EcoStruxure IT forum
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 10:53 PM . Last Modified: 3 weeks ago
Hi team,
we have an installation with DCE 7.6 and Netbotz 250 and we are receiving a lot of emails from different T/H sensors
As you can see the maximum value was 78% since 19th:
And the treshold is configured above 80:
And last days we received too many alarms:
What could be the problem?
(CID:149786615)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 10:53 PM . Last Modified: 3 weeks ago
Any suggestion?
(CID:151060533)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 10:53 PM . Last Modified: 3 weeks ago
Dear Javier Zurera,
I highly suspect, that the source of all these alarms is not your custom thresholds, that you wrote about, but devace alarms, which can be configured by default on your NetBotz-250.
Therefore, you need to make sure through the web-GUI NetBotz-250, that all humidity alarms that are configured there are disabled or have the values you need.
With respect.
(CID:151062312)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 10:53 PM . Last Modified: 2023-10-22 01:28 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.