Sign In Help
Schneider Electric
HelpSign In
Schneider Electric Exchange
  • Home
  • Collaborate
  • Develop
  • Shop
Home Collaborate Develop Shop Log in or Register Help

Invite a Co-worker

Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel

Invitation Sent

Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
  • Home
  • Collaborate
  • Exchange Community
  • :
  • EcoStruxure IT
  • :
  • EcoStruxure IT forum
  • :
  • DCE Time Settings off by 1 hour
Community Menu
  • Forums
    • By Topic
        • EcoStruxure IT
          • EcoStruxure IT forum
        • Industrial Automation
          • Industry Automation and Control Forum
          • Alliance System Integrators Forum
          • Machine Solutions in the Digital Transformation
          • EcoStruxure Automation Expert / IEC 61499 Forum
          • Industrial Edge Computing Forum
          • Level and Pressure Instrumentation Forum
          • Modicon User Group
          • PLC Club Indonesia
          • SEE Automation Club Forum
          • Fabrika ve Makina Otomasyonu Çözümleri
          • Форум по промышленной автоматизации СНГ
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Forum
          • SCADA and Telemetry Devices Forum
        • Power Distribution IEC
          • Power Distribution and Digital
          • Power Standards & Regulations
          • Paneelbouw & Energie Distributie
        • Power Distribution Softwares
          • EcoStruxure Power Design Forum
          • SEE Electrical Building+ Forum
          • LayoutFAST User Group Forum
        • Solutions for your Business
          • Solutions for Food & Beverage Forum
          • Solutions for Healthcare Forum
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Forum
        • Healthcare
          • Solutions for Healthcare Forum
      • EcoStruxure IT
        • EcoStruxure IT forum
      • Industrial Automation
        • Industry Automation and Control Forum
        • Alliance System Integrators Forum
        • Machine Solutions in the Digital Transformation
        • EcoStruxure Automation Expert / IEC 61499 Forum
        • Industrial Edge Computing Forum
        • Level and Pressure Instrumentation Forum
        • Modicon User Group
        • PLC Club Indonesia
        • SEE Automation Club Forum
        • Fabrika ve Makina Otomasyonu Çözümleri
        • Форум по промышленной автоматизации СНГ
      • SCADA & Telemetry Solutions
        • Geo SCADA Expert Forum
        • SCADA and Telemetry Devices Forum
      • Power Distribution IEC
        • Power Distribution and Digital
        • Power Standards & Regulations
        • Paneelbouw & Energie Distributie
      • Power Distribution Softwares
        • EcoStruxure Power Design Forum
        • SEE Electrical Building+ Forum
        • LayoutFAST User Group Forum
      • Solutions for your Business
        • Solutions for Food & Beverage Forum
        • Solutions for Healthcare Forum
      • Food & Beverage
        • Solutions for Food & Beverage Forum
      • Healthcare
        • Solutions for Healthcare Forum
  • Blogs
    • By Topic
        • Industrial Automation
          • Industrial Edge Computing Blog
          • Industry 4.0 Blog
          • Industrie du Futur France
        • SCADA & Telemetry Solutions
          • SCADA and Telemetry Blog
        • Power Distribution IEC
          • Power Events & Webinars
          • Power Foundations Blog
        • Power Distribution NEMA
          • NEMA Power Foundations Blog
        • Power Distribution Softwares
          • EcoStruxure Power Design Blog
          • SEE Electrical Building+ Blog
        • Solutions for your Business
          • Solutions for Food & Beverage Blog
          • Solutions for Healthcare Blog
          • Solutions for Retail Blog
        • Community experts & publishers
          • Publishers Community
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Blog
        • Healthcare
          • Solutions for Healthcare Blog
        • Retail
          • Solutions for Retail Blog
      • Industrial Automation
        • Industrial Edge Computing Blog
        • Industry 4.0 Blog
        • Industrie du Futur France
      • SCADA & Telemetry Solutions
        • SCADA and Telemetry Blog
      • Power Distribution IEC
        • Power Events & Webinars
        • Power Foundations Blog
      • Power Distribution NEMA
        • NEMA Power Foundations Blog
      • Power Distribution Softwares
        • EcoStruxure Power Design Blog
        • SEE Electrical Building+ Blog
      • Solutions for your Business
        • Solutions for Food & Beverage Blog
        • Solutions for Healthcare Blog
        • Solutions for Retail Blog
      • Community experts & publishers
        • Publishers Community
      • Food & Beverage
        • Solutions for Food & Beverage Blog
      • Healthcare
        • Solutions for Healthcare Blog
      • Retail
        • Solutions for Retail Blog
  • Ideas
        • Industrial Automation
          • Modicon Ideas & new features
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Ideas
          • SCADA and Telemetry Devices Ideas
  • Knowledge Center
    • Building Automation Knowledge Base
    • Industrial Automation How-to videos
    • Ask Exchange
    • Digital E-books
    • Success Stories Corner
    • Power Talks
  • Events & Webinars
  • Support
    • User Guide
    • Leaderboard
    • Releases Notes
How can we help?
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
49470members
Join Now
242767posts
Join Now

DCE Time Settings off by 1 hour

Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Back to EcoStruxure IT forum
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 06:07 PM
0 Likes
8
153
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 06:07 PM

DCE Time Settings off by 1 hour

This question was originally posted on DCIM Support by Michael Adachi on 2019-03-18


DCE Version 7.3.1.114

I've reset the server time on DCE via the System -> Server Administration Settings -> Time Settings ...

tab several times to our ntp server.  After the server reboots, the time reported is correct.  However, after a few days, the time is off by 1 hour, and the check box to "Enable StruxureWare Data Center Expert as NTP server" gets unchecked.

