Sign In Help
Schneider Electric
HelpSign In
Schneider Electric Exchange
  • Home
  • Collaborate
  • Develop
  • Shop
Home Collaborate Develop Shop Log in or Register Help

Invite a Co-worker

Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel

Invitation Sent

Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
  • Home
  • Collaborate
  • Exchange Community
  • :
  • EcoStruxure IT
  • :
  • EcoStruxure IT forum
  • :
  • Re: DCO 8.2.12 Application status down
Community Menu
  • Forums
    • By Topic
        • EcoStruxure IT
          • EcoStruxure IT forum
        • Industrial Automation
          • Industry Automation and Control Forum
          • Alliance System Integrators Forum
          • Machine Solutions in the Digital Transformation
          • EcoStruxure Automation Expert / IEC 61499 Forum
          • Industrial Edge Computing Forum
          • Level and Pressure Instrumentation Forum
          • Modicon User Group
          • PLC Club Indonesia
          • SEE Automation Club Forum
          • Fabrika ve Makina Otomasyonu Çözümleri
          • Форум по промышленной автоматизации СНГ
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Forum
          • SCADA and Telemetry Devices Forum
        • Power Distribution IEC
          • Power Distribution and Digital
          • Power Standards & Regulations
          • Paneelbouw & Energie Distributie
        • Power Distribution Softwares
          • EcoStruxure Power Design Forum
          • SEE Electrical Building+ Forum
          • LayoutFAST User Group Forum
        • Wireless Information Network Solutions
          • Instrument Area Network
          • Remote Monitoring
          • Tank Level Monitoring
          • Remote Data Collection
        • Solutions for your Business
          • Solutions for Food & Beverage Forum
          • Solutions for Healthcare Forum
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Forum
        • Healthcare
          • Solutions for Healthcare Forum
      • EcoStruxure IT
        • EcoStruxure IT forum
      • Industrial Automation
        • Industry Automation and Control Forum
        • Alliance System Integrators Forum
        • Machine Solutions in the Digital Transformation
        • EcoStruxure Automation Expert / IEC 61499 Forum
        • Industrial Edge Computing Forum
        • Level and Pressure Instrumentation Forum
        • Modicon User Group
        • PLC Club Indonesia
        • SEE Automation Club Forum
        • Fabrika ve Makina Otomasyonu Çözümleri
        • Форум по промышленной автоматизации СНГ
      • SCADA & Telemetry Solutions
        • Geo SCADA Expert Forum
        • SCADA and Telemetry Devices Forum
      • Power Distribution IEC
        • Power Distribution and Digital
        • Power Standards & Regulations
        • Paneelbouw & Energie Distributie
      • Power Distribution Softwares
        • EcoStruxure Power Design Forum
        • SEE Electrical Building+ Forum
        • LayoutFAST User Group Forum
      • Wireless Information Network Solutions
        • Instrument Area Network
        • Remote Monitoring
        • Tank Level Monitoring
        • Remote Data Collection
      • Solutions for your Business
        • Solutions for Food & Beverage Forum
        • Solutions for Healthcare Forum
      • Food & Beverage
        • Solutions for Food & Beverage Forum
      • Healthcare
        • Solutions for Healthcare Forum
  • Blogs
    • By Topic
        • Industrial Automation
          • Industrial Edge Computing Blog
          • Industry 4.0 Blog
          • Industrie du Futur France
        • SCADA & Telemetry Solutions
          • SCADA and Telemetry Blog
        • Power Distribution IEC
          • Power Events & Webinars
          • Power Foundations Blog
        • Power Distribution NEMA
          • NEMA Power Foundations Blog
        • Power Distribution Softwares
          • EcoStruxure Power Design Blog
          • SEE Electrical Building+ Blog
        • Solutions for your Business
          • Solutions for Food & Beverage Blog
          • Solutions for Healthcare Blog
          • Solutions for Retail Blog
        • Community experts & publishers
          • Publishers Community
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Blog
        • Healthcare
          • Solutions for Healthcare Blog
        • Retail
          • Solutions for Retail Blog
      • Industrial Automation
        • Industrial Edge Computing Blog
        • Industry 4.0 Blog
        • Industrie du Futur France
      • SCADA & Telemetry Solutions
        • SCADA and Telemetry Blog
      • Power Distribution IEC
        • Power Events & Webinars
        • Power Foundations Blog
      • Power Distribution NEMA
        • NEMA Power Foundations Blog
      • Power Distribution Softwares
        • EcoStruxure Power Design Blog
        • SEE Electrical Building+ Blog
      • Solutions for your Business
        • Solutions for Food & Beverage Blog
        • Solutions for Healthcare Blog
        • Solutions for Retail Blog
      • Community experts & publishers
        • Publishers Community
      • Food & Beverage
        • Solutions for Food & Beverage Blog
      • Healthcare
        • Solutions for Healthcare Blog
      • Retail
        • Solutions for Retail Blog
  • Ideas
        • Industrial Automation
          • Modicon Ideas & new features
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Ideas
          • SCADA and Telemetry Devices Ideas
  • Knowledge Center
    • Building Automation Knowledge Base
    • Industrial Automation Knowledge Base
    • Industrial Automation How-to videos
    • SCADA & Telemetry Solutions Knowledge Base
    • Digital E-books
    • Success Stories Corner
    • Power Talks
  • Events & Webinars
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Technology Partners
  • Support
    • Ask Exchange
    • Leaderboard
    • Our Community Guidelines
    • Community User Guide
    • How-To & Best Practices
    • More
Join Now
How can we help?
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
51009members
Join Now
245062posts
Join Now

