  • DCE monitors DCO PUE
Community Menu
  • Forums
    • By Topic
        • EcoStruxure IT
          • EcoStruxure IT forum
        • Industrial Automation
          • Industry Automation and Control Forum
          • Alliance System Integrators Forum
          • Machine Solutions in the Digital Transformation
          • EcoStruxure Automation Expert / IEC 61499 Forum
          • Industrial Edge Computing Forum
          • Level and Pressure Instrumentation Forum
          • Modicon User Group
          • PLC Club Indonesia
          • SEE Automation Club Forum
          • Fabrika ve Makina Otomasyonu Çözümleri
          • Форум по промышленной автоматизации СНГ
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Forum
          • SCADA and Telemetry Devices Forum
        • Power Distribution IEC
          • Power Distribution and Digital
          • Power Standards & Regulations
          • Paneelbouw & Energie Distributie
        • Power Distribution Softwares
          • EcoStruxure Power Design Forum
          • SEE Electrical Building+ Forum
          • LayoutFAST User Group Forum
        • Wireless Information Network Solutions
          • Instrument Area Network
          • Remote Monitoring
          • Tank Level Monitoring
          • Remote Data Collection
        • Solutions for your Business
          • Solutions for Food & Beverage Forum
          • Solutions for Healthcare Forum
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Forum
        • Healthcare
          • Solutions for Healthcare Forum
      • EcoStruxure IT
        • EcoStruxure IT forum
      • Industrial Automation
        • Industry Automation and Control Forum
        • Alliance System Integrators Forum
        • Machine Solutions in the Digital Transformation
        • EcoStruxure Automation Expert / IEC 61499 Forum
        • Industrial Edge Computing Forum
        • Level and Pressure Instrumentation Forum
        • Modicon User Group
        • PLC Club Indonesia
        • SEE Automation Club Forum
        • Fabrika ve Makina Otomasyonu Çözümleri
        • Форум по промышленной автоматизации СНГ
      • SCADA & Telemetry Solutions
        • Geo SCADA Expert Forum
        • SCADA and Telemetry Devices Forum
      • Power Distribution IEC
        • Power Distribution and Digital
        • Power Standards & Regulations
        • Paneelbouw & Energie Distributie
      • Power Distribution Softwares
        • EcoStruxure Power Design Forum
        • SEE Electrical Building+ Forum
        • LayoutFAST User Group Forum
      • Wireless Information Network Solutions
        • Instrument Area Network
        • Remote Monitoring
        • Tank Level Monitoring
        • Remote Data Collection
      • Solutions for your Business
        • Solutions for Food & Beverage Forum
        • Solutions for Healthcare Forum
      • Food & Beverage
        • Solutions for Food & Beverage Forum
      • Healthcare
        • Solutions for Healthcare Forum
  • Blogs
    • By Topic
        • Industrial Automation
          • Industrial Edge Computing Blog
          • Industry 4.0 Blog
          • Industrie du Futur France
        • SCADA & Telemetry Solutions
          • SCADA and Telemetry Blog
        • Power Distribution IEC
          • Power Events & Webinars
          • Power Foundations Blog
        • Power Distribution NEMA
          • NEMA Power Foundations Blog
        • Power Distribution Softwares
          • EcoStruxure Power Design Blog
          • SEE Electrical Building+ Blog
        • Solutions for your Business
          • Solutions for Food & Beverage Blog
          • Solutions for Healthcare Blog
          • Solutions for Retail Blog
        • Community experts & publishers
          • Publishers Community
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Blog
        • Healthcare
          • Solutions for Healthcare Blog
        • Retail
          • Solutions for Retail Blog
      • Industrial Automation
        • Industrial Edge Computing Blog
        • Industry 4.0 Blog
        • Industrie du Futur France
      • SCADA & Telemetry Solutions
        • SCADA and Telemetry Blog
      • Power Distribution IEC
        • Power Events & Webinars
        • Power Foundations Blog
      • Power Distribution NEMA
        • NEMA Power Foundations Blog
      • Power Distribution Softwares
        • EcoStruxure Power Design Blog
        • SEE Electrical Building+ Blog
      • Solutions for your Business
        • Solutions for Food & Beverage Blog
        • Solutions for Healthcare Blog
        • Solutions for Retail Blog
      • Community experts & publishers
        • Publishers Community
      • Food & Beverage
        • Solutions for Food & Beverage Blog
      • Healthcare
        • Solutions for Healthcare Blog
      • Retail
        • Solutions for Retail Blog
  • Ideas
        • Industrial Automation
          • Modicon Ideas & new features
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Ideas
          • SCADA and Telemetry Devices Ideas
  • Knowledge Center
    • Building Automation Knowledge Base
    • Industrial Automation Knowledge Base
    • Industrial Automation How-to videos
    • SCADA & Telemetry Solutions Knowledge Base
    • Digital E-books
    • Success Stories Corner
    • Power Talks
  • Events & Webinars
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Technology Partners
  • Support
    • Ask Exchange
    • Leaderboard
    • Our Community Guidelines
    • Community User Guide
    • How-To & Best Practices
    • More
Join Now
How can we help?
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
50955members
Join Now
244990posts
Join Now

