  • DCO 8.3.2 support on Portal 1.3.7
Community Menu
  • Forums
    • By Topic
        • EcoStruxure IT
          • EcoStruxure IT forum
        • Industrial Automation
          • Industry Automation and Control Forum
          • Alliance System Integrators Forum
          • Machine Solutions in the Digital Transformation
          • EcoStruxure Automation Expert / IEC 61499 Forum
          • Industrial Edge Computing Forum
          • Level and Pressure Instrumentation Forum
          • Modicon User Group
          • PLC Club Indonesia
          • SEE Automation Club Forum
          • Fabrika ve Makina Otomasyonu Çözümleri
          • Форум по промышленной автоматизации СНГ
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Forum
          • SCADA and Telemetry Devices Forum
        • Power Distribution IEC
          • Power Distribution and Digital
          • Power Standards & Regulations
          • Paneelbouw & Energie Distributie
        • Power Distribution Softwares
          • EcoStruxure Power Design Forum
          • SEE Electrical Building+ Forum
          • LayoutFAST User Group Forum
        • Solutions for your Business
          • Solutions for Food & Beverage Forum
          • Solutions for Healthcare Forum
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Forum
        • Healthcare
          • Solutions for Healthcare Forum
      • EcoStruxure IT
        • EcoStruxure IT forum
      • Industrial Automation
        • Industry Automation and Control Forum
        • Alliance System Integrators Forum
        • Machine Solutions in the Digital Transformation
        • EcoStruxure Automation Expert / IEC 61499 Forum
        • Industrial Edge Computing Forum
        • Level and Pressure Instrumentation Forum
        • Modicon User Group
        • PLC Club Indonesia
        • SEE Automation Club Forum
        • Fabrika ve Makina Otomasyonu Çözümleri
        • Форум по промышленной автоматизации СНГ
      • SCADA & Telemetry Solutions
        • Geo SCADA Expert Forum
        • SCADA and Telemetry Devices Forum
      • Power Distribution IEC
        • Power Distribution and Digital
        • Power Standards & Regulations
        • Paneelbouw & Energie Distributie
      • Power Distribution Softwares
        • EcoStruxure Power Design Forum
        • SEE Electrical Building+ Forum
        • LayoutFAST User Group Forum
      • Solutions for your Business
        • Solutions for Food & Beverage Forum
        • Solutions for Healthcare Forum
      • Food & Beverage
        • Solutions for Food & Beverage Forum
      • Healthcare
        • Solutions for Healthcare Forum
  • Blogs
    • By Topic
        • Industrial Automation
          • Industrial Edge Computing Blog
          • Industry 4.0 Blog
          • Industrie du Futur France
        • SCADA & Telemetry Solutions
          • SCADA and Telemetry Blog
        • Power Distribution IEC
          • Power Events & Webinars
          • Power Foundations Blog
        • Power Distribution NEMA
          • NEMA Power Foundations Blog
        • Power Distribution Softwares
          • EcoStruxure Power Design Blog
          • SEE Electrical Building+ Blog
        • Solutions for your Business
          • Solutions for Food & Beverage Blog
          • Solutions for Healthcare Blog
          • Solutions for Retail Blog
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Blog
        • Healthcare
          • Solutions for Healthcare Blog
        • Retail
          • Solutions for Retail Blog
      • Industrial Automation
        • Industrial Edge Computing Blog
        • Industry 4.0 Blog
        • Industrie du Futur France
      • SCADA & Telemetry Solutions
        • SCADA and Telemetry Blog
      • Power Distribution IEC
        • Power Events & Webinars
        • Power Foundations Blog
      • Power Distribution NEMA
        • NEMA Power Foundations Blog
      • Power Distribution Softwares
        • EcoStruxure Power Design Blog
        • SEE Electrical Building+ Blog
      • Solutions for your Business
        • Solutions for Food & Beverage Blog
        • Solutions for Healthcare Blog
        • Solutions for Retail Blog
      • Food & Beverage
        • Solutions for Food & Beverage Blog
      • Healthcare
        • Solutions for Healthcare Blog
      • Retail
        • Solutions for Retail Blog
  • Ideas
        • Industrial Automation
          • Modicon Ideas & new features
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Ideas
          • SCADA and Telemetry Devices Ideas
  • Knowledge Center
    • Building Automation Knowledge Base
    • Industrial Automation How-to videos
    • Ask Exchange
    • Digital E-books
    • Success Stories Corner
    • Power Talks
  • Events & Webinars
  • Support
    • User Guide
    • Leaderboard
    • Releases Notes
How can we help?
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
49248members
Join Now
242460posts
Join Now

DCO 8.3.2 support on Portal 1.3.7

Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Solved Go to Solution
Back to EcoStruxure IT forum
Solved
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 10:12 PM
0 Likes
8
532
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 10:12 PM

DCO 8.3.2 support on Portal 1.3.7

This question was originally posted on DCIM Support by Law TJ on 2019-09-18


Dear Community, 

 

We have recently upgraded to DCO 8.3.2 from DCO 8.2.12. We found that values from DCO was not able to display properly and it runs until "timeout". However, values from DCE has no issue. 

 

Does anyone have any idea on this? 

Best Regards, 

 

TJ

(CID:148770719)

Solved! Go to Solution.

