Hello,
Is it possible to create half equipment in rack ?
(for example a RAD ETX202) but with 2 equipments for the same U ?
(CID:132671293)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 09:05 PM
This answer was originally posted on DCIM Support by Ed Tarento on 2018-08-01
Hi
if the devices are shelf mounted then you can model these exactly. if the devices are in a chassis then model a chassis with 2 devices in there. if the devices are half ru each then you can only model a single device representing both or do the shelf option. shelf is best I think because you have good asset control
i hope that helps
Ed
(CID:132671302)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 09:05 PM
This answer was originally posted on DCIM Support by Ed Tarento on 2018-08-01
Hi
if the devices are shelf mounted then you can model these exactly. if the devices are in a chassis then model a chassis with 2 devices in there. if the devices are half ru each then you can only model a single device representing both or do the shelf option. shelf is best I think because you have good asset control
i hope that helps
Ed
(CID:132671302)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 09:05 PM
This comment was originally posted on DCIM Support by JEGO-AQUILINA on 2018-08-01
Hello Ed,
Thanks for your help. the devices are shelf mounted but i cann't create the equipment on the half of the bay to put two side by side on shelf
(CID:132671343)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 09:05 PM
This answer was originally posted on DCIM Support by JEGO-AQUILINA on 2018-08-01
OOOOOh it's good !
Juste in properties - mounting and tick Shelf and left or right !
It's magic 😂 Thanks Ed for pointing me in the right direction
(CID:132671345)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 09:05 PM
This comment was originally posted on DCIM Support by Carsten Hjuler Madsen on 2018-08-02
I works. 😀 😀
(CID:132671756)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 09:06 PM
This answer was originally posted on DCIM Support by Winnie Chau on 2018-08-02
Eddie Mou Daniel Kwong Fergus Wong
Support for half-rack via Shelf option - Thanks to our expert Ed 😀
(CID:132671677)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 09:06 PM . Last Modified: 2023-10-22 01:33 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.