DCE monitors DCO PUE

Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Back to EcoStruxure IT forum
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 02:15 PM
0 Likes
49
364
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 02:15 PM

DCE monitors DCO PUE

This question was originally posted on DCIM Support by Ed Tarento on 2018-11-19


If you have DCO and want the PUE dashboard amount shown by your SNMP monitor, especially DCE, here is a way to do it.

DCO PUE in DCE V2.pdf

Cheers,

Ed

(CID:136153387)

Labels
  • Data Center Expert
  • Data Center Operation
Share
  • All forum topics
  • Previous Topic
  • Next Topic
49 Replies 49
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 02:15 PM
0 Likes
0
364
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 02:15 PM

Re: DCE monitors DCO PUE

This comment was originally posted on DCIM Support by spezialist on 2018-11-21


Dear Stine Hansen,

Tell me please, the attachment below is not available only for my EcoStruxure IT user account or for all EcoStruxure IT users (non-employees =SE=)? If so, why?

Very thanks for the support.

(CID:136644429)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 02:15 PM
0 Likes
0
364
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 02:15 PM

Re: DCE monitors DCO PUE

This comment was originally posted on DCIM Support by Greg Sterling on 2018-11-21


Is your browser removing the link? I can see and download the pdf attached on this page.

Regards

Greg Sterling

(CID:136644498)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 02:15 PM
0 Likes
0
364
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 02:15 PM

Re: DCE monitors DCO PUE

This comment was originally posted on DCIM Support by spezialist on 2018-11-21


Dear Greg Sterling,

No, it does not depend on the browser or on the PC, etc. It looks like this is a feature from =SE= for me ☹️...

Very thanks for the support.

(CID:136644504)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 02:15 PM
0 Likes
0
364
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 02:15 PM

Re: DCE monitors DCO PUE

This comment was originally posted on DCIM Support by Gianluca Bertuletti on 2018-11-21


same issue to me

 

(CID:136644526)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 02:16 PM
0 Likes
0
364
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 02:16 PM

Re: DCE monitors DCO PUE

This comment was originally posted on DCIM Support by Stine Hansen on 2018-11-21


Hi spezialist, to avoid disclosure of sensitive information in attachments we have chosen to limit the visibility of certain attachments.

Thanks,

Stine 

(CID:136644583)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 02:16 PM
0 Likes
0
364
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 02:16 PM

Re: DCE monitors DCO PUE

This comment was originally posted on DCIM Support by Miguel angel solans on 2018-11-21


If it's not public, why Ed Tarento has publised here?

 

(CID:136644594)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 02:16 PM
0 Likes
0
364
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 02:16 PM

Re: DCE monitors DCO PUE

This comment was originally posted on DCIM Support by Stine Hansen on 2018-11-21


It's not Ed who has hidden the attachment. It's our policy to hide certain attachments. We're currently working on identifying and releasing attachments that don't reveal any sensitive information.

Thanks,

Stine

(CID:136644610)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 02:16 PM
0 Likes
0
364
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 02:16 PM

Re: DCE monitors DCO PUE

This comment was originally posted on DCIM Support by spezialist on 2018-11-21


Dear Stine Hansen,

Thanks for the support: now I can see the pdf document in this topic well and can download it 😀.

With respect.

(CID:136644783)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 02:16 PM
0 Likes
0
364
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 02:16 PM

Re: DCE monitors DCO PUE

This comment was originally posted on DCIM Support by Miguel angel solans on 2018-11-22


thanks Stine and ed. 

