-03-27


Hi Andrew,

The next release of DCO will contain the fix (please see my answer below), thanks.

Kind regards

(CID:141267511)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 06:16 PM
0 Likes
0
168
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 06:16 PM

🔒 Closed

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Share
Top Experts
User Count
Jef
Commander Jef Commander
41
APC_Steve
Lt. Commander APC_Steve Lt. Commander
24
gsterling
Lt. Commander gsterling Lt. Commander
20
Cory_McDonald
Lieutenant Cory_McDonald Lieutenant
13
GavanOB
Lieutenant GavanOB Lieutenant
7
See More Top Experts
Find a Service Provider
Find a certified partner to help you address your integration, installation, maintenance and project needs.
View all Providers
Support

Have a question? Please contact us with details, and we will respond.

Contact Us
FAQ

Look through existing questions to find popular answers.

Learn More
About

Want to know more about Exchange and its possibilities?

Learn More

Full access is just steps away!

Join Exchange for FREE and get unlimited access to our global community of experts.

Connect with Peers & Experts

Discuss challenges in energy and automation with 30,000+ experts and peers.

Get Support in Our Knowledge Base

Find answers in 10,000+ support articles to help solve your product and business challenges.

Ask Questions. Give Solutions

Find peer based solutions to your questions. Provide answers for fellow community members!

Register today for FREE

Register Now

Already have an account?Log in

About Us FAQ Terms & Conditions Privacy Notice Change your cookie settings
©2020, Schneider Electric