Sign In Help
Schneider Electric
HelpSign In
Schneider Electric Exchange
  • Home
  • Collaborate
  • Develop
  • Shop
Home Collaborate Develop Shop Log in or Register Help

Invite a Co-worker

Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel

Invitation Sent

Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
  • Home
  • Collaborate
  • Exchange Community
  • :
  • EcoStruxure IT
  • :
  • EcoStruxure IT forum
  • :
  • Re: DCO DR node - frequency for synchronisation job
Community Menu
  • Forums
    • By Topic
        • EcoStruxure IT
          • EcoStruxure IT forum
        • Industrial Automation
          • Industry Automation and Control Forum
          • Alliance System Integrators Forum
          • Machine Solutions in the Digital Transformation
          • EcoStruxure Automation Expert / IEC 61499 Forum
          • Industrial Edge Computing Forum
          • Level and Pressure Instrumentation Forum
          • Modicon User Group
          • PLC Club Indonesia
          • SEE Automation Club Forum
          • Fabrika ve Makina Otomasyonu Çözümleri
          • Форум по промышленной автоматизации СНГ
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Forum
          • SCADA and Telemetry Devices Forum
        • Power Distribution IEC
          • Power Distribution and Digital
          • Power Standards & Regulations
          • Paneelbouw & Energie Distributie
        • Power Distribution Softwares
          • EcoStruxure Power Design Forum
          • SEE Electrical Building+ Forum
          • LayoutFAST User Group Forum
        • Wireless Information Network Solutions
          • Instrument Area Network
          • Remote Monitoring
          • Tank Level Monitoring
          • Remote Data Collection
        • Solutions for your Business
          • Solutions for Food & Beverage Forum
          • Solutions for Healthcare Forum
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Forum
        • Healthcare
          • Solutions for Healthcare Forum
      • EcoStruxure IT
        • EcoStruxure IT forum
      • Industrial Automation
        • Industry Automation and Control Forum
        • Alliance System Integrators Forum
        • Machine Solutions in the Digital Transformation
        • EcoStruxure Automation Expert / IEC 61499 Forum
        • Industrial Edge Computing Forum
        • Level and Pressure Instrumentation Forum
        • Modicon User Group
        • PLC Club Indonesia
        • SEE Automation Club Forum
        • Fabrika ve Makina Otomasyonu Çözümleri
        • Форум по промышленной автоматизации СНГ
      • SCADA & Telemetry Solutions
        • Geo SCADA Expert Forum
        • SCADA and Telemetry Devices Forum
      • Power Distribution IEC
        • Power Distribution and Digital
        • Power Standards & Regulations
        • Paneelbouw & Energie Distributie
      • Power Distribution Softwares
        • EcoStruxure Power Design Forum
        • SEE Electrical Building+ Forum
        • LayoutFAST User Group Forum
      • Wireless Information Network Solutions
        • Instrument Area Network
        • Remote Monitoring
        • Tank Level Monitoring
        • Remote Data Collection
      • Solutions for your Business
        • Solutions for Food & Beverage Forum
        • Solutions for Healthcare Forum
      • Food & Beverage
        • Solutions for Food & Beverage Forum
      • Healthcare
        • Solutions for Healthcare Forum
  • Blogs
    • By Topic
        • Industrial Automation
          • Industrial Edge Computing Blog
          • Industry 4.0 Blog
          • Industrie du Futur France
        • SCADA & Telemetry Solutions
          • SCADA and Telemetry Blog
        • Power Distribution IEC
          • Power Events & Webinars
          • Power Foundations Blog
        • Power Distribution NEMA
          • NEMA Power Foundations Blog
        • Power Distribution Softwares
          • EcoStruxure Power Design Blog
          • SEE Electrical Building+ Blog
        • Solutions for your Business
          • Solutions for Food & Beverage Blog
          • Solutions for Healthcare Blog
          • Solutions for Retail Blog
        • Community experts & publishers
          • Publishers Community
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Blog
        • Healthcare
          • Solutions for Healthcare Blog
        • Retail
          • Solutions for Retail Blog
      • Industrial Automation
        • Industrial Edge Computing Blog
        • Industry 4.0 Blog
        • Industrie du Futur France
      • SCADA & Telemetry Solutions
        • SCADA and Telemetry Blog
      • Power Distribution IEC
        • Power Events & Webinars
        • Power Foundations Blog
      • Power Distribution NEMA
        • NEMA Power Foundations Blog
      • Power Distribution Softwares
        • EcoStruxure Power Design Blog
        • SEE Electrical Building+ Blog
      • Solutions for your Business
        • Solutions for Food & Beverage Blog
        • Solutions for Healthcare Blog
        • Solutions for Retail Blog
      • Community experts & publishers
        • Publishers Community
      • Food & Beverage
        • Solutions for Food & Beverage Blog
      • Healthcare
        • Solutions for Healthcare Blog
      • Retail
        • Solutions for Retail Blog
  • Ideas
        • Industrial Automation
          • Modicon Ideas & new features
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Ideas
          • SCADA and Telemetry Devices Ideas
  • Knowledge Center
    • Building Automation Knowledge Base
    • Industrial Automation Knowledge Base
    • Industrial Automation How-to videos
    • SCADA & Telemetry Solutions Knowledge Base
    • Digital E-books
    • Success Stories Corner
    • Power Talks
  • Events & Webinars
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Technology Partners
  • Support
    • Ask Exchange
    • Leaderboard
    • Our Community Guidelines
    • Community User Guide
    • How-To & Best Practices
    • More
Join Now
How can we help?
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
50955members
Join Now
244990posts
Join Now

