Sign In Help
Schneider Electric
HelpSign In
Schneider Electric Exchange
  • Home
  • Collaborate
  • Develop
  • Shop
Home Collaborate Develop Shop Log in or Register Help

Invite a Co-worker

Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel

Invitation Sent

Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
  • Home
  • Collaborate
  • Exchange Community
  • :
  • EcoStruxure IT
  • :
  • EcoStruxure IT forum
  • :
  • Re: DCO 8.3.2 - Asset Provisioning
Community Menu
  • Forums
    • By Topic
        • EcoStruxure IT
          • EcoStruxure IT forum
        • Industrial Automation
          • Industry Automation and Control Forum
          • Alliance System Integrators Forum
          • Machine Solutions in the Digital Transformation
          • EcoStruxure Automation Expert / IEC 61499 Forum
          • Industrial Edge Computing Forum
          • Level and Pressure Instrumentation Forum
          • Modicon User Group
          • PLC Club Indonesia
          • SEE Automation Club Forum
          • Fabrika ve Makina Otomasyonu Çözümleri
          • Форум по промышленной автоматизации СНГ
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Forum
          • SCADA and Telemetry Devices Forum
        • Power Distribution IEC
          • Power Distribution and Digital
          • Power Standards & Regulations
          • Paneelbouw & Energie Distributie
          • Eldistribution & Fastighetsautomation
        • Power Distribution Softwares
          • EcoStruxure Power Design Forum
          • SEE Electrical Building+ Forum
          • LayoutFAST User Group Forum
        • Wireless Information Network Solutions
          • Instrument Area Network
          • Remote Monitoring
          • Tank Level Monitoring
          • Remote Data Collection
        • Solutions for your Business
          • Solutions for Food & Beverage Forum
          • Solutions for Healthcare Forum
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Forum
        • Healthcare
          • Solutions for Healthcare Forum
      • EcoStruxure IT
        • EcoStruxure IT forum
      • Industrial Automation
        • Industry Automation and Control Forum
        • Alliance System Integrators Forum
        • Machine Solutions in the Digital Transformation
        • EcoStruxure Automation Expert / IEC 61499 Forum
        • Industrial Edge Computing Forum
        • Level and Pressure Instrumentation Forum
        • Modicon User Group
        • PLC Club Indonesia
        • SEE Automation Club Forum
        • Fabrika ve Makina Otomasyonu Çözümleri
        • Форум по промышленной автоматизации СНГ
      • SCADA & Telemetry Solutions
        • Geo SCADA Expert Forum
        • SCADA and Telemetry Devices Forum
      • Power Distribution IEC
        • Power Distribution and Digital
        • Power Standards & Regulations
        • Paneelbouw & Energie Distributie
        • Eldistribution & Fastighetsautomation
      • Power Distribution Softwares
        • EcoStruxure Power Design Forum
        • SEE Electrical Building+ Forum
        • LayoutFAST User Group Forum
      • Wireless Information Network Solutions
        • Instrument Area Network
        • Remote Monitoring
        • Tank Level Monitoring
        • Remote Data Collection
      • Solutions for your Business
        • Solutions for Food & Beverage Forum
        • Solutions for Healthcare Forum
      • Food & Beverage
        • Solutions for Food & Beverage Forum
      • Healthcare
        • Solutions for Healthcare Forum
  • Blogs
    • By Topic
        • Industrial Automation
          • Industrial Edge Computing Blog
          • Industry 4.0 Blog
          • Industrie du Futur France
        • SCADA & Telemetry Solutions
          • SCADA and Telemetry Blog
        • Power Distribution IEC
          • Power Events & Webinars
          • Power Foundations Blog
        • Power Distribution NEMA
          • NEMA Power Foundations Blog
        • Power Distribution Softwares
          • EcoStruxure Power Design Blog
          • SEE Electrical Building+ Blog
        • Solutions for your Business
          • Solutions for Food & Beverage Blog
          • Solutions for Healthcare Blog
          • Solutions for Retail Blog
        • Community experts & publishers
          • Publishers Community
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Blog
        • Healthcare
          • Solutions for Healthcare Blog
        • Retail
          • Solutions for Retail Blog
      • Industrial Automation
        • Industrial Edge Computing Blog
        • Industry 4.0 Blog
        • Industrie du Futur France
      • SCADA & Telemetry Solutions
        • SCADA and Telemetry Blog
      • Power Distribution IEC
        • Power Events & Webinars
        • Power Foundations Blog
      • Power Distribution NEMA
        • NEMA Power Foundations Blog
      • Power Distribution Softwares
        • EcoStruxure Power Design Blog
        • SEE Electrical Building+ Blog
      • Solutions for your Business
        • Solutions for Food & Beverage Blog
        • Solutions for Healthcare Blog
        • Solutions for Retail Blog
      • Community experts & publishers
        • Publishers Community
      • Food & Beverage
        • Solutions for Food & Beverage Blog
      • Healthcare
        • Solutions for Healthcare Blog
      • Retail
        • Solutions for Retail Blog
  • Ideas
        • Industrial Automation
          • Modicon Ideas & new features
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Ideas
          • SCADA and Telemetry Devices Ideas
  • Knowledge Center
    • Building Automation Knowledge Base
    • Industrial Automation Knowledge Base
    • Industrial Automation How-to videos
    • SCADA & Telemetry Solutions Knowledge Base
    • Digital E-books
    • Success Stories Corner
    • Power Talks
  • Events & Webinars
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Technology Partners
  • Support
    • Ask Exchange
    • Leaderboard
    • Our Community Guidelines
    • Community User Guide
    • How-To & Best Practices
    • More
Join Now
How can we help?
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
51315members
Join Now
245520posts
Join Now

DCO 8.3.2 - Asset Provisioning

Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Solved Go to Solution
Back to EcoStruxure IT forum
Solved
Venkat
Ensign Venkat Ensign
Ensign
‎2020-07-24 01:48 AM
0 Likes
4
670
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-24 01:48 AM

DCO 8.3.2 - Asset Provisioning

Hi,

 

We have noticed the Warning Recommendation as stated "Rack support Equipment Watts per U Height" even if the Rack is empty. 

