  • DCE-Apply Firmware Update device show problem
Community Menu
  • Forums
    • By Topic
        • EcoStruxure IT
          • EcoStruxure IT forum
        • Industrial Automation
          • Industry Automation and Control Forum
          • Alliance System Integrators Forum
          • Machine Solutions in the Digital Transformation
          • EcoStruxure Automation Expert / IEC 61499 Forum
          • Industrial Edge Computing Forum
          • Level and Pressure Instrumentation Forum
          • Modicon User Group
          • PLC Club Indonesia
          • SEE Automation Club Forum
          • Fabrika ve Makina Otomasyonu Çözümleri
          • Форум по промышленной автоматизации СНГ
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Forum
          • SCADA and Telemetry Devices Forum
        • Power Distribution IEC
          • Power Distribution and Digital
          • Power Standards & Regulations
          • Paneelbouw & Energie Distributie
        • Power Distribution Softwares
          • EcoStruxure Power Design Forum
          • SEE Electrical Building+ Forum
          • LayoutFAST User Group Forum
        • Solutions for your Business
          • Solutions for Food & Beverage Forum
          • Solutions for Healthcare Forum
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Forum
        • Healthcare
          • Solutions for Healthcare Forum
      • EcoStruxure IT
        • EcoStruxure IT forum
      • Industrial Automation
        • Industry Automation and Control Forum
        • Alliance System Integrators Forum
        • Machine Solutions in the Digital Transformation
        • EcoStruxure Automation Expert / IEC 61499 Forum
        • Industrial Edge Computing Forum
        • Level and Pressure Instrumentation Forum
        • Modicon User Group
        • PLC Club Indonesia
        • SEE Automation Club Forum
        • Fabrika ve Makina Otomasyonu Çözümleri
        • Форум по промышленной автоматизации СНГ
      • SCADA & Telemetry Solutions
        • Geo SCADA Expert Forum
        • SCADA and Telemetry Devices Forum
      • Power Distribution IEC
        • Power Distribution and Digital
        • Power Standards & Regulations
        • Paneelbouw & Energie Distributie
      • Power Distribution Softwares
        • EcoStruxure Power Design Forum
        • SEE Electrical Building+ Forum
        • LayoutFAST User Group Forum
      • Solutions for your Business
        • Solutions for Food & Beverage Forum
        • Solutions for Healthcare Forum
      • Food & Beverage
        • Solutions for Food & Beverage Forum
      • Healthcare
        • Solutions for Healthcare Forum
  • Blogs
    • By Topic
        • Industrial Automation
          • Industrial Edge Computing Blog
          • Industry 4.0 Blog
          • Industrie du Futur France
        • SCADA & Telemetry Solutions
          • SCADA and Telemetry Blog
        • Power Distribution IEC
          • Power Events & Webinars
          • Power Foundations Blog
        • Power Distribution NEMA
          • NEMA Power Foundations Blog
        • Power Distribution Softwares
          • EcoStruxure Power Design Blog
          • SEE Electrical Building+ Blog
        • Solutions for your Business
          • Solutions for Food & Beverage Blog
          • Solutions for Healthcare Blog
          • Solutions for Retail Blog
        • Community experts & publishers
          • Publishers Community
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Blog
        • Healthcare
          • Solutions for Healthcare Blog
        • Retail
          • Solutions for Retail Blog
      • Industrial Automation
        • Industrial Edge Computing Blog
        • Industry 4.0 Blog
        • Industrie du Futur France
      • SCADA & Telemetry Solutions
        • SCADA and Telemetry Blog
      • Power Distribution IEC
        • Power Events & Webinars
        • Power Foundations Blog
      • Power Distribution NEMA
        • NEMA Power Foundations Blog
      • Power Distribution Softwares
        • EcoStruxure Power Design Blog
        • SEE Electrical Building+ Blog
      • Solutions for your Business
        • Solutions for Food & Beverage Blog
        • Solutions for Healthcare Blog
        • Solutions for Retail Blog
      • Community experts & publishers
        • Publishers Community
      • Food & Beverage
        • Solutions for Food & Beverage Blog
      • Healthcare
        • Solutions for Healthcare Blog
      • Retail
        • Solutions for Retail Blog
  • Ideas
        • Industrial Automation
          • Modicon Ideas & new features
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Ideas
          • SCADA and Telemetry Devices Ideas
  • Knowledge Center
    • Building Automation Knowledge Base
    • Industrial Automation How-to videos
    • Ask Exchange
    • Digital E-books
    • Success Stories Corner
    • Power Talks
  • Events & Webinars
  • Support
    • User Guide
    • Leaderboard
    • Releases Notes
How can we help?
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
49412members
Join Now
242712posts
Join Now

DCE-Apply Firmware Update device show problem

Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Solved Go to Solution
Back to EcoStruxure IT forum
Solved
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 04:40 PM
0 Likes
7
103
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 04:40 PM

DCE-Apply Firmware Update device show problem

This question was originally posted on DCIM Support by Boris on 2019-01-30


Hello

In all customers where that installed DCE version 7.5 I have the same problem when I opened "Apply Firmware Updates" window.

