A customer has some cases where the graphical report in Data Center Expert are not showing the same values as in the table view:
That makes it difficult to trust the graphical reports.
Is this a known issue or is there a workaround?
--Christian
(CID:105467001)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 12:25 AM . Last Modified: 2 weeks ago
Hi Christian,
My first thought on this would be to check out k-base FA158422. It states that ISXC / DCE "graphs may not include all data points including some peaks or valleys". This will in part be based on how many data points are being graphed. I would suggest verifying this is what's happening by graphing that specific day instead of the 2 weeks that are graphed on that image. Please also keep in mind that if this is a critical value, DCE can always alert based on that state change.
Thanks,
Steve
(CID:105467038)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 12:26 AM . Last Modified: 2023-10-31 10:26 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.