DCO 8.2.12 Application status down

Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Back to EcoStruxure IT forum
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 10:28 PM
0 Likes
4
98
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 10:28 PM

DCO 8.2.12 Application status down

This question was originally posted on DCIM Support by mike sutton on 2019-10-01


Hi I have upgraded a clients DCO to 8.2.12 however now its showing app status down tried rebooting but still the same issue. I checked the no 3rd party and do not download from internet so i know that isn't the issue anyone got any ideas??

TIA 

Mike

(CID:149293111)

Labels
  • Data Center Operation
Share
  • All forum topics
  • Previous Topic
  • Next Topic
4 Replies 4
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 10:28 PM
0 Likes
2
98
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 10:28 PM

Re: DCO 8.2.12 Application status down

This answer was originally posted on DCIM Support by Jef Faridi on 2019-10-01


Hi Mike,

From what version?

During the upgrade, did you see nay error messages being displayed?

Depending on the complexity of the setup, upgrade may take some time (even hours) to be successfully completed. Upgrade process shall not be interrupted, otherwise server will be left in bad/unrecoverable state. Manually rebooting the server, while the upgrade is in progress would damage the database. When the server is in bad state, then the best (or only) option could be a clean installation and then restoring the latest backup file.

PS: the latest release versions are DCO 8.3.2 and ITA 9.0.4. If you/customer should wish to stay in DCO, then 8.3.2 is recommended otherwise I would go for ITA 9.0.4.    

Kind regards

(CID:149293130)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 10:28 PM
0 Likes
0
98
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 10:28 PM

Re: DCO 8.2.12 Application status down

This comment was originally posted on DCIM Support by mike sutton on 2019-10-01


Hi Jef,

Thanks it was from 8.7 to 8.12 the status page showed it had accepted the update but the services page throws this little gem at me!!

 

(CID:149293353)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 10:28 PM
0 Likes
0
98
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 10:28 PM

Re: DCO 8.2.12 Application status down

This comment was originally posted on DCIM Support by Jef Faridi on 2019-10-02


Hi Mike,

Thanks for the info - the status page is usually showing the status of the application, I guess (only guessing) either the services was starting (if the upgrade was successful) or mot likely the upgrade was not finished yet (as mentioned it may take some time even hours to be completed). So apparently by forcing the server to reboot, the upgrade job have been interrupted and left the server in unrecoverable state. At this moment, I think the best option is to make a clean installation of 8.2.12 (but 8.3.2 is recommended) and then restoring the latest backup file.

It is also highly recommended to save the backup files (/data/backup) somewhere safe (for safekeeping) such as network drive.

Kind regards

(CID:149293357)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 10:28 PM
0 Likes
0
98
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 10:28 PM

🔒 Closed

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Share
Top Experts
User Count
Jef
Commander Jef Commander
41
APC_Steve
Lt. Commander APC_Steve Lt. Commander
23
gsterling
Lt. Commander gsterling Lt. Commander
20
Cory_McDonald
Lieutenant Cory_McDonald Lieutenant
13
GavanOB
Lieutenant GavanOB Lieutenant
7
See More Top Experts
Find a Service Provider
Find a certified partner to help you address your integration, installation, maintenance and project needs.
View all Providers
Support

Have a question? Please contact us with details, and we will respond.

Contact Us
FAQ

Look through existing questions to find popular answers.

Learn More
About

Want to know more about Exchange and its possibilities?

Learn More

Full access is just steps away!

Join Exchange for FREE and get unlimited access to our global community of experts.

Connect with Peers & Experts

Discuss challenges in energy and automation with 30,000+ experts and peers.

Get Support in Our Knowledge Base

Find answers in 10,000+ support articles to help solve your product and business challenges.

Ask Questions. Give Solutions

Find peer based solutions to your questions. Provide answers for fellow community members!

Register today for FREE

Register Now

Already have an account?Log in

About Us FAQ Terms & Conditions Privacy Notice Change your cookie settings
©2020, Schneider Electric