Labels
  • Data Center Operation
  • Portal
Share

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 10:13 PM
0 Likes
6
532
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 10:13 PM

Re: DCO 8.3.2 support on Portal 1.3.7

This answer was originally posted on DCIM Support by Jef Faridi on 2019-09-18


Hi TJ,

Your portlets are getting timeout - it seems your Portal is not able to communicate with its integrated DCO. That might be network related or possibly configuration issue. Check the settings/configuration in Portal: "Go to" > Control Panel > Connect to StruxureWare system. I would either edit the current integrated server and/or re-add and reconfigure the portlets. Make sure the "Endpoint URL" correctly defined and credentials (User Name/Password) are correct:

 

Kind regards

(CID:148770846)

See Answer In Context

Share
  • All forum topics
  • Previous Topic
  • Next Topic
8 Replies 8
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 10:13 PM
0 Likes
6
533
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 10:13 PM

Re: DCO 8.3.2 support on Portal 1.3.7

This answer was originally posted on DCIM Support by Jef Faridi on 2019-09-18


Hi TJ,

Your portlets are getting timeout - it seems your Portal is not able to communicate with its integrated DCO. That might be network related or possibly configuration issue. Check the settings/configuration in Portal: "Go to" > Control Panel > Connect to StruxureWare system. I would either edit the current integrated server and/or re-add and reconfigure the portlets. Make sure the "Endpoint URL" correctly defined and credentials (User Name/Password) are correct:

 

Kind regards

(CID:148770846)

See Answer In Context

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 10:13 PM
0 Likes
0
532
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 10:13 PM

Re: DCO 8.3.2 support on Portal 1.3.7

This comment was originally posted on DCIM Support by Law TJ on 2019-09-18


Hi Jef, 

What is the port used between DCO and Portal connection? Just want to make sure Portal server allows the port traffic

 

BR, 

 

TJ.

(CID:148770928)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 10:13 PM
0 Likes
0
532
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 10:13 PM

Re: DCO 8.3.2 support on Portal 1.3.7

This comment was originally posted on DCIM Support by Jef Faridi on 2019-09-19


Hi TJ,

My above illustration is showing that as well 😀 , Communication between Portal and DCO can be via port 8080 (http) and/or 443 (https).

So when defining the Endpoint URL, you would need to enter:

http://<dco-server-IP>:8080

or

https://<dco-server-IP>:443

 

You might also want to check if your DCO accepts http and/or https connections. To verify this, go to DCO Webmin interface, StruxureWare DC Operation > Setup.

Kind regards

(CID:148771201)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 10:13 PM
0 Likes
0
532
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 10:13 PM

Re: DCO 8.3.2 support on Portal 1.3.7

This comment was originally posted on DCIM Support by Law TJ on 2019-09-20


Hi Jef, 

Those site are connected before and running well.  Below are the things I checked:

  1. DCO setup page - http and https accepted. 
  2. Disabled firewall in Portal server - same result. 
  3. One of the DCO sites was connected via APC LAN (192.168.x.x), but it also shows the same issue. 
  4. Checked java version - Ver7 update 79, not sure if this causes the issue? 
  5. Tried the endpoint to format https://<ip>:443 for all DCO sites but not working. 

So I am still wondering which part might be gone wrong...

 

BR

TJ

 

(CID:148771589)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 10:13 PM
0 Likes
0
532
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 10:13 PM

Re: DCO 8.3.2 support on Portal 1.3.7

This comment was originally posted on DCIM Support by Jef Faridi on 2019-09-20


Hi TJ,

It seems the Java version is okay (it is similar to my test setup).

Verify if the servers (DCO and Portal) are reachable (ex: ssh log in DCO and ping to Portal server or vice versa), eg. if they can communicate.

Try adding/configuring a new DCO connection in Portal (instead of modifying the existing one) and see if that works - and make sure the endpoint url is properly set and also verify the credentials are correct.

Kind regards

(CID:148771595)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 10:13 PM
0 Likes
0
532
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 10:13 PM

Re: DCO 8.3.2 support on Portal 1.3.7

This comment was originally posted on DCIM Support by Law TJ on 2019-09-20


 

Hi Jef,

 

Update from my attempt:

  1. Actually there are 3 DCO sites connected to the Portal. One of the sites is running quite slow when we open the DCO webpage of it. 
  2. After I remove this site from the list, it seems that the other 2 sites' data are able to load very fast. 

I am guessing the slow loading DCO have caused this issue. 

Since this one issue is identified, I may need to check why is the other DCO is running very slow...

BR, 

 

TJ 

(CID:148771662)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 10:13 PM
0 Likes
0
532
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 10:13 PM

Re: DCO 8.3.2 support on Portal 1.3.7

This comment was originally posted on DCIM Support by Jef Faridi on 2019-09-20


Hi TJ,

Great, many thanks for the update.

Kind regards

(CID:148771667)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 10:13 PM
0 Likes
0
532
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 10:13 PM

🔒 Closed

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Share
Top Experts
User Count
APC_Steve
Lt. Commander APC_Steve Lt. Commander
2
MateFekete
Crewman MateFekete
1
GavanOB
Lieutenant GavanOB Lieutenant
1
lasalle_1
Crewman lasalle_1
1
Jef
Commander Jef Commander
1
See More Top Experts
Find a Service Provider
Find a certified partner to help you address your integration, installation, maintenance and project needs.
View all Providers
Support

Have a question? Please contact us with details, and we will respond.

Contact Us
FAQ

Look through existing questions to find popular answers.

Learn More
About

Want to know more about Exchange and its possibilities?

Learn More

Full access is just steps away!

Join Exchange for FREE and get unlimited access to our global community of experts.

Connect with Peers & Experts

Discuss challenges in energy and automation with 30,000+ experts and peers.

Get Support in Our Knowledge Base

Find answers in 10,000+ support articles to help solve your product and business challenges.

Ask Questions. Give Solutions

Find peer based solutions to your questions. Provide answers for fellow community members!

Register today for FREE

Register Now

Already have an account?Log in

About Us FAQ Terms & Conditions Privacy Notice Change your cookie settings
©2020, Schneider Electric