This question was originally posted on DCIM Support by Jimmy Leung on 2019-07-16
After I identify higher than expected peak power display in the branch circuit in PDU, I have changed the trending setting to its lowest value which is 2 days. However, after 2 days or even 1 week, the same expected peak is still displayed even though the DCE history the peak is much less than what is displayed.
Is there a way to flush the history and start again ? or there is another setting controlling this peak value displayed?
(CID:147195408)
This answer was originally posted on DCIM Support by Jef Faridi on 2019-07-16
Hi Jimmy,
Power info (peak and avg.) displayed in DCO are the result of power data calculations over the user defined period (default 30 days). This time period (7 days is the minimum) can be modified in DCO desktop client by editing the integrated DCE in System Setup > External Systems Configuration (https://sxwhelpcenter.ecostruxureit.com/display/UADCO8x/Configuring+StruxureWare+Data+Center+Expert+...).
Kind regards
(CID:147195612)
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.