EcoStruxure IT forum
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 09:33 PM
This question was originally posted on DCIM Support by Erik Torres on 2019-08-14
Hello everyone.
I just configured all devices in DCE and its working great, even added DDFs files for new devices and they are working as expected.
I am integrating DCE with a Network monitoring system (Nagios) using SNMP Traps and I am receiving the traps just fine. But I get too much useless information in the trap that I dont want, that information is in the message field for SNMP.
Is there a way to configure the message that DCE sends to the Monitoring System, just as I do for sending mails?
This is an example of a message that I receive as Trap.
"B7fbf77_nbErrorCond_87928E65 Alarma de dispositivo 14 B7fbf77_nbSNMPEnc5C105037 MANEJADORA UE ALT-02 (xxx.xxx.xxx.xxx) 44 69 73 70 6F 73 69 74 69 76 6F 20 64 65 20 72 65 66 72 69 67 65 72 61 63 69 C3 B3 6E ISUnityDP xxx.xxx.xxx.xxx SALA DE ALISTAMIENTO EMPRESA C.A 1565801736 1565801917 Active Message has returned to normal."
|
Text in bold is the information I want to keep
Thanks in advance.
ET
(CID:147784512)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 09:33 PM
This answer was originally posted on DCIM Support by Steven Marchetti on 2019-08-14
Hi Erik,
Sorry but no, you can't edit the info sent in a trap. I can provide you info on what that data is (see below links) but if you wanted only a limited subset of info, you'll have to use e-mails or short e-mail messages and use macros to specify the data you want.
http://www.apc.com/us/en/faqs/FA231439
http://www.apc.com/us/en/faqs/FA236815
Thanks,
Steve
(CID:147784538)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 09:33 PM
This answer was originally posted on DCIM Support by Steven Marchetti on 2019-08-14
Hi Erik,
Sorry but no, you can't edit the info sent in a trap. I can provide you info on what that data is (see below links) but if you wanted only a limited subset of info, you'll have to use e-mails or short e-mail messages and use macros to specify the data you want.
http://www.apc.com/us/en/faqs/FA231439
http://www.apc.com/us/en/faqs/FA236815
Thanks,
Steve
(CID:147784538)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 09:33 PM
This comment was originally posted on DCIM Support by Erik Torres on 2019-08-19
Hey Steven,
Thanks for your quick answer. Instead of sending traps I managed to create scripts that sends the exact information I need, the problem is that I need to create a Script for every service of every host.
(CID:148341095)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 09:33 PM . Last Modified: 2023-10-22 01:27 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.