DCO DR node - frequency for synchronisation job

Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Back to EcoStruxure IT forum
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 11:17 PM
0 Likes
9
140
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 11:17 PM

DCO DR node - frequency for synchronisation job

This question was originally posted on DCIM Support by Lukasz Staciwo on 2019-11-06


Hi Team,

Could you please advise what is the frequency for the DCO DR node updates?
Once the DCO DR node has been attached to the main DCO server the sftp connection is established...how often will the transfer between the two happen?

Trying to establish the maximum expected data loss for the DR scenario.

For example:
If the synchronisation happens every 15min and it takes between 5-15 minutes to complete than in a worst case scenario we could expect that 30minutes worth of changes done by the DCO users will not be available in an event of the PROD DCO failing...

(CID:151063079)

Labels
  • Data Center Operation
Share
  • All forum topics
  • Previous Topic
  • Next Topic
9 Replies 9
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 11:17 PM
0 Likes
7
140
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 11:17 PM

Re: DCO DR node - frequency for synchronisation job

This answer was originally posted on DCIM Support by Jim Davis on 2019-11-06


Lukasz

 

The following is documented on the page https://sxwhelpcenter.ecostruxureit.com/display/public/UADCO8x/StruxureWare+Data+Center+Operation+Ne....

Based on some data usage testing we found that the minimum requirement for running a DR node on a 200 rack solution is 10 Mbit/s. This of course varies by usage, but unless the user performs multiple changes to the entire solution in short succession, the DR node will stay in sync within a few minutes on a 10 Mbit/s connection even with larger changes (e.g. adding 50 racks). For most common tasks, the DR will be sync'd within seconds. DCO also has a large buffer (8 GB), so the DR node will be able to catch up even if there are many changes at once, it will simply be a few saves behind the main node (however, still in a consistent state).

Regards

Jim

(CID:151063106)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 11:17 PM
0 Likes
0
140
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 11:17 PM

Re: DCO DR node - frequency for synchronisation job

This comment was originally posted on DCIM Support by Lukasz Staciwo on 2019-11-06


Thanks Jim,

This refers to PostgreSQL and the whole section is titled "Disaster recovery node and cluster related protocols" so my suspicion is that this long description is actually talking about the way CLUSTER would synchronise and not how the PROD and DR nodes would...

