Hi,
I am running the latest DCO and found that not all cabinets are showing bar graphs on web interface power layer. Here is screenshot:
Only one rack shows bar graph (yellow:estimated, green: theoretical peak) and all the rest just numeric value (theoretical peak).
I tested with Chrome, Firefox, IE and Edge as well but the result is the same.
How can I see bar graphs on each rack?
(CID:137731791)
This answer was originally posted on DCIM Support by Greg Sterling on 2019-01-11
Hello Mate
Try setting a design limit on the racks in the room. This will cause the power overlay to appear in the web client.
To set the design limit, from the dco desktop client go to the power properties view of the rack and place a value in the design limit field like in the example I pasted below.
Design limit values can also be assigned using the multi-edit feature of the equipment browser.
Regards
Greg Sterling
(CID:137732501)
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.