(CID:136645290)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 02:16 PM
0 Likes
0
364
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 02:16 PM

Re: DCE monitors DCO PUE

This comment was originally posted on DCIM Support by Ed Tarento on 2019-01-15


I tried editing my original post but some errors so here's V2 instructions, adding some trouble shooting info and some minor changes.  Let me know how you go

DCO PUE in DCE V2.pdf

Cheers

Ed

(CID:137733103)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 02:16 PM
0 Likes
0
364
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 02:16 PM

Re: DCE monitors DCO PUE

This comment was originally posted on DCIM Support by spezialist on 2019-01-16


Dear Stine Hansen,

Could you again help fix the inaccessibility of the file V2 instructions published by Ed Tarento?

Very thanks for the support.

(CID:137733204)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 02:16 PM
0 Likes
0
364
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 02:16 PM

Re: DCE monitors DCO PUE

This comment was originally posted on DCIM Support by Ed Tarento on 2019-01-16


DCO PUE in DCE V2.pdf

(CID:137733520)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 02:16 PM
0 Likes
0
364
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 02:16 PM

Re: DCE monitors DCO PUE

This comment was originally posted on DCIM Support by Ed Tarento on 2019-01-16


Try that

(CID:137733522)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 02:17 PM
0 Likes
0
364
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 02:17 PM

Re: DCE monitors DCO PUE

This comment was originally posted on DCIM Support by spezialist on 2019-01-16


Unfortunately the result is the same:

With respect.

(CID:137733538)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 02:17 PM
0 Likes
0
364
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 02:17 PM

Re: DCE monitors DCO PUE

This comment was originally posted on DCIM Support by Stine Hansen on 2019-01-16


Hi spezialist and Ed Tarento,

there seems to be a bug here. We're working on it.

Thanks,

Stine

(CID:137733558)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 02:17 PM
0 Likes
0
364
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 02:17 PM

Re: DCE monitors DCO PUE

This comment was originally posted on DCIM Support by Panagiotis Karampis on 2019-01-16


Hello,

At the time being we don't have a way to mark individual attachments as safe, thus we do it explicitly. A new upload will take a new ID and we will have to approve and whitelist it again, manually.

We will be working on making something more robust for future.

(CID:137733611)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 02:17 PM
0 Likes
0
364
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 02:17 PM

Re: DCE monitors DCO PUE

This comment was originally posted on DCIM Support by Miguel angel solans on 2019-01-16


thanks Ed

(CID:138380976)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 02:17 PM
0 Likes
0
364
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 02:17 PM

Re: DCE monitors DCO PUE

This comment was originally posted on DCIM Support by Andrew Stoakes on 2019-03-28


This is fantastic, thanks for sharing. Everything was working fine but now when i look at the PUE sensor it's saying  "Offline" and I'm not getting any data. 

(CID:141268047)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 02:17 PM
0 Likes
0
364
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 02:17 PM

Re: DCE monitors DCO PUE

This comment was originally posted on DCIM Support by Ed Tarento on 2019-03-28


Hi Andrew

Thanks for the feedback.  Does the DCO PUE Dashboard work?  show a figure you're expecting?  Is DCE properly reporting the status of the DCO server?  If needed, please also check "Troubleshooting" in the attached DCO PUE in DCE V2.pdf

Let us know how you go

Cheers

Ed

(CID:141268049)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 02:17 PM
0 Likes
0
364
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 02:17 PM

Re: DCE monitors DCO PUE

This comment was originally posted on DCIM Support by Andrew Stoakes on 2019-03-28


PUE is working on DCO and DCE has values from yesterday, it appears to stop working at midnight. snmp.conf is correct and getPUE is a copy of the txt in the file so that should be correct. 

If i run the test script i get the result 

(23) Failed writing body
./test.sh: line 8: /1/ {print $2}: No such file or directory

 

ls dir is

-rwxr-xr-x.  1 root root   900 Mar 28 09:28 getPUE.sh

 

 

(CID:141268065)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 02:17 PM
0 Likes
0
364
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 02:17 PM

Re: DCE monitors DCO PUE

This comment was originally posted on DCIM Support by Ed Tarento on 2019-03-28


Andrew, 

Check the line in test.sh is a single line

pue=`/bin/curl -ks https://"$DCOip"/rest/pue-v1/instantPueData| awk -F":" '/1/ {print $2}'|awk -F"," '/1/ {print $1}' `

and not 2 lines as it show in the PDF

I'll update the doco to make this clear

Let me know how you go

Ed

(CID:141268097)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 02:17 PM
0 Likes
0
364
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 02:17 PM

Re: DCE monitors DCO PUE

This comment was originally posted on DCIM Support by Andrew Stoakes on 2019-03-29


Perfect, test script works and returns the correct value. What's also interesting is that at midnight last night we started receiving data again. 

