Hi Team ,
We config DCO and showed 2D was very well . When turn to 3D mode , it's showed cooling is not
enough ,the temp. may incorrect . I'm tring to add more cooling but the result was the same ,
can someone advice what's the problem'on it ? Many thanks.
Best Regards
(CID:130098033)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 04:45 PM . Last Modified: 3 weeks ago
Billy,
Your cold aisle containment need to cover the rack, not only till the front door of the rack
Look at the video example around 6 minute on how to model the containtment.
The video showed hot aisle containment, but the method is the same.
http://sxwhelpcenter.ecostruxureit.com/display/VIDEO/How+to+model+different+types+of+cooling
(CID:130098046)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 04:45 PM . Last Modified: 3 weeks ago
Billy,
Your cold aisle containment need to cover the rack, not only till the front door of the rack
Look at the video example around 6 minute on how to model the containtment.
The video showed hot aisle containment, but the method is the same.
http://sxwhelpcenter.ecostruxureit.com/display/VIDEO/How+to+model+different+types+of+cooling
(CID:130098046)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 04:45 PM . Last Modified: 3 weeks ago
Hi Chris ,
Thank you ,I will check it later .
Best Regards
(CID:130098674)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 04:45 PM . Last Modified: 3 weeks ago
Hi Chris ,
Thank you ,I will check it later .
Best Regards
(CID:130098675)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 04:46 PM . Last Modified: 2023-10-22 01:29 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.