The Server Locale: is set to English (METRIC) and

Server Time Zone:  is set to (GMT-7:00) Mountain Standard Time (America/Edmonton)

 

Any idea why the server time is going off by an hour, and why the "Enable StruxureWare Data Center Expert as NTP server" check box is getting unchecked?

 

Thanks

(CID:140715257)

Labels
  • Data Center Expert
Tags (1)
  • Tags:
  • bug
Share
  • All forum topics
  • Previous Topic
  • Next Topic
8 Replies 8
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 06:07 PM
0 Likes
0
153
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 06:07 PM

Re: DCE Time Settings off by 1 hour

This answer was originally posted on DCIM Support by spezialist on 2019-03-19


Dear Michael Adachi,

Please clarify, is your DCE-server a physical appliance (server) or VMware VM appliance?

If this is a physical appliance (server), you need to make sure that its RTC settings in BIOS are set to GMT.

If this is a VMware VM appliance, then you need to make sure that the checkbox Synchronize guest time with host is not checked:


Hope this helps you.

With respect.

(CID:141269640)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 06:07 PM
0 Likes
0
153
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 06:07 PM

Re: DCE Time Settings off by 1 hour

This comment was originally posted on DCIM Support by Michael Adachi on 2019-03-19


Hi,

The DCE server is a VM, and the VM appliance is configured as above.

 

Any other ideas?

 

Thanks

(CID:141264813)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 06:07 PM
0 Likes
0
153
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 06:07 PM

Re: DCE Time Settings off by 1 hour

This answer was originally posted on DCIM Support by spezialist on 2019-03-20


Dear Michael Adachi,

Please ensure, that the your external NTP servers are configured to use Coordinated Universal Time (GMT).

Try to check it, for example, with the help of your MS Windows PC and the standard w32tm utility:

textw32tmC:\>w32tm /stripchart /computer:us.pool.ntp.org /dataonly /samples:5 Tracking us.pool.ntp.org [208.87.221.228:123]. Collecting 5 samples. The current time is 19/07/2012 18:36:32. 18:36:32, +03.3575094s 18:36:34, +03.3573679s 18:36:37, +03.3572986s 18:36:39, +03.3570290s 18:36:41, +03.3565357s

Make sure the local time is displayed correctly.

With respect.

(CID:141269643)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 06:07 PM
0 Likes
0
153
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 06:07 PM

Re: DCE Time Settings off by 1 hour

This comment was originally posted on DCIM Support by Michael Adachi on 2019-03-20


Here is the result of the above command:

C:\>w32tm /stripchart /computer:ntp.yyc.com /dataonly /samples:5

Tracking ntp.yyc.com [10.250.6.30:123].

Collecting 5 samples.

The current time is 2019-03-20 3:05:10 PM.

15:05:10, -00.1674209s

15:05:12, -00.1704247s

15:05:14, -00.1703914s

15:05:16, -00.1704150s

15:05:18, -00.1705623s

(CID:141265251)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 06:07 PM
0 Likes
0
153
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 06:07 PM

Re: DCE Time Settings off by 1 hour

This comment was originally posted on DCIM Support by spezialist on 2019-04-01


Dear Michael Adachi,

Tell us, please, did you solve your problem or not?

With respect.

(CID:141269190)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 06:08 PM
0 Likes
0
153
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 06:08 PM

Re: DCE Time Settings off by 1 hour

This comment was originally posted on DCIM Support by Michael Adachi on 2019-04-01


Hi,

The problem has gone away (but I'm not too sure why...)

 

Thank you

(CID:141269614)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 06:08 PM
0 Likes
0
153
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 06:08 PM

Re: DCE Time Settings off by 1 hour

This comment was originally posted on DCIM Support by spezialist on 2019-04-01


Ok, very thanks for the good feedback 😀.

(CID:141269639)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 06:08 PM
0 Likes
0
153
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 06:08 PM

🔒 Closed

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Share
Top Experts
User Count
APC_Steve
Lt. Commander APC_Steve Lt. Commander
2
GavanOB
Lieutenant GavanOB Lieutenant
1
lasalle_1
Crewman lasalle_1
1
Jef
Commander Jef Commander
1
tjlaw
Lieutenant JG tjlaw Lieutenant JG
1
See More Top Experts
Find a Service Provider
Find a certified partner to help you address your integration, installation, maintenance and project needs.
View all Providers
Support

Have a question? Please contact us with details, and we will respond.

Contact Us
FAQ

Look through existing questions to find popular answers.

Learn More
About

Want to know more about Exchange and its possibilities?

Learn More

Full access is just steps away!

Join Exchange for FREE and get unlimited access to our global community of experts.

Connect with Peers & Experts

Discuss challenges in energy and automation with 30,000+ experts and peers.

Get Support in Our Knowledge Base

Find answers in 10,000+ support articles to help solve your product and business challenges.

Ask Questions. Give Solutions

Find peer based solutions to your questions. Provide answers for fellow community members!

Register today for FREE

Register Now

Already have an account?Log in

About Us FAQ Terms & Conditions Privacy Notice Change your cookie settings
©2020, Schneider Electric