Am i correct in assuming that  DCO only calculates the PuE once a day, the values for PuE are the same for the 24h period, or is this an issue with the way that I have this setup? 

Thanks for the assistance 

(CID:141268615)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 02:17 PM
0 Likes
0
364
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 02:17 PM

Re: DCE monitors DCO PUE

This comment was originally posted on DCIM Support by Ed Tarento on 2019-03-29


Glad its working.  I know that the value only changes once per day and I assume its therefore only calculated once per day.

Cheers

Ed

(CID:141268623)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 02:18 PM
0 Likes
0
364
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 02:18 PM

Re: DCE monitors DCO PUE

This comment was originally posted on DCIM Support by Fergus Wong on 2019-07-04


Hi Ed Tarento,

Glad to be able to search your valuable input here.

Is this method calculating historical PUE from DCE and DCO still applicable the latest DCE and DCO version?

 

Thanks,

Fergus

(CID:146670089)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 02:18 PM
0 Likes
0
364
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 02:18 PM

Re: DCE monitors DCO PUE

This comment was originally posted on DCIM Support by Ed Tarento on 2019-07-04


Hi Fergus.  I'm not aware of any reason this solution should not still work.  Have you tried and failed with latest version/s?  If SE has changed DCO SNMP agent behaviour and/or PUE Dashboard API then that would affect this.  

Cheers

Ed

(CID:146670222)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 02:18 PM
0 Likes
0
364
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 02:18 PM

Re: DCE monitors DCO PUE

This comment was originally posted on DCIM Support by Winnie Chau on 2019-07-16


Hi Ed,

Thanks so much for the script. It helps us to solve a few headaches.

I have some DCO that work directly from your original script, maybe only need to edit the file via Webmin to make sure encoding follows Linux requirements. But for 3pcs DCOs I recently encountered, they only worked when I cut away the /1/ from awk commands i.e.

/bin/curl -ks https://"$DCOip"/rest/pue-v1/instantPueData| awk -F":" '{print $2}'|awk -F"," '{print $1}'

Is there any concern if I cut the /1/ away? Thanks a lot

Fergus Wong Daniel Kwong ben lai Michael Lam

Best regards,

Winnie

(CID:147195524)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 02:18 PM
0 Likes
0
364
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 02:18 PM

Re: DCE monitors DCO PUE

This comment was originally posted on DCIM Support by Gianluca Bertuletti on 2020-01-21


Hi Ed Tarento 

im trying to configure PUE with DCE 7.8.0 and DCO 8.3.2 but i cannot see the Value on DCE

i did the test.sh and no pue value

 

with snmpwalk i cannot find .1.3.6.1.4.1.26639.1.2.0

i have followed all PDF's steps

with API https://<dco server IP>/rest/pue-v1/instantPueData i can see the value

 where am i wrong?

 

thanks

(CID:153944595)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 02:18 PM
0 Likes
0
364
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 02:18 PM

Re: DCE monitors DCO PUE

This comment was originally posted on DCIM Support by spezialist on 2020-01-21


Dear Gianluca Bertuletti,

From your question:

with snmpwalk i cannot find .1.3.6.1.4.1.26639.1.2.0

Have you made the necessary changes to the /etc/snmp/snmpd.conf file?

You have created the necessary /etc/snmp/getPUE.sh script as follows:

Have you restarted the snmpd service?

With respect.

(CID:153944802)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 02:18 PM
0 Likes
0
364
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 02:18 PM

Re: DCE monitors DCO PUE

This comment was originally posted on DCIM Support by Gianluca Bertuletti on 2020-01-21


Hi spezialist

snmpd

here the file that i have used getPUE.sh

 

service restarted also rebooted DCO server

(CID:153944816)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 02:18 PM
0 Likes
0
364
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 02:18 PM

Re: DCE monitors DCO PUE

This comment was originally posted on DCIM Support by spezialist on 2020-01-21


Ok, and this /etc/snmp/getPUE.sh script is executable?

