This question was originally posted on DCIM Support by Ed Tarento on 2016-08-15
Is there a way to "pause" DCO polling an individual DCE external system whilst retaining the device associations?
DCO 7.5 and DCO 8
(CID:107448062)
This answer was originally posted on DCIM Support by Jef Faridi on 2016-08-16
Hi Ed,
There is no supported feature to pause DCO polling for an individual DCE external system, but as a sort of work-around you might want to try to set the polling intervals as high as possible and the timeouts as low as possible (in the external systems configurations). You might also want to try disabling the "Retrieve sensors", that would disable retrieving humidity and temperature sensors (but not the power data).
Kind regards
(CID:107448228)
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.