No any devices areappears into windows where I need ro "Select Device Updates"

How I can fix it ?

 

Thanks

(CID:138811493)

Solved! Go to Solution.

Labels
  • Data Center Expert
Share

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 04:40 PM
0 Likes
4
103
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 04:40 PM

Re: DCE-Apply Firmware Update device show problem

This answer was originally posted on DCIM Support by spezialist on 2019-01-30


Dear Boris,

This means, that either the DCE-server does not have firmware updates for your devices, or your devices has the latest firmware.

A DCE-server (not a DCE-client) can obtain firmware updates for your devices in two ways.

  • The first way is to import the DCE device firmware catalog (if the DCE-server does not have access to the Internet).
  • The second way is for the DCE-server to download the necessary firmware updates from online resource https://updates.apc.com/ (i.e. the DCE-server must have network access to the Internet at https://updates.apc.com:443).

If you have further questions, please ask.

With respect.

(CID:138811512)

See Answer In Context

Share
  • All forum topics
  • Previous Topic
  • Next Topic
7 Replies 7
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 04:40 PM
0 Likes
4
104
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 04:40 PM

Re: DCE-Apply Firmware Update device show problem

This answer was originally posted on DCIM Support by spezialist on 2019-01-30


Dear Boris,

This means, that either the DCE-server does not have firmware updates for your devices, or your devices has the latest firmware.

A DCE-server (not a DCE-client) can obtain firmware updates for your devices in two ways.

  • The first way is to import the DCE device firmware catalog (if the DCE-server does not have access to the Internet).
  • The second way is for the DCE-server to download the necessary firmware updates from online resource https://updates.apc.com/ (i.e. the DCE-server must have network access to the Internet at https://updates.apc.com:443).

If you have further questions, please ask.

With respect.

(CID:138811512)

See Answer In Context

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 04:41 PM
0 Likes
0
103
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 04:41 PM

Re: DCE-Apply Firmware Update device show problem

This comment was originally posted on DCIM Support by Boris on 2019-01-30


Hello

Many thanks for ypur answer I'll check .

Unfortunately the link of the download frimware is broken

(CID:138811546)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 04:41 PM
0 Likes
0
103
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 04:41 PM

Re: DCE-Apply Firmware Update device show problem

This comment was originally posted on DCIM Support by Cory McDonald on 2019-01-30


Boris,

You can see in your URL that you are trying to directly access https://updates.apc.com via a web browser, which is not possible.  You need to use the full link.  To access and download the upgrades manually, it would be: https://download.schneider-electric.com/files?p_Archive_Name=DBUE-7H7NVA.zip&p_enDocType=Software+-+...

If you are unable to access that full link, most likely something on your network is changing the URL, such as a proxy, and preventing the access/download of the file.  I have just tested the URL and the download works fine.

Kind Regards,

Cory

(CID:138811550)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 04:41 PM
0 Likes
0
103
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 04:41 PM

Re: DCE-Apply Firmware Update device show problem

This comment was originally posted on DCIM Support by Boris on 2019-01-30


many thanks

I haven't problem with full link . My question how I get this full link ?

(CID:138811565)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 04:41 PM
0 Likes
0
103
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 04:41 PM

Re: DCE-Apply Firmware Update device show problem

This comment was originally posted on DCIM Support by Cory McDonald on 2019-01-30


Video: How do I manually load APC and NetBotz device firmware to StruxureWare Data Center Expert?

https://www.apc.com/us/en/faqs/FA226042/

(CID:138811573)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 04:41 PM
0 Likes
0
103
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 04:41 PM

Re: DCE-Apply Firmware Update device show problem

This comment was originally posted on DCIM Support by spezialist on 2019-02-09


Dear Boris,

Tell us, please, did you solve your problem or not?

With respect.

(CID:139693913)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 04:41 PM
0 Likes
0
103
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 04:41 PM

🔒 Closed

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Share
Top Experts
User Count
APC_Steve
Lt. Commander APC_Steve Lt. Commander
2
GavanOB
Lieutenant GavanOB Lieutenant
1
lasalle_1
Crewman lasalle_1
1
Jef
Commander Jef Commander
1
tjlaw
Lieutenant JG tjlaw Lieutenant JG
1
See More Top Experts
Find a Service Provider
Find a certified partner to help you address your integration, installation, maintenance and project needs.
View all Providers
Support

Have a question? Please contact us with details, and we will respond.

Contact Us
FAQ

Look through existing questions to find popular answers.

Learn More
About

Want to know more about Exchange and its possibilities?

Learn More

Full access is just steps away!

Join Exchange for FREE and get unlimited access to our global community of experts.

Connect with Peers & Experts

Discuss challenges in energy and automation with 30,000+ experts and peers.

Get Support in Our Knowledge Base

Find answers in 10,000+ support articles to help solve your product and business challenges.

Ask Questions. Give Solutions

Find peer based solutions to your questions. Provide answers for fellow community members!

Register today for FREE

Register Now

Already have an account?Log in

About Us FAQ Terms & Conditions Privacy Notice Change your cookie settings
©2020, Schneider Electric