With respect.

(CID:153944831)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 02:18 PM
0 Likes
0
364
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 02:18 PM

Re: DCE monitors DCO PUE

This comment was originally posted on DCIM Support by Gianluca Bertuletti on 2020-01-21


Hi spezialist

(CID:153944839)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 02:18 PM
0 Likes
0
364
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 02:18 PM

Re: DCE monitors DCO PUE

This comment was originally posted on DCIM Support by François on 2020-01-21


Hi Gianluca Bertuletti,

Couldn't it be an encoding error of you executable files ? How did you create the .sh file ?

F

(CID:153944858)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 02:19 PM
0 Likes
0
364
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 02:19 PM

Re: DCE monitors DCO PUE

This comment was originally posted on DCIM Support by Gianluca Bertuletti on 2020-01-21


Hi

created as test.sh file

i used notepad++

(CID:153944865)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 02:19 PM
0 Likes
0
364
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 02:19 PM

Re: DCE monitors DCO PUE

This comment was originally posted on DCIM Support by spezialist on 2020-01-21


For proper testing, you need, for example, to run this script with two parameters:

./getPUE.sh -g .1.3.6.1.4.1.26639.1.2.0

or

./getPUE.sh -n .1.3.6.1.4.1.26639.1.1.0

Try it.

(CID:153944868)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 02:19 PM
0 Likes
0
364
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 02:19 PM

Re: DCE monitors DCO PUE

This comment was originally posted on DCIM Support by Gianluca Bertuletti on 2020-01-21


Hi spezialist

with your test i can see the PUE

(CID:153944873)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 02:19 PM
0 Likes
0
364
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 02:19 PM

Re: DCE monitors DCO PUE

This comment was originally posted on DCIM Support by François on 2020-01-21


Gianluca Bertuletti, you mean Notepad++ under Windows, and then you uploaded the file to the DCO server ? If yes, I did something very similar and it ended up not working.

I had to rewrite all the scripts by hand directly on the DCO server and using a text editor.

 

(CID:153944875)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 02:19 PM
0 Likes
0
364
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 02:19 PM

Re: DCE monitors DCO PUE

This comment was originally posted on DCIM Support by Gianluca Bertuletti on 2020-01-21


Hi François

with spezialist comment i can see the PUE on DCO consolle

(CID:153944880)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 02:19 PM
0 Likes
0
364
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 02:19 PM

Re: DCE monitors DCO PUE

This comment was originally posted on DCIM Support by spezialist on 2020-01-21


Great, now show the output of the command:

systemctl status snmpd

With respect.

(CID:153944887)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 02:19 PM
0 Likes
0
364
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 02:19 PM

Re: DCE monitors DCO PUE

This comment was originally posted on DCIM Support by Gianluca Bertuletti on 2020-01-21


Hi spezialist

 

(CID:153944894)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 02:19 PM
0 Likes
0
364
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 02:19 PM

Re: DCE monitors DCO PUE

This comment was originally posted on DCIM Support by spezialist on 2020-01-21


Ok, then try the following from DCO command line:

snmpwalk -v2c -cpublic 127.0.0.1 .1.3.6.1.4.1.26639.1.2.0

or from outside:

snmpwalk -v2c -cpublic <DCOip> .1.3.6.1.4.1.26639.1.2.0

I assume using SNMP v2 and public community string.

(CID:153944910)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 02:19 PM
0 Likes
0
364
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 02:19 PM

Re: DCE monitors DCO PUE

This comment was originally posted on DCIM Support by spezialist on 2020-01-21


From the comments above regarding test.sh:

Andrew, 

Check the line in test.sh is a single line

pue=`/bin/curl -ks https://"$DCOip"/rest/pue-v1/instantPueData| awk -F":" '/1/ {print $2}'|awk -F"," '/1/ {print $1}' `

and not 2 lines as it show in the PDF

I'll update the doco to make this clear

Let me know how you go

(CID:153944914)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 02:20 PM
0 Likes
0
364
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 02:20 PM

Re: DCE monitors DCO PUE

This comment was originally posted on DCIM Support by Gianluca Bertuletti on 2020-01-21


No snmpwalk on DCO

i did a snmpwalk with DCE but no .1.3.6.1.4.1.26639.1.2.0 

Walk.txt

(CID:153944917)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 02:20 PM
0 Likes
0
364
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 02:20 PM