(CID:151063121)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 11:17 PM
0 Likes
0
140
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 11:17 PM

Re: DCO DR node - frequency for synchronisation job

This comment was originally posted on DCIM Support by Jeff Shaw on 2019-11-06


Lukasz Staciwo, Cluster is no longer an available option on DCO. This documentation refers to DR nodes.

(CID:151063276)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 11:17 PM
0 Likes
0
140
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 11:17 PM

Re: DCO DR node - frequency for synchronisation job

This comment was originally posted on DCIM Support by Lukasz Staciwo on 2019-11-07


Thank you Jeff Shaw

I am well aware of cluster setup not being supported anymore.

What I am saying is that the description on the above article refers to PostgreSQL ports which were previously used when cluster was available...I do not believe that DR DCO node uses PostgreSQL port to synchronise with PROD DCO node...

This page probably needs updating and my question still remains as per original post...

(CID:151063458)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 11:18 PM
0 Likes
0
140
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 11:18 PM

Re: DCO DR node - frequency for synchronisation job

This comment was originally posted on DCIM Support by Lukasz Staciwo on 2019-11-11


Hi Team,

Could you please advise?

Is the answer that Jim pointed me to describing the DR node operation and not the cluster setup? If yes that is great...I am just not sure if PostgreSQL ports are being used by DR node...

(CID:151064473)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 11:18 PM
0 Likes
0
140
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 11:18 PM

Re: DCO DR node - frequency for synchronisation job

This comment was originally posted on DCIM Support by Jef Faridi on 2019-11-20


Hi Lukasz,

Yes, Jim has pointed to the correct documentation. The description is also valid for the DR node.

Kind regards

(CID:152077145)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 11:18 PM
0 Likes
0
140
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 11:18 PM

Re: DCO DR node - frequency for synchronisation job

This comment was originally posted on DCIM Support by Lukasz Staciwo on 2019-11-21


Thank you Jef Faridi

Could you please requirest tha the documentation page is updated to remove the cluster references since it is no longer valid. If this desciption is valid for DR node does it mean that DR node uses  PostgreSQL on port 5432. to commnicate with Production DCO node?

(CID:152077530)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 11:18 PM
0 Likes
0
140
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 11:18 PM

Re: DCO DR node - frequency for synchronisation job

This comment was originally posted on DCIM Support by Jef Faridi on 2019-11-22


Hi Lukasz,

You are most welcome. Documentation will be updated soon (for the time being intentionally cluster description is not removed yet). Yes, postgresql on port 5432 is used to sync the data between master node and the DR.

Kind regards

(CID:152077722)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 11:18 PM
0 Likes
0
140
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 11:18 PM

🔒 Closed

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Share
Top Experts
User Count
Jef
Commander Jef Commander
41
APC_Steve
Lt. Commander APC_Steve Lt. Commander
23
gsterling
Lt. Commander gsterling Lt. Commander
20
Cory_McDonald
Lieutenant Cory_McDonald Lieutenant
13
GavanOB
Lieutenant GavanOB Lieutenant
7
See More Top Experts
Find a Service Provider
Find a certified partner to help you address your integration, installation, maintenance and project needs.
View all Providers
Support

Have a question? Please contact us with details, and we will respond.

Contact Us
FAQ

Look through existing questions to find popular answers.

Learn More
About

Want to know more about Exchange and its possibilities?

Learn More

Full access is just steps away!

Join Exchange for FREE and get unlimited access to our global community of experts.

Connect with Peers & Experts

Discuss challenges in energy and automation with 30,000+ experts and peers.

Get Support in Our Knowledge Base

Find answers in 10,000+ support articles to help solve your product and business challenges.

Ask Questions. Give Solutions

Find peer based solutions to your questions. Provide answers for fellow community members!

Register today for FREE

Register Now

Already have an account?Log in

About Us FAQ Terms & Conditions Privacy Notice Change your cookie settings
©2020, Schneider Electric