 

Please find herewith the screenshot attached for your kind reference.

 

Request you to advice the reason behind this recommendation.

 

If required, we can share the DCO Backup also.

 

Thanks - K.Venkat.

Solved! Go to Solution.

Attachments
Labels
  • Data Center Operation
Tags (1)
  • Tags:
  • english
Share
Reply

Accepted Solutions
Jef
Commander Jef Commander
Commander
‎2020-07-24 04:44 AM
1 Like
3
655
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-24 04:44 AM

Re: DCO 8.3.2 - Asset Provisioning

Hi Venkat,

Apparently it has to do with asset U-Height calculations. I can reproduce similar notification for assets with U-height 2 or larger. I will capture this in our backlog for code review and possible enhancements, thanks.

Kind regards

See Answer In Context

Tags (1)
  • Tags:
  • english
Share
Reply
ATrabert
Lieutenant JG ATrabert Lieutenant JG
Lieutenant JG
‎2020-07-24 06:54 AM
1 Like
1
647
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-24 06:54 AM

Re: DCO 8.3.2 - Asset Provisioning

Venkat,

As I understand this, you get this warning if the asset your using will leave stranded capacity if it were to fill the rack.  So a 42U rack can hold 24 2U servers.  At 300W each, you would only have 7200 watts or 7.2 kW.  This will leave around 4kW left, which is why you get a warning.  You could test this with by adjusting the nameplate value to be around 450W.

 

If my explanation is correct, in my opinion, its more of a nuisance warning.  It would be red if it was something more critical.

See Answer In Context

Tags (1)
  • Tags:
  • english
Share
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
4 Replies 4
Jef
Commander Jef Commander
Commander
‎2020-07-24 04:44 AM
1 Like
3
656
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-24 04:44 AM

Re: DCO 8.3.2 - Asset Provisioning

Hi Venkat,

Apparently it has to do with asset U-Height calculations. I can reproduce similar notification for assets with U-height 2 or larger. I will capture this in our backlog for code review and possible enhancements, thanks.

Kind regards

See Answer In Context

Tags (1)
  • Tags:
  • english
Share
Reply
Venkat
Ensign Venkat Ensign
Ensign
‎2020-07-24 06:36 AM
0 Likes
2
650
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-24 06:36 AM

Re: DCO 8.3.2 - Asset Provisioning

Hi Jef.

 

Thanks for your prompt response. We need to provide the justification to customer, why this is giving an warning message even for an empty rack. The design limit set for the Rack is 11 kW. We have tried the asset with 300 W. Still we get this warning note. How the system is calculating watt per U-height.

 

Thanks - K.Venkat

Tags (1)
  • Tags:
  • english
Share
Reply
ATrabert
Lieutenant JG ATrabert Lieutenant JG
Lieutenant JG
‎2020-07-24 06:54 AM
1 Like
1
648
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-24 06:54 AM

Re: DCO 8.3.2 - Asset Provisioning

Venkat,

As I understand this, you get this warning if the asset your using will leave stranded capacity if it were to fill the rack.  So a 42U rack can hold 24 2U servers.  At 300W each, you would only have 7200 watts or 7.2 kW.  This will leave around 4kW left, which is why you get a warning.  You could test this with by adjusting the nameplate value to be around 450W.

 

If my explanation is correct, in my opinion, its more of a nuisance warning.  It would be red if it was something more critical.

See Answer In Context

Tags (1)
  • Tags:
  • english
Share
Reply
ATrabert
Lieutenant JG ATrabert Lieutenant JG
Lieutenant JG
‎2020-07-30 10:03 AM
0 Likes
0
610
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-30 10:03 AM

Re: DCO 8.3.2 - Asset Provisioning

this should read "So a 42U rack can hold 21 2U servers", but the rest of the explanation is the same.

Tags (1)
  • Tags:
  • english
Share
Reply
Top Experts
User Count
Jef
Commander Jef Commander
41
APC_Steve
Lt. Commander APC_Steve Lt. Commander
24
gsterling
Lt. Commander gsterling Lt. Commander
20
Cory_McDonald
Lieutenant Cory_McDonald Lieutenant
13
GavanOB
Lieutenant GavanOB Lieutenant
7
See More Top Experts
Find a Service Provider
Find a certified partner to help you address your integration, installation, maintenance and project needs.
View all Providers
Support

Have a question? Please contact us with details, and we will respond.

Contact Us
FAQ

Look through existing questions to find popular answers.

Learn More
About

Want to know more about Exchange and its possibilities?

Learn More

Full access is just steps away!

Join Exchange for FREE and get unlimited access to our global community of experts.

Connect with Peers & Experts

Discuss challenges in energy and automation with 30,000+ experts and peers.

Get Support in Our Knowledge Base

Find answers in 10,000+ support articles to help solve your product and business challenges.

Ask Questions. Give Solutions

Find peer based solutions to your questions. Provide answers for fellow community members!

Register today for FREE

Register Now

Already have an account?Log in

About Us FAQ Terms & Conditions Privacy Notice Change your cookie settings
©2020, Schneider Electric