Re: DCE monitors DCO PUE

This comment was originally posted on DCIM Support by spezialist on 2020-01-21


Please take a screenshot (not txt or pdf file) and attach it:

(CID:153944922)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 02:20 PM
0 Likes
0
364
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 02:20 PM

Re: DCE monitors DCO PUE

This comment was originally posted on DCIM Support by Gianluca Bertuletti on 2020-01-21


(CID:153944929)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 02:20 PM
0 Likes
0
364
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 02:20 PM

Re: DCE monitors DCO PUE

This comment was originally posted on DCIM Support by spezialist on 2020-01-22


Dear Gianluca Bertuletti,

Regarding the test.sh file: make sure that you have exactly this line (spaces are important):

pue=`/bin/curl -ks https://"$DCOip"/rest/pue-v1/instantPueData| awk -F":" '/1/ {print $2}'|awk -F"," '/1/ {print $1}'`

This works fine for me:

[root@dco ~]# ./test.sh
localhost
-1.0

Regarding getPUE.sh file: this file is very simple and does not support snmpwalking of the full MIB tree (this is important). That is, snmpwalk ... <DCOip> enterprises, for example, will not work (you will not see what you would like). There are two ways to check the operation of this file:

[root@dco snmp]# snmpwalk -v2c -cpublic localhost enterprises.26639.1.2.0
SNMPv2-SMI::enterprises.26639.1.2.0 = STRING: "-1.0"

or

[root@dco snmp]# snmpget -v2c -cpublic localhost enterprises.26639.1.2.0
SNMPv2-SMI::enterprises.26639.1.2.0 = STRING: "-1.0"

For a DCE server, this is quite enough, since, for example, in its work it uses only snmpget requests, but not snmpwalk requests.

Hope this helps you.

With respect.

(CID:153945238)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 02:20 PM
0 Likes
0
364
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 02:20 PM

Re: DCE monitors DCO PUE

This comment was originally posted on DCIM Support by Gianluca Bertuletti on 2020-01-22


Hi spezialist

i did some test on my DCO Vm and now works.

for your experience, is it possible to have 2 decimals? 

now is 1.2 but in real 1.14

(CID:153945243)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 02:20 PM
0 Likes
0
364
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 02:20 PM

Re: DCE monitors DCO PUE

This comment was originally posted on DCIM Support by spezialist on 2020-01-22


Dear Gianluca Bertuletti,

Excellent 😀.

I understand you, and I'll write here as soon as I can.

With respect.

(CID:153945526)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 02:20 PM
0 Likes
0
364
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 02:20 PM

Re: DCE monitors DCO PUE

This comment was originally posted on DCIM Support by spezialist on 2020-01-24


Dear Gianluca Bertuletti,

From your question:

for your experience, is it possible to have 2 decimals? 

now is 1.2 but in real 1.14

Unfortunately, the problem is on the DCE software side: for the Generic sensor type from Supplemental OIDs... menu it is impossible to specify the number of decimal places. That is, by default, only one decimal place (i.e. 1.0).

With respect.

(CID:154403349)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 02:20 PM
0 Likes
0
364
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 02:20 PM

🔒 Closed

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Share
Top Experts
User Count
Jef
Commander Jef Commander
41
APC_Steve
Lt. Commander APC_Steve Lt. Commander
23
gsterling
Lt. Commander gsterling Lt. Commander
20
Cory_McDonald
Lieutenant Cory_McDonald Lieutenant
13
GavanOB
Lieutenant GavanOB Lieutenant
7
See More Top Experts
Find a Service Provider
Find a certified partner to help you address your integration, installation, maintenance and project needs.
View all Providers
Support

Have a question? Please contact us with details, and we will respond.

Contact Us
FAQ

Look through existing questions to find popular answers.

Learn More
About

Want to know more about Exchange and its possibilities?

Learn More

Full access is just steps away!

Join Exchange for FREE and get unlimited access to our global community of experts.

Connect with Peers & Experts

Discuss challenges in energy and automation with 30,000+ experts and peers.

Get Support in Our Knowledge Base

Find answers in 10,000+ support articles to help solve your product and business challenges.

Ask Questions. Give Solutions

Find peer based solutions to your questions. Provide answers for fellow community members!

Register today for FREE

Register Now

Already have an account?Log in

About Us FAQ Terms & Conditions Privacy Notice Change your cookie settings
